I have an emonPi and a single emonTx in the same room, connected via the low-power wireless link. I see frequent data loss for the emonTx data. Over the course of an hour, I see ~12 gaps where each gap is typically missing 1-2 samples. My sampling interval is 10 seconds.
Is this rate of data loss expected? Would I get significantly less data loss if I hooked up a wire connection?
Welcome, Richard, to the OEM forum.
I take it you’re seeing the gaps in the emonPi data. In the normal scheme of things, the emonTx transmits at intervals of just under 10 s, whilst the emonPi’s database - assuming you’re using PHPFina, is exactly 10 s, the idea being that data arrives slightly faster than it’s accepted, so once in a while a reading gets overwritten, so that you don’t have the odd missing value should one get delayed while the Pi is doing some housekeeping, say. You haven’t set your emonPi to do something else as well, I assume?
I wonder whether there’s another transmitter on the same frequency nearby that’s interfering with the radio transmissions. The other thought is, although I’ve never seen it, have you got too much signal and the emonPi’s receiver is being swamped? What is the RSSI you’re seeing? Losing 12 - 24 messages out of 360 does seem excessive. Are the missing values happening at regular intervals, or do they appear to be at random?
If the data is being lost in transmission, then a wired connection will obviously provide a secure path for the data.
If it’s not, then I’m not sure what to suggest - I’m assuming everything is recently acquired so I can rule out software that isn’t the current version.
I’m not using the published radio software at present, so this doesn’t mean much - I’m using an old RPi 2B as an emonBase, one emonTx only 1 m or so away has missed 2 samples in a little over 3 hours, a second emonTx 2 rooms and 3 walls away missed 22 samples, one of those being coincident with the other emonTx. So I think one missing sample could well be a r.f. collision.
You can watch the emonhub log and see exactly what is happening. Check your log setting is set to DEBUG in the emonhub config, then SSH in and run
tail -f /var/log/emonhub/emonhub.log | grep "NEW FRAME : OK 19"
where the number (19) is changed to match the nodeid (probably 15).
You will get one line for every set of data from the emonTX.
Correct. My feed from the emonTx is set to 10 seconds. My RSSI is -44, as shown on the Inputs
tab and in the logs:
MQTT Publishing: emon/emontx3cm15/rssi -44
The data loss appears randomly spaced as well as random duration (i.e. 1, 2 or sometimes more samples lost).
I’m not aware of another transmitter nearby, but I don’t have equipment to monitor that.
This is a recent purchase (within the last month), so I hope I’ve got fresh firmware!
Yes, watching the logs I see those NEW FRAME
logs from my emonTX. I also see there are missing entries where I would have expected to see them.
Here is a what I scraped from my current logfile (well, all I was allowed to paste in):
2020-12-14 16:28:51,817 DEBUG RFM2Pi 139233 NEW FRAME : OK 15 16 253 85 85 57 126 161 82 222 85 221 85 85 85 96 25 85 85 120 96 85 85 217 84 85 85 85 85 85 85 7 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:29:01,698 DEBUG RFM2Pi 139236 NEW FRAME : OK 15 19 253 85 85 62 126 160 82 222 85 221 85 85 85 110 25 85 85 120 96 85 85 217 84 85 85 85 85 85 85 7 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:29:11,611 DEBUG RFM2Pi 139239 NEW FRAME : OK 15 18 253 85 85 50 126 163 82 223 85 221 85 85 85 20 25 85 85 123 96 85 85 217 84 85 85 85 85 85 85 7 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:29:21,627 DEBUG RFM2Pi 139242 NEW FRAME : OK 15 29 253 85 85 56 126 173 82 220 85 210 85 85 85 19 25 85 85 123 96 85 85 216 84 85 85 85 85 85 85 7 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:29:31,543 DEBUG RFM2Pi 139245 NEW FRAME : OK 15 28 253 85 85 36 126 174 82 223 85 221 85 85 85 25 25 85 85 123 96 85 85 216 84 85 85 85 85 85 85 7 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:29:41,534 DEBUG RFM2Pi 139248 NEW FRAME : OK 15 31 