I have two emontx. v3
one of the emontx will only transmit values if the 5V USB power is connected.
only one emontx works 100% with only the 9V AC power connection.
The other one needs the 9V AC voltage reference + 5V USB to work correctly.
Both are powered by identical 9V AC transformers
Only one transmits wirelessly to to the emonPi. The other gets stuck with RED LED constantly on.
The good emontx values arrive in emonPi
The bad emontx values appear to transmit, but the values seen in emonPi CMS are all ZERO.
i worked out that if I add 5V DC (via FTDI or USB cable) then the bad emontx works fine.
Is there a configuration setting (hardware or software) i am missing on the bad emontx to allow it to operate correctly exclusively on the 9V AC power supply? and not need the 5V USB connetion to be applied?
Good emontx config and versions
emonTx V3.4 EmonLibCM ContinemonTx V3.4 EmonLibCM Continuous Monitoring V2.00
OpenEnergyMonitor.org
No EEPROM config
Settings:
Group 210, Node 15, Band 433 MHz
Calibration:
vCal = 298.22
assumedV = 240.00
i1Cal = 90.90
i1Lead = 4.20
i2Cal = 90.90
i2Lead = 4.20
i3Cal = 90.90
i3Lead = 4.20
i4Cal = 16.67
i4Lead = 6.00
datalog = 9.96
pulses = 1
pulse period = 100
temp_enable = 1
Temperature Sensors found = 0 of 1
Temperature measurement is NOT enabled.
RF whitened
RFM69CW only Node: 15 Freq: 433MHz Group: 210
bad emontx and config
emonTx V3.4 EmonLibCM Contide
No EEPROM config
Settings:
Group 210, Node 16, Band 433 MHz
Calibration:
vCal = 268.97
assumedV = 240.00
i1Cal = 90.90
i1Lead = 4.20
i2Cal = 90.90
i2Lead = 4.20
i3Cal = 90.90
i3Lead = 4.20
i4Cal = 16.67
i4Lead = 6.00
datalog = 9.96
pulses = 1
pulse period = 100
temp_enable = 1
RF whitened
RFM69CW only Node: 16 Freq: 433MHz Group: 210
They look identical to me
both emontx are running
emonTxV3.4 Continuous Sampling
using EmonLibCM https://github.com/openenergymonitor/EmonLibCM
Authors: Robin Emley, Robert Wall, Trystan Lea
Part of the openenergymonitor.org project
Licence: GNU GPL V3