And here is the firmware I have running on my emonTx v.3
emonTxV3.4 Discrete Sampling
If AC-AC adapter is detected assume emonTx is also powered from adapter (jumper shorted) and take Real Power Readings and disable sleep mode to keep load on power supply constant
If AC-AC addapter is not detected assume powering from battereis / USB 5V AC sample is not present so take Apparent Power Readings and enable sleep mode
Transmitt values via RFM69CW radio
Part of the openenergymonitor.org project
Authors: Glyn Hudson & Trystan Lea
Builds upon JCW JeeLabs RF12 library and Arduino
Licence: GNU GPL V3
/*Recommended node ID allocation
-ID- -Node Type-
0 - Special allocation in JeeLib RFM12 driver - reserved for OOK use
1-4 - Control nodes
5-10 - Energy monitoring nodes
11-14 --Un-assigned --
15-16 - Base Station & logging nodes
17-30 - Environmental sensing nodes (temperature humidity etc.)
31 - Special allocation in JeeLib RFM12 driver - Node31 can communicate with nodes on any network group
Change Log:
v2.3 16/11/15 Change to unsigned long for pulse count and make default node ID 8 to avoid emonHub node decoder conflict & fix counting pulses faster than 110ms, strobed meter LED http://openenergymonitor.org/emon/node/11490
v2.2 12/11/15 Remove debug timming serial print code
v2.1 24/10/15 Improved timing so that packets are sent just under 10s, reducing resulting data gaps in feeds + default status code for no temp sensors of 3000 which reduces corrupt packets improving data reliability
V2.0 30/09/15 Update number of samples 1480 > 1662 to improve sampling accurancy: 1662 samples take 300 mS, which equates to 15 cycles @ 50 Hz or 18 cycles @ 60 Hz.
V1.9 25/08/15 Fix spurious pulse readings from RJ45 port when DS18B20 but no pulse counter is connected (enable internal pull-up)
V1.8 - 18/06/15 Increase max pulse width to 110ms
V1.7 - 12/06/15 Fix pulse count debounce issue & enable pulse count pulse temperature
V1.6 - Add support for multiple DS18B20 temperature sensors
V1.5 - Add interrupt pulse counting - simplify serial print debug
V1.4.1 - Remove filter settle routine as latest emonLib 19/01/15 does not require
V1.4 - Support for RFM69CW, DIP switches and battery voltage reading on emonTx V3.4
V1.3 - fix filter settle time to eliminate large inital reading
V1.2 - fix bug which caused Vrms to be returned as zero if CT1 was not connected
V1.1 - fix bug in startup Vrms calculation, startup Vrms startup calculation is now more accuratre
#define emonTxV3 // Tell emonLib this is the emonTx V3 - don't read Vcc assume Vcc = 3.3V as is always the case on emonTx V3 eliminates bandgap error and need for calibration http://harizanov.com/2013/09/thoughts-on-avr-adc-accuracy/
#define RF69_COMPAT 1 // Set to 1 if using RFM69CW or 0 is using RFM12B
#include <JeeLib.h>
ISR(WDT_vect) { Sleepy::watchdogEvent(); } // Attached JeeLib sleep function to Atmega328 watchdog -enables MCU to be put into sleep mode inbetween readings to reduce power consumption
#include "EmonLib.h" // Include EmonLib energy monitoring library
EnergyMonitor ct1, ct2, ct3, ct4;
#include "OneWire.h"
#include <DallasTemperature.h>
const byte version = 232; // firmware version divided by 10 e,g 16 = V1.6
//----------------------------emonTx V3 Settings---------------------------------------------------------------------------------------------------------------
const byte Vrms= 230; // Vrms for apparent power readings (when no AC-AC voltage sample is present)
const byte TIME_BETWEEN_READINGS = 10; //Time between readings
//http://openenergymonitor.org/emon/buildingblocks/calibration
const float Ical1= 90.9; // (2000 turns / 22 Ohm burden) = 90.9
const float Ical2= 90.9; // (2000 turns / 22 Ohm burden) = 90.9
const float Ical3= 90.9; // (2000 turns / 22 Ohm burden) = 90.9
const float Ical4= 16.67; // (2000 turns / 120 Ohm burden) = 16.67
float Vcal= 268.97; // (230V x 13) / (9V x 1.2) = 276.9 Calibration for UK AC-AC adapter 77DB-06-09
//float Vcal=276.9;
//const float Vcal= 260; // Calibration for EU AC-AC adapter 77DE-06-09
const float Vcal_USA= 130.0; //Calibration for US AC-AC adapter 77DA-10-09
boolean USA=FALSE;
const float phase_shift= 1.7;
const int no_of_samples= 1662;
const int no_of_half_wavelengths= 30;
const int timeout= 2000; //emonLib timeout
const int ACAC_DETECTION_LEVEL= 3000;
const byte min_pulsewidth= 110; // minimum width of interrupt pulse (default pulse output meters = 100ms)
const int TEMPERATURE_PRECISION= 11; //9 (93.8ms),10 (187.5ms) ,11 (375ms) or 12 (750ms) bits equal to resplution of 0.5C, 0.25C, 0.125C and 0.0625C
const byte MaxOnewire= 6;
#define ASYNC_DELAY 375 // DS18B20 conversion delay - 9bit requres 95ms, 10bit 187ms, 11bit 375ms and 12bit resolution takes 750ms
//----------------------------emonTx V3 hard-wired connections---------------------------------------------------------------------------------------------------------------
const byte LEDpin= 6; // emonTx V