253 85 85 36 126 168 82 222 85 220 85 85 85 7 25 85 85 122 96 85 85 219 84 85 85 85 85 85 85 7 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:29:51,418 DEBUG RFM2Pi 139251 NEW FRAME : OK 15 30 253 85 85 59 126 85 93 222 85 221 85 85 85 2 25 85 85 122 96 85 85 219 84 85 85 85 85 85 85 19 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:30:01,417 DEBUG RFM2Pi 139254 NEW FRAME : OK 15 25 253 85 85 57 126 85 93 223 85 210 85 85 85 8 25 85 85 101 96 85 85 219 84 85 85 85 85 85 85 19 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:30:11,325 DEBUG RFM2Pi 139257 NEW FRAME : OK 15 24 253 85 85 59 126 84 93 223 85 210 85 85 85 54 25 85 85 101 96 85 85 218 84 85 85 85 85 85 85 19 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:30:21,251 DEBUG RFM2Pi 139260 NEW FRAME : OK 15 27 253 85 85 39 126 86 93 222 85 221 85 85 85 61 25 85 85 101 96 85 85 218 84 85 85 85 85 85 85 19 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:30:31,256 DEBUG RFM2Pi 139263 NEW FRAME : OK 15 26 253 85 85 36 126 81 93 223 85 210 85 85 85 59 25 85 85 100 96 85 85 218 84 85 85 85 85 85 85 19 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:30:41,153 DEBUG RFM2Pi 139266 NEW FRAME : OK 15 5 253 85 85 59 126 80 93 223 85 221 85 85 85 33 25 85 85 100 96 85 85 197 84 85 85 85 85 85 85 19 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:30:51,125 DEBUG RFM2Pi 139269 NEW FRAME : OK 15 4 253 85 85 60 126 93 93 222 85 220 85 85 85 44 25 85 85 100 96 85 85 197 84 85 85 85 85 85 85 19 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:31:01,104 DEBUG RFM2Pi 139272 NEW FRAME : OK 15 7 253 85 85 61 126 93 93 220 85 210 85 85 85 42 25 85 85 103 96 85 85 196 84 85 85 85 85 85 85 19 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:31:10,989 DEBUG RFM2Pi 139275 NEW FRAME : OK 15 6 253 85 85 58 126 94 93 221 85 211 85 85 85 208 25 85 85 103 96 85 85 196 84 85 85 85 85 85 85 19 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:31:21,001 DEBUG RFM2Pi 139278 NEW FRAME : OK 15 1 253 85 85 60 126 89 93 220 85 211 85 85 85 223 25 85 85 102 96 85 85 196 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:31:30,892 DEBUG RFM2Pi 139281 NEW FRAME : OK 15 0 253 85 85 50 126 119 82 210 85 208 85 85 85 218 25 85 85 102 96 85 85 199 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:31:40,912 DEBUG RFM2Pi 139284 NEW FRAME : OK 15 3 253 85 85 63 126 193 83 210 85 208 85 85 85 193 25 85 85 102 96 85 85 199 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:31:50,894 DEBUG RFM2Pi 139287 NEW FRAME : OK 15 2 253 85 85 63 126 231 83 211 85 209 85 85 85 204 25 85 85 97 96 85 85 199 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:32:00,792 DEBUG RFM2Pi 139290 NEW FRAME : OK 15 13 253 85 85 199 126 152 83 211 85 209 85 85 85 203 25 85 85 97 96 85 85 198 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:32:10,762 DEBUG RFM2Pi 139293 NEW FRAME : OK 15 12 253 85 85 151 126 177 83 211 85 209 85 85 85 247 25 85 85 97 96 85 85 198 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:32:20,661 DEBUG RFM2Pi 139296 NEW FRAME : OK 15 15 253 85 85 158 126 173 83 211 85 209 85 85 85 242 25 85 85 96 96 85 85 198 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:32:30,647 DEBUG RFM2Pi 139299 NEW FRAME : OK 15 14 253 85 85 158 126 56 83 211 85 209 85 85 85 249 25 85 85 96 96 85 85 193 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:32:40,638 DEBUG RFM2Pi 139302 NEW FRAME : OK 15 9 253 85 85 157 126 91 83 211 85 209 85 85 85 229 25 85 85 99 96 85 85 193 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:32:50,550 DEBUG RFM2Pi 139305 NEW FRAME : OK 15 8 253 85 85 158 126 92 83 211 85 209 85 85 85 225 25 85 85 99 96 85 85 192 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:33:00,459 DEBUG RFM2Pi 139308 NEW FRAME : OK 15 11 253 85 85 145 126 81 83 208 85 214 85 85 85 236 25 85 85 99 96 85 85 192 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:33:10,409 DEBUG RFM2Pi 139311 NEW FRAME : OK 15 10 253 85 85 153 126 171 80 208 85 214 85 85 85 232 25 85 85 98 96 85 85 192 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:33:20,420 