Daikin Altherma, ESPAltherma & Home Assistant with OpenEnergyMonitor

Thanks to the efforts of @squarepeg77 and Dan from Daikin (thanks!), the cause of the R1T/R2T/R4T thermistor value differences has been traced to the tape heaters around the plate heat exchanger being activated as part of what seems to be a “belt and braces” anti-freezing policy by Daikin. Your friendly engineer can remove said link (5-7 on X7M) which is described in a Daikin technical bulletin for exactly this situation i.e. using 3rd party monitoring which relies on these sensors, which in my case got them to within 0.1C of each other.

So now I don’t need the offset! And I’m saving 66W while the circulation pump is running. Hurrah.

2 Likes