Hello everyone,
I am an HVAC service engineer from Slovakia, leading a service team working mainly with Daikin air-to-water heat pumps.
Over the past two heating seasons, we have been investigating recurring 89-01 faults and 89-03 warnings on several Daikin Altherma LT-CB systems, particularly those equipped with ERLQ011–016CA outdoor units.
With the beginning of the current heating season, the problem has started to reappear. Despite extensive troubleshooting and communication with the manufacturer’s technical support, we have not yet established a reliable diagnostic procedure or a common root cause.
I would appreciate any experience from other service engineers who have encountered similar problems.
Current case
Outdoor unit: ERLQ011CAW1
Indoor unit: EHVX11S26CB9W
Refrigerant: R410A
Error codes: 89-01 / 89-03
Diagnostic equipment: Daikin D-checker and independent Testo pressure and temperature probes
The unit generally operates in heating mode, but intermittently generates freeze protection warnings during defrost. In some cases, the compressor is locked out and heating continues using the electric backup heater.
1. Recorded fault conditions
During approximately 21 hours of continuous monitoring, we recorded 15 defrost cycles, five of which were associated with code 89.
The most critical recorded event:
| Parameter | Value |
| Indoor refrigerant liquid thermistor R3T | −27.0°C |
| Entering water temperature R4T | 27.7°C |
| Leaving water temperature R1T (after PHE) | 27.2°C |
| Leaving water temperature R2T (after BUH) | 27.7°C |
| Water flow rate | 28.3 l/min |
| Compressor frequency | 36 rps |
| EEV commanded position | 400 pulses |
The compressor stopped immediately after the fault was recorded.
We also recorded another defrost during which R3T reached −23.5°C without triggering code 89. During that cycle, entering water temperature was approximately 44°C and the three-way valve was in the DHW position.
Interestingly, the refrigerant temperature remained below −20°C for considerably longer during this successful defrost than during some of the failed defrosts.
This suggests that the protection algorithm may involve additional parameters rather than a fixed R3T temperature threshold alone.
2. Thermistor verification
We have performed the following checks:
Outdoor heat exchanger thermistor R4T: checked, no fault identified.
Indoor refrigerant thermistor R3T: mechanical installation and thermal contact checked.
R3T resistance-temperature characteristic: checked.
Indoor R3T replaced with a new original thermistor for testing.
After replacing R3T, independent Testo measurements during defrost recorded:
Testo refrigerant pipe surface temperature: −19.8°C.
New Daikin R3T reading: −16.1°C.
The Testo clamp probe was installed close to the original thermistor on the same pipe.
The fault subsequently returned, with the new R3T recording temperatures as low as −27°C.
Therefore, the abnormally low refrigerant pipe temperature cannot simply be attributed to an incorrect reading from the original R3T thermistor.
3. Suspicious electronic expansion valve behaviour
During heating operation, we have repeatedly observed the following pattern in D-checker:
The commanded EEV position progressively decreases.
The reported evaporating pressure decreases.
Calculated suction superheat increases.
Water-side heating capacity decreases.
One example, with the defrost flag still OFF:
| Parameter | Initial condition | 140 seconds later |
| EEV position | 264 pulses | 58 pulses |
| Reported pressure | 5.2 bar | 1.7 bar |
| Reported saturation temperature | −6.2°C | −31.1°C |
| Calculated suction superheat | 6.8 K | 33.7 K |
| Estimated water-side heating capacity | 5.0 kW | 2.4 kW |
In other heating cycles, calculated superheat exceeded 35–40 K while the EEV command was approximately 45–60 pulses.
We are investigating whether this behaviour is related to:
Mechanical sticking or incorrect positioning of the EEV.
Incorrect sensor input or EEV control logic.
A refrigerant circuit restriction.
Insufficient refrigerant charge.
A specific control sequence before defrost.
Internal leakage through the four-way reversing valve.
In at least two previous service cases involving similar faults, the expansion valve was identified as the cause. However, we cannot yet confirm that the current case has the same root cause.
Further independent pressure and temperature measurements are planned to distinguish between these possibilities.
4. D-checker outdoor unit data freezing
Another unusual issue is that several outdoor unit diagnostic channels occasionally stop updating for extended periods, sometimes for several hours.
The affected channels include:
Outdoor ambient temperature.
Outdoor heat exchanger temperature.
Suction and discharge temperatures.
Liquid pipe temperature.
Refrigerant pressure and corresponding saturation temperature.
Meanwhile, compressor frequency, EEV commands, four-way valve status and indoor unit measurements continue to update.
We do not yet know whether this is a D-checker communication/logging issue or a problem affecting the outdoor PCB diagnostic data.
Consequently, the reported refrigerant pressure and calculated superheat values must be treated with caution until independently verified.
5. Questions for other service engineers
Have you encountered recurring 89-01 or 89-03 faults on Daikin Altherma LT-CB systems, particularly ERLQ011–016CA models?
What was the actual root cause, and which repair permanently resolved the problem?
Have you experienced mechanically sticking electronic expansion valves on these outdoor units, even when the electrical windings and commanded valve positions appeared normal?
Have you observed EEV closing commands while actual suction superheat was increasing? Is there a known pre-defrost control sequence that could explain this behaviour?
Does anyone know the exact 89-03 protection algorithm for this generation?
The service manual ESIE14-01C, page 59, refers to excessively low Te during defrost and an R2T water temperature below 6°C. However, it does not specify the exact Te threshold, time delay or how Te is determined.
Are there any known technical service bulletins, problematic production batches of EEVs or reversing valves, revised spare parts, or firmware updates related to these faults?
Has anyone experienced similar frozen outdoor unit sensor data when using D-checker?
We are particularly interested in confirmed field repairs rather than trial-and-error component replacement.
We have extensive D-checker logs and independent Testo measurements from several affected systems and can share anonymised data and graphs if required.
Any technical feedback or previous field experience would be greatly appreciated.
I will update this thread with further measurements and findings, hopefully including the confirmed root cause and a successful repair.
Thank you.
Best regards,
Peter
HVAC Service Engineer
Slovakia