DEBUG RFM2Pi 139314 NEW FRAME : OK 15 53 253 85 85 154 126 173 80 211 85 209 85 85 85 148 25 85 85 98 96 85 85 195 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:33:30,317 DEBUG RFM2Pi 139317 NEW FRAME : OK 15 52 253 85 85 135 126 232 80 211 85 209 85 85 85 144 25 85 85 98 96 85 85 195 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:33:40,312 DEBUG RFM2Pi 139320 NEW FRAME : OK 15 55 253 85 85 143 126 204 80 211 85 209 85 85 85 156 25 85 85 109 96 85 85 195 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:33:50,212 DEBUG RFM2Pi 139323 NEW FRAME : OK 15 54 253 85 85 128 126 196 80 208 85 214 85 85 85 152 25 85 85 109 96 85 85 194 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:34:00,229 DEBUG RFM2Pi 139326 NEW FRAME : OK 15 49 253 85 85 134 126 222 80 211 85 209 85 85 85 132 25 85 85 109 96 85 85 194 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:34:10,130 DEBUG RFM2Pi 139329 NEW FRAME : OK 15 48 253 85 85 155 126 208 80 211 85 208 85 85 85 128 25 85 85 108 96 85 85 194 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:34:20,132 DEBUG RFM2Pi 139332 NEW FRAME : OK 15 51 253 85 85 134 126 213 80 208 85 214 85 85 85 140 25 85 85 108 96 85 85 205 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:34:30,016 DEBUG RFM2Pi 139335 NEW FRAME : OK 15 50 253 85 85 155 126 40 80 211 85 208 85 85 85 136 25 85 85 111 96 85 85 205 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:34:40,030 DEBUG RFM2Pi 139338 NEW FRAME : OK 15 61 253 85 85 144 126 44 80 211 85 208 85 85 85 180 25 85 85 111 96 85 85 204 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:34:49,951 DEBUG RFM2Pi 139341 NEW FRAME : OK 15 60 253 85 85 148 126 32 80 208 85 209 85 85 85 177 25 85 85 111 96 85 85 204 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:34:59,863 DEBUG RFM2Pi 139344 NEW FRAME : OK 15 63 253 85 85 147 126 38 80 208 85 209 85 85 85 189 25 85 85 110 96 85 85 204 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:35:09,860 DEBUG RFM2Pi 139347 NEW FRAME : OK 15 62 253 85 85 233 126 37 80 211 85 208 85 85 85 185 25 85 85 110 96 85 85 207 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:35:19,836 DEBUG RFM2Pi 139350 NEW FRAME : OK 15 57 253 85 85 145 126 59 80 210 85 211 85 85 85 165 25 85 85 110 96 85 85 207 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:35:29,848 DEBUG RFM2Pi 139353 NEW FRAME : OK 15 56 253 85 85 157 126 56 80 221 85 211 85 85 85 161 25 85 85 105 96 85 85 207 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:35:59,823 DEBUG RFM2Pi 139360 NEW FRAME : OK 15 37 253 85 85 237 126 61 80 221 85 211 85 85 85 170 25 85 85 104 96 85 85 201 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:36:39,871 DEBUG RFM2Pi 139369 NEW FRAME : OK 15 33 253 85 85 251 126 56 80 211 85 208 85 85 85 90 24 85 85 107 96 85 85 200 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:36:49,793 DEBUG RFM2Pi 139372 NEW FRAME : OK 15 32 253 85 85 252 126 39 80 221 85 211 85 85 85 71 24 85 85 106 96 85 85 200 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:36:59,792 DEBUG RFM2Pi 139375 NEW FRAME : OK 15 35 253 85 85 244 126 33 80 210 85 208 85 85 85 67 24 85 85 106 96 85 85 203 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:37:09,796 DEBUG RFM2Pi 139378 NEW FRAME : OK 15 34 253 85 85 247 126 34 80 211 85 208 85 85 85 79 24 85 85 21 96 85 85 203 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:37:19,888 DEBUG RFM2Pi 139381 NEW FRAME : OK 15 45 253 85 85 247 126 45 80 211 85 208 85 85 85 75 24 85 85 21 96 85 85 203 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:37:49,899 DEBUG RFM2Pi 139388 NEW FRAME : OK 15 46 253 85 85 243 126 25 80 211 85 209 85 85 85 124 24 85 85 20 96 85 85 245 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:38:09,802 DEBUG RFM2Pi 139393 NEW FRAME : OK 15 40 253 85 85 230 126 5 80 210 85 211 85 85 85 100 24 85 85 23 96 85 85 245 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:38:19,859 DEBUG RFM2Pi 139396 NEW FRAME : OK 15 43 253 85 85 224 126 27 80 221 85 211 85 85 85 96 24 85 85 23 96 85 85 244 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:38:29,878 