Hello,
Had Vaillant AT+ 7kW with buffer installed a couple of months ago.
6.3 kW heatloss in design (actual seems to be around 4.5 kW)
50C design flow temp at -2.9 with SCOP 3.65
All radiators were replaced to oversized (microbore 15mm only to radiators), around 10m run from ASHP to cylinder and buffer installed in garage.
1 zone, no TRV. DHW 250L to 48C once a day. Heating - constant temperature, no setback. Weather compensation. Active room mode. No short cycling. 4 lock shields are half closed in bedrooms, was too hot upstairs otherwise.
Combined COP was terrible at the beginning - lowest 2.2 with outdoor avg -2C, installer attributed this to defrosts but it didnât improve much when it became warmer outside - stayed around 2.5 - 3.0. This was with average indoor temperature 18-19C instead of design 20-21C.
There was about 6-7C difference in return temperatures measured on the buffer.
Brought it up with installer again, long story short - to reduce mixing in buffer, primary pump speed was reduced 1200->850lph (set to 50% on WizAI and the rest by adjusting physical valve), secondary pump speed was set to highest. Heat curve from 1 to 0.5-0.6.
This resulted in 3-4C return temps difference and COP improved - I saw 4 for the first time when it was +10 outside.
Now when temperatures dropped again it is around 3-3.5. Around 0.3-0.5 COP improvement.
Comparing to the Czech tables for 35 flow temperature / 35 compressor speed (this is what it is mostly running at) I should still be getting around 1 COP more. Pump speeds canât be adjusted further.
Are there any options left to improve efficiency, or my expectations are unrealistic and 1 COP difference can be explained by not having ideal conditions as presumed in Czech tables? Installer seems to have closed the case by now.
I lurked through various forum posts and there were several user stories for similar heatloss houses and same ASHP and microbore with no UFH that could achieve 5 with +10 outside while having indoor temperature in the 20Cs, above 3 at worst when cold.
Bills while on the best tariff seem to be on par with previous gas bills on an ancient Economy7 tariff, would probably be around 30% higher if I stayed.
Another issue is secondary pump on the highest speed generating a lot of background noise everywhere in the house (like a working bathroom extractor fan in the next room)
Thanks
* Havenwise is mentioned because it distorted average COP on graphs - was blasting at high temperatures or idle..