Ecodan pump speed settings

I was wondering if anyone has gotten to the bottom of the Ecodan FTC’s ability to control pump speeds.

Ecodans rely on external circulation pumps. There are settings in the service menu for pump speeds for heating and DHW. On my system changing these doesn’t do anything.

I’m assuming on the Ecodan pre-plumbed cylinders this does work?
If it does how does it work? PWM or some other way?
Is there any way to get this working with other pumps?

I wouldn’t be bothered if I just needed a single pump speed as I can just set this on the pump but I am wondering about experimenting with different speeds for the heating and hot water as the circuits are very different I would have thought there would be benefit in the ability to have different speeds.
Anyone have any experience of this?

A few of us were playing with it back in March

Thanks @MyForest that is interesting but my problem is more fundamental than that.
Changing the speed setting on the FTC6 controller doesn’t actually seem to change the pump speed.

How are your, @mjr and @Rachel pumps connected to the FTC?
My pump has its power coming from the FTC for in and off but has a separate PWM cable that isn’t connected to anything. I can’t work out how the FTC varies pump speed (when it works).

My main pump seems to be connected only with a power cable, but I didn’t wire it and haven’t checked the markings, so that cable might contain more cores for all I know. It has its own on-pump speed control buttons.

I can’t figure out what the FTC5 pump speed setting does, if anything.

My two pumps are connected through a Heatmiser UH6 and hence the FTC6 pump outputs are just controlling relays.

The Wilo pumps do have a PWM connector but they are unused.

I’ve come across this video that suggests it works in some circumstances, you can hear the pump speed change when they change the pump speed setting.

1 Like

When I was converting my system to auto adaptation etc. which required some rewiring of the FTC6, I sent a query to Mitsubishi asking …

“The pump outputs for Zones 1& 2 - are they 240v or are they PWM etc. for pump speed control?”

The response I got back was …

“All the pump outputs; Out1, Out2, Out3, Out13 are 240v.”

1 Like

So has anyone got a set up where the controller pump speed settings change their pump speed?

Hi Andrew,
yes - sort of! I got interested in the pumps, because my system tends to have a low temperature drop through the radiators, so I figured that dropping the flow speed would be a good thing to do. I found that it was a bit more complicated than that.
I have an Ecodan with the Mitsubishi pre-plumbed standard cylinder. I have 3 pumps, one of which can be changed from the FTC5 controller.
I found the manual for the cylinder very informative. Having studied it, I finally understood what all the spaghetti on the cylinder was actually doing, and why there are 3 pumps.
Here’s a schematic of my system…

I have highlighted the 3 pumps in red.

  1. Grundfos UPM GEO 25-85 130 which pumps the heat pump primary circuit
  2. Grundfos UPM3 AUTO 25-70 130 ZZZ which pumps the radiator circuit
  3. Grundfos UPS0 15-60 CIL2 which pumps the hot water circuit
    My primary pump has both a power cable, and a separate pulse width modulation cable from the FTC5.
    So if I navigate through the menus on the FTC5, to alter the pump speed setting between 1 and 5, then only this pump is affected.
    My other pumps only have power cables. The hot water pump has 3 possible speed settings, which can be selected using a switch on housing. But my cylinder manual says that it should be set to speed setting II to ensure optimum DHW heating performance, so I never tried altering that.
    The setting on the pump on the radiator circuit can also be adjusted manually, by pressing a button on the front of the pump. This has at least 10 possible modes.
    It was at this point that I twigged that my system has a “low loss header” (which explained why I have 3 pumps). I have watched the videos on the Heat Geeks website, but I still don’t really understand why my system has a LLH. All my rads are on one circuit, and there’s no under floor heating, so I don’t really understand what good it does. As far as I can see, it just makes the system more complicated, and potentially less efficient. eg. if the pump on the HP circuit is on full power, but the rad pump is on low power, then most of the flow from the HP can take a short cut through the LLH, and go back to the HP return without ever seeing a radiator. This doesn’t sound like a great idea to me. Conversely, if the HP pump is pumping less flow than the rad pump, then the return flow from the radiators can take a short circuit through the LLH. There it will mix with the weak flow out of the HP, and drop the temp of the flow going to the rads, which also seems like a bad idea to me.
    As far as I can see, for my system, the ideal would be to balance the HP pump and the rad pump, so that there is zero flow taking a short cut through the LLH. In the end, I fitted 4 thermometers (1 on each the 4 pipes connected to the LLH), and recorded them on the OEM system. I set the HP pump to 5 on the FTC5, and then messed around with the rad pump settings until I found one which gave HP flow temp = rad circuit inlet temp, and HP return temp = rad circuit exit temp. Then I repeated the experiment with the HP pump on setting 4 etc. Whilst doing all this, I was also trying to measure the COP. The variations in the COP were not huge (roughly 10%). But they seemed to peak when the temperatures across the LLH were balanced. It was all a bit time consuming in the end - and my initial idea of just tweaking the pump speed on the control panel seems quite naive in retrospect.
    I don’t like complexity for no reason, and I don’t really see what the LLH contributes to my system. To be honest, I reckon the design of my whole system is rubbish. I am thinking about draining it down, fitting larger K3 radiators downstairs, anti freeze valves, and bypassing the LLH completely.
1 Like

Where does the PWM cable come from within the FTC5 and does the power also come from there?

1 Like

Thanks @richb99999 for that explanation.

My installer couldn’t get stock of an Ecodan cylinder so sourced a different cylinder and reading this I’m glad they did as they’ve set it up with a single pump and no other complexity like LLH.
I vaguely remember reading somewhere that it might be possible to not plumb in the LLH on the Ecodan cylinders but not sure how that would work if there are multiple pumps.

Do you know where the PWM cable wires in to the FTC5?

I have always believed that the software adjustment is only for adapting the pump speed to the system hydraulic requirements. I don’t think there is any feedback control (dt etc) to vary the speed to adapt at any one point in time. Maybe on FTC7?

Yes it is just a fixed value set at the controller but the main advantage from being able to set it is that you can have different pump speeds for heating vs DHW.

However I still don’t know how it can actually be set up to work. Hoping someone who it does work for can let me know how their pump is connected.

Another advantage is that it seems to have 5 levels whereas my pump control has only 3 so might allow for more fine tuning of flow rates.

Apologies for the slow response - holidays.

Here’s a photo of where the PWM cable plugs into my FTC5 (I’m 99% certain this is right, but my installer doesn’t seem to have shortened any of the cables, so I have a mass of spaghetti in there).


…and here’s an excerpt from the pump manual…

The circuit board marking at the top implies you have an FTC6!

Looking at my manual, that connector is CNPWM which sounds promising but there’s no mention of it anywhere than on pictures of the board.

There’s another 3-pin connector above it labelled CN3C but that is also similarly obscure.

Yes it looks like CNPWM is the PWM connector and CN01 the power to the pump.
I have a PWM connector on my pump I just don’t know if it is compatible if I wired it up.

@richb99999 does your pump have any specs for the PWM pins?
Maybe I could use this to compare for my own pump.

Hi,
The manual for my pump is here…
https://product-selection.grundfos.com/products/up-oem/upm2-oem?tab=documentation
…then it’s [UPM2, UPM GEO, UPM2K, Circulator pumps (Data booklet)
There seems to be some info about the PWM side of things

My pumps are Wilo Para and seem to conform to the same spec.

Just need a cable with the correct connectors on each end now; probably simpler said than done.

1 Like