DEBUG RFM2Pi 139399 NEW FRAME : OK 15 42 253 85 85 230 126 97 80 210 85 211 85 85 85 109 24 85 85 22 96 85 85 244 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:38:39,883 DEBUG RFM2Pi 139402 NEW FRAME : OK 15 213 253 85 85 248 126 119 80 211 85 208 85 85 85 105 24 85 85 22 96 85 85 244 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:38:49,892 DEBUG RFM2Pi 139405 NEW FRAME : OK 15 212 253 85 85 254 126 118 80 210 85 211 85 85 85 21 24 85 85 22 96 85 85 247 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:38:59,895 DEBUG RFM2Pi 139408 NEW FRAME : OK 15 215 253 85 85 249 126 115 80 210 85 208 85 85 85 22 24 85 85 17 96 85 85 247 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:39:08,575 DEBUG RFM2Pi 139410 NEW FRAME : OK 15 214 253 85 85 241 126 126 80 211 85 208 85 85 85 18 24 85 85 17 96 85 85 246 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:39:18,514 DEBUG RFM2Pi 139413 NEW FRAME : OK 15 209 253 85 85 251 126 121 80 211 85 208 85 85 85 30 24 85 85 17 96 85 85 246 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:39:28,535 DEBUG RFM2Pi 139416 NEW FRAME : OK 15 208 253 85 85 251 126 65 80 210 85 211 85 85 85 27 24 85 85 16 96 85 85 246 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:39:38,433 DEBUG RFM2Pi 139419 NEW FRAME : OK 15 211 253 85 85 249 126 168 81 221 85 211 85 85 85 7 24 85 85 16 96 85 85 241 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:39:48,335 DEBUG RFM2Pi 139422 NEW FRAME : OK 15 210 253 85 85 251 126 175 81 221 85 210 85 85 85 0 24 85 85 19 96 85 85 241 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:39:58,325 DEBUG RFM2Pi 139425 NEW FRAME : OK 15 221 253 85 85 254 126 173 81 221 85 210 85 85 85 12 24 85 85 19 96 85 85 241 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:40:08,231 DEBUG RFM2Pi 139428 NEW FRAME : OK 15 220 253 85 85 241 126 173 81 221 85 210 85 85 85 9 24 85 85 19 96 85 85 240 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:40:18,217 DEBUG RFM2Pi 139431 NEW FRAME : OK 15 223 253 85 85 254 126 169 81 221 85 210 85 85 85 53 24 85 85 18 96 85 85 240 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:40:28,135 DEBUG RFM2Pi 139434 NEW FRAME : OK 15 222 253 85 85 254 126 174 81 210 85 211 85 85 85 54 24 85 85 18 96 85 85 240 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:40:38,133 DEBUG RFM2Pi 139437 NEW FRAME : OK 15 217 253 85 85 250 126 175 81 210 85 211 85 85 85 50 24 85 85 18 96 85 85 243 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:40:48,066 DEBUG RFM2Pi 139440 NEW FRAME : OK 15 216 253 85 85 224 126 169 81 210 85 211 85 85 85 63 24 85 85 29 96 85 85 243 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:40:57,981 DEBUG RFM2Pi 139443 NEW FRAME : OK 15 219 253 85 85 225 126 169 81 210 85 211 85 85 85 59 24 85 85 29 96 85 85 242 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:41:07,996 DEBUG RFM2Pi 139446 NEW FRAME : OK 15 218 253 85 85 239 126 168 81 210 85 211 85 85 85 36 24 85 85 28 96 85 85 242 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:41:17,909 DEBUG RFM2Pi 139449 NEW FRAME : OK 15 197 253 85 85 224 126 171 81 210 85 210 85 85 85 32 24 85 85 28 96 85 85 242 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:41:27,906 DEBUG RFM2Pi 139452 NEW FRAME : OK 15 196 253 85 85 235 126 21 81 221 85 210 85 85 85 45 24 85 85 28 96 85 85 253 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:41:37,811 DEBUG RFM2Pi 139455 NEW FRAME : OK 15 199 253 85 85 145 126 3 86 220 85 221 85 85 85 47 24 85 85 31 96 85 85 253 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:41:47,723 DEBUG RFM2Pi 139458 NEW FRAME : OK 15 198 253 85 85 159 126 17 86 221 85 221 85 85 85 40 24 85 85 31 96 85 85 253 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:41:57,731 DEBUG RFM2Pi 139461 NEW FRAME : OK 15 193 253 85 85 159 126 99 86 210 85 210 85 85 85 42 24 85 85 31 96 85 85 252 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:42:07,676 DEBUG RFM2Pi 139464 NEW FRAME : OK 15 192 253 85 85 134 126 127 86 210 85 211 85 85 85 212 24 85 85 30 96 85 85 252 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:42:17,580 DEBUG RFM2Pi 139467 NEW FRAME : OK 15 195 253 85 85 154 126 117 86 221 85 210 85 85 85 214 24 85 85 30 96 85 85 255 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:42:27,566 DEBUG RFM2Pi 139470 NEW FRAME : OK 15 194 253 85 85 154 126 60 86 210 85 210 85 85 85 211 24 85 85 25 96 85 85 255 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:42:37,488 DEBUG RFM2Pi 139473 NEW FRAME : OK 15 205 253 85 85 155 126 186 86 211 85 211 85 85 85 221 24 85 85 25 96 85 85 255 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:42:47,395 DEBUG RFM2Pi 139476 NEW FRAME : OK 15 204 253 85 85 135 126 84 81 210 85 211 85 85 85 222 24 85 85 25 96 85 85 254 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:42:57,421 DEBUG RFM2Pi 139479 NEW FRAME : OK 15 207 253 85 85 143 126 64 81 210 85 211 85 85 85 219 24 85 85 24 96 85 85 254 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:43:07,306 DEBUG RFM2Pi 139482 NEW FRAME : OK 15 206 253 85 85 143 126 125 81 210 85 211 85 85 85 196 24 85 85 24 96 85 85 254 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:43:17,298 DEBUG RFM2Pi 139485 NEW FRAME : OK 15 201 253 85 85 137 126 96 81 210 85 211 85 85 85 193 24 85 85 24 96 85 85 249 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:43:27,187 DEBUG RFM2Pi 139488 NEW FRAME : OK 15 200 253 85 85 142 126 132 86 210 85 211 85 85 85 194 24 85 85 27 96 85 85 249 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:43:37,181 DEBUG RFM2Pi 139491 NEW FRAME : OK 15 203 253 85 85 142 126 54 86 210 85 210 85 85 85 204 24 85 85 27 96 85 85 248 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:43:47,077 DEBUG RFM2Pi 139494 NEW FRAME : OK 15 202 253 85 85 137 126 52 86 220 85 221 85 85 85 201 24 85 85 27 96 85 85 248 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:43:57,089 DEBUG RFM2Pi 139497 NEW FRAME : OK 15 245 253 85 85 139 126 53 86 221 85 221 85 85 85 203 24 85 85 26 96 85 85 248 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:44:07,013 DEBUG RFM2Pi 139500 NEW FRAME : OK 15 244 253 85 85 137 126 11 86 221 85 221 85 85 85 245 24 85 85 26 96 85 85 251 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:44:16,999 DEBUG RFM2Pi 139503 NEW FRAME : OK 15 247 253 85 85 142 126 9 86 222 85 223 85 85 85 246 24 85 85 5 96 85 85 251 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:44:26,955 DEBUG RFM2Pi 139506 NEW FRAME : OK 15 246 253 85 85 142 126 14 86 223 85 223 85 85 85 240 24 85 85 5 96 85 85 251 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:44:36,868 DEBUG RFM2Pi 139509 NEW FRAME : OK 15 241 253 85 85 140 126 15 86 220 85 220 85 85 85 242 24 85 85 5 96 85 85 250 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:44:46,770 DEBUG RFM2Pi 139512 NEW FRAME : OK 15 240 253 85 85 182 126 12 86 220 85 220 85 85 85 255 24 85 85 4 96 85 85 250 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:44:56,767 DEBUG RFM2Pi 139515 NEW FRAME : OK 15 243 253 85 85 139 126 2 86 220 85 220 85 85 85 249 24 85 85 4 96 85 85 229 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:45:06,678 DEBUG RFM2Pi 139518 NEW FRAME : OK 15 242 253 85 85 181 126 3 86 220 85 221 85 85 85 250 24 85 85 7 96 85 85 229 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:45:16,664 DEBUG RFM2Pi 139521 NEW FRAME : OK 15 253 253 85 85 182 126 0 86 223 85 220 85 85 85 228 24 85 85 7 96 85 85 229 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:45:26,559 DEBUG RFM2Pi 139524 NEW FRAME : OK 15 252 253 85 85 189 126 0 86 223 85 220 85 85 85 230 24 85 85 7 96 85 85 228 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:45:36,547 DEBUG RFM2Pi 139527 NEW FRAME : OK 15 255 253 85 85 180 126 0 86 220 85 221 85 85 85 227 24 85 85 6 96 85 85 228 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:45:46,456 DEBUG RFM2Pi 139530 NEW FRAME : OK 15 254 253 85 85 182 126 3 86 223 85 220 85 85 85 237 24 85 85 6 96 85 85 228 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:45:56,467 DEBUG RFM2Pi 139533 NEW FRAME : OK 15 249 253 85 85 177 126 3 86 223 85 223 85 85 85 239 24 85 85 6 96 85 85 231 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:46:06,380 DEBUG RFM2Pi 139536 NEW FRAME : OK 15 248 253 85 85 176 126 3 86 223 85 223 85 85 85 232 24 85 85 1 96 85 85 231 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:46:16,285 DEBUG RFM2Pi 139539 NEW FRAME : OK 15 251 253 85 85 139 126 3 86 220 85 220 85 85 85 234 24 85 85 1 96 85 85 230 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:46:26,211 DEBUG RFM2Pi 139542 NEW FRAME : OK 15 250 253 85 85 245 126 2 86 221 85 221 85 85 85 148 24 85 85 0 96 85 85 230 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:46:36,210 DEBUG RFM2Pi 139545 NEW FRAME : OK 15 229 253 85 85 194 126 13 86 220 85 221 85 85 85 145 24 85 85 0 96 85 85 230 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:46:46,127 DEBUG RFM2Pi 139548 NEW FRAME : OK 15 228 253 85 85 194 126 13 86 221 85 221 85 85 85 147 24 85 85 0 96 85 85 225 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:46:56,039 DEBUG RFM2Pi 139551 NEW FRAME : OK 15 231 253 85 85 192 126 12 86 220 85 221 85 85 85 156 24 85 85 3 96 85 85 225 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:47:06,046 DEBUG RFM2Pi 139554 NEW FRAME : OK 15 230 253 85 85 192 126 12 86 223 85 220 85 85 85 158 24 85 85 3 96 85 85 225 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:47:15,954 DEBUG RFM2Pi 139557 NEW FRAME : OK 15 225 253 85 85 205 126 12 86 220 85 221 85 85 85 152 24 85 85 3 96 85 85 224 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:47:25,865 DEBUG RFM2Pi 139560 NEW FRAME : OK 15 224 253 85 85 207 126 15 86 221 85 221 85 85 85 133 24 85 85 2 96 85 85 224 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:47:35,860 DEBUG RFM2Pi 139563 NEW FRAME : OK 15 227 253 85 85 205 126 14 86 223 85 220 85 85 85 135 24 85 85 2 96 85 85 227 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:47:45,744 DEBUG RFM2Pi 139566 NEW FRAME : OK 15 226 253 85 85 192 126 9 86 220 85 221 85 85 85 129 24 85 85 13 96 85 85 227 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:47:55,740 DEBUG RFM2Pi 139569 NEW FRAME : OK 15 237 253 85 85 192 126 8 86 220 85 221 85 85 85 130 24 85 85 13 96 85 85 227 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:48:05,657 DEBUG RFM2Pi 139572 NEW FRAME : OK 15 236 253 85 85 192 126 11 86 223 85 220 85 85 85 140 24 85 85 13 96 85 85 226 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:48:15,641 DEBUG RFM2Pi 139575 NEW FRAME : OK 15 239 253 85 85 192 126 10 86 223 85 223 85 85 85 137 24 85 85 12 96 85 85 226 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:48:25,548 DEBUG RFM2Pi 139578 NEW FRAME : OK 15 238 253 85 85 199 126 53 86 223 85 223 85 85 85 139 24 85 85 12 96 85 85 237 84 85 85 85 85 85 85 117 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:48:35,554 DEBUG RFM2Pi 139581 NEW FRAME : OK 15 233 253 85 85 196 126 53 86 223 85 223 85 85 85 181 24 85 85 12 96 85 85 237 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:48:45,442 DEBUG RFM2Pi 139584 NEW FRAME : OK 15 232 253 85 85 219 126 55 86 223 85 223 85 85 85 182 24 85 85 15 96 85 85 237 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:48:55,387 DEBUG RFM2Pi 139587 NEW FRAME : OK 15 235 253 85 85 199 126 55 86 222 85 223 85 85 85 176 24 85 85 15 96 85 85 236 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:49:05,312 DEBUG RFM2Pi 139590 NEW FRAME : OK 15 234 253 85 85 199 126 55 86 223 85 220 85 85 85 178 24 85 85 14 96 85 85 236 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:49:15,255 DEBUG RFM2Pi 139593 NEW FRAME : OK 15 149 253 85 85 196 126 55 86 220 85 220 85 85 85 191 24 85 85 14 96 85 85 236 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:49:25,268 DEBUG RFM2Pi 139596 NEW FRAME : OK 15 148 253 85 85 197 126 54 86 220 85 220 85 85 85 185 24 85 85 14 96 85 85 239 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:49:35,184 DEBUG RFM2Pi 139599 NEW FRAME : OK 15 151 253 85 85 218 126 54 86 223 85 220 85 85 85 186 24 85 85 9 96 85 85 239 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:49:45,093 DEBUG RFM2Pi 139602 NEW FRAME : OK 15 150 253 85 85 197 126 49 86 220 85 220 85 85 85 164 24 85 85 9 96 85 85 238 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:49:55,110 DEBUG RFM2Pi 139605 NEW FRAME : OK 15 145 253 85 85 198 126 48 86 223 85 220 85 85 85 166 24 85 85 8 96 85 85 238 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:50:05,113 DEBUG RFM2Pi 139608 NEW FRAME : OK 15 144 253 85 85 199 126 48 86 223 85 220 85 85 85 163 24 85 85 8 96 85 85 238 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:51:35,073 DEBUG RFM2Pi 139627 NEW FRAME : OK 15 155 253 85 85 43 126 48 86 222 85 223 85 85 85 94 27 85 85 53 96 85 85 234 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:51:45,079 DEBUG RFM2Pi 139630 NEW FRAME : OK 15 154 253 85 85 206 126 51 86 223 85 220 85 85 85 91 27 85 85 52 96 85 85 234 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:51:55,091 DEBUG RFM2Pi 139633 NEW FRAME : OK 15 133 253 85 85 153 126 51 86 223 85 220 85 85 85 69 27 85 85 52 96 85 85 234 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:52:05,107 DEBUG RFM2Pi 139636 NEW FRAME : OK 15 132 253 85 85 153 126 51 86 222 85 222 85 85 85 70 27 85 85 55 96 85 85 149 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:52:25,108 DEBUG RFM2Pi 139641 NEW FRAME : OK 15 134 253 85 85 145 126 51 86 217 85 222 85 85 85 66 27 85 85 55 96 85 85 148 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:52:45,113 DEBUG RFM2Pi 139646 NEW FRAME : OK 15 128 253 85 85 157 126 51 86 222 85 223 85 85 85 73 27 85 85 54 96 85 85 148 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:52:55,117 DEBUG RFM2Pi 139649 NEW FRAME : OK 15 131 253 85 85 146 126 51 86 222 85 223 85 85 85 74 27 85 85 54 96 85 85 151 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:53:05,140 DEBUG RFM2Pi 139652 NEW FRAME : OK 15 130 253 85 85 146 126 51 86 222 85 223 85 85 85 116 27 85 85 49 96 85 85 151 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:53:15,073 DEBUG RFM2Pi 139655 NEW FRAME : OK 15 141 253 85 85 159 126 50 86 217 85 222 85 85 85 118 27 85 85 49 96 85 85 150 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:53:23,847 DEBUG RFM2Pi 139657 NEW FRAME : OK 15 140 253 85 85 131 126 50 86 216 85 217 85 85 85 115 27 85 85 48 96 85 85 150 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:53:33,814 DEBUG RFM2Pi 139660 NEW FRAME : OK 15 143 253 85 85 130 126 50 86 216 85 217 85 85 85 125 27 85 85 48 96 85 85 150 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:53:43,725 DEBUG RFM2Pi 139663 NEW FRAME : OK 15 142 253 85 85 130 126 51 86 217 85 222 85 85 85 126 27 85 85 48 96 85 85 145 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:53:53,714 DEBUG RFM2Pi 139666 NEW FRAME : OK 15 137 253 85 85 130 126 51 86 222 85 222 85 85 85 120 27 85 85 51 96 85 85 145 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:54:03,647 DEBUG RFM2Pi 139669 NEW FRAME : OK 15 136 253 85 85 134 126 51 86 222 85 223 85 85 85 122 27 85 85 51 96 85 85 145 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:54:13,581 DEBUG RFM2Pi 139672 NEW FRAME : OK 15 139 253 85 85 135 126 51 86 217 85 222 85 85 85 103 27 85 85 50 96 85 85 144 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:54:23,492 DEBUG RFM2Pi 139675 NEW FRAME : OK 15 138 253 85 85 143 126 51 86 216 85 217 85 85 85 97 27 85 85 50 96 85 85 144 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:54:33,508 DEBUG RFM2Pi 139678 NEW FRAME : OK 15 181 253 85 85 129 126 51 86 216 85 217 85 85 85 98 27 85 85 50 96 85 85 147 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:54:43,408 DEBUG RFM2Pi 139681 NEW FRAME : OK 15 180 253 85 85 131 126 51 86 216 85 217 85 85 85 108 27 85 85 61 96 85 85 147 84 85 85 85 85 85 85 120 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:54:53,402 DEBUG RFM2Pi 139684 NEW FRAME : OK 15 183 253 85 85 132 126 51 86 216 85 217 85 85 85 110 27 85 85 61 96 85 85 147 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:55:03,304 DEBUG RFM2Pi 139687 NEW FRAME : OK 15 182 253 85 85 134 126 51 86 216 85 217 85 85 85 107 27 85 85 61 96 85 85 146 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:55:13,293 DEBUG RFM2Pi 139690 NEW FRAME : OK 15 177 253 85 85 141 126 51 86 216 85 217 85 85 85 21 27 85 85 60 96 85 85 146 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:55:23,214 DEBUG RFM2Pi 139693 NEW FRAME : OK 15 176 253 85 85 135 126 50 86 216 85 217 85 85 85 22 27 85 85 60 96 85 85 157 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:55:33,107 DEBUG RFM2Pi 139696 NEW FRAME : OK 15 179 253 85 85 131 126 50 86 222 85 223 85 85 85 16 27 85 85 63 96 85 85 157 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:55:43,112 DEBUG RFM2Pi 139699 NEW FRAME : OK 15 178 253 85 85 140 126 50 86 217 85 222 85 85 85 29 27 85 85 63 96 85 85 157 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:55:52,970 DEBUG RFM2Pi 139702 NEW FRAME : OK 15 189 253 85 85 143 126 61 86 216 85 217 85 85 85 31 27 85 85 63 96 85 85 156 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:56:03,020 DEBUG RFM2Pi 139705 NEW FRAME : OK 15 188 253 85 85 181 126 61 86 217 85 223 85 85 85 25 27 85 85 62 96 85 85 156 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:56:12,935 DEBUG RFM2Pi 139708 NEW FRAME : OK 15 191 253 85 85 142 126 61 86 217 85 222 85 85 85 26 27 85 85 62 96 85 85 156 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:56:22,846 DEBUG RFM2Pi 139711 NEW FRAME : OK 15 190 253 85 85 138 126 61 86 217 85 223 85 85 85 4 27 85 85 57 96 85 85 159 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:56:32,852 DEBUG RFM2Pi 139714 NEW FRAME : OK 15 185 253 85 85 143 126 61 86 219 85 217 85 85 85 1 27 85 85 57 96 85 85 159 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:56:42,771 DEBUG RFM2Pi 139717 NEW FRAME : OK 15 184 253 85 85 130 126 61 86 216 85 217 85 85 85 3 27 85 85 57 96 85 85 158 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:56:52,670 DEBUG RFM2Pi 139720 NEW FRAME : OK 15 187 253 85 85 128 126 60 86 216 85 222 85 85 85 13 27 85 85 56 96 85 85 158 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:57:02,660 DEBUG RFM2Pi 139723 NEW FRAME : OK 15 186 253 85 85 130 126 60 86 216 85 217 85 85 85 14 27 85 85 56 96 85 85 158 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-43)
2020-12-14 16:57:12,567 DEBUG RFM2Pi 139726 NEW FRAME : OK 15 165 253 85 85 131 126 60 86 216 85 217 85 85 85 8 27 85 85 59 96 85 85 153 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
2020-12-14 16:57:22,555 DEBUG RFM2Pi 139729 NEW FRAME : OK 15 164 253 85 85 134 126 60 86 216 85 217 85 85 85 53 27 85 85 59 96 85 85 153 84 85 85 85 85 85 85 108 80 101 32 101 32 84 85 85 85 (-44)
[Formatted for clarity - Moderator - RW]
@rgooch
For future reference, when posting code or output, please put 3 ‘backticks’ (normally found at the [top left of the keyboard] (typing - How do I type the tick and backtick characters on Windows? - Super User)) on a line of their own before the code, and 3 more backticks on a line of their own after the code.
code
If it is something like php you can add a language identifier after the first 3 backticks: ```php
or even ```text
if you don’t want any language markup applied.
OK, noted. I actually tried to upload the file but as a new user I can’t do that
Perhaps when one purchases something from the shop a signup code could be generated that can be used to indicate “not spammer”?
Try it again, Rich. You should be good to go now.
Pasting the text is the best way anyway.
Now you can see this output, the next thing is to monitor your feeds and try and correlate gaps with gaps in the debug log. As it stands this log looks like what you’d expect to see, data coming in at just under 10s intervals except for this burst where there are gaps.
next thing then is to find a full log section around the time where this identifies gaps.
What this tells you is that it may be an RF issue (at first glance) as there is apparently no new frame received.
@rgooch it would be interesting to see a screenshot of the one of the EmonTx feeds with a tick in the show missing data checkbox at the top (in the graph module). That might give an idea if there’s a pattern to the data loss. Underneath the graph in the ‘feeds in view’ box, it also shows a % of data points missing under the quality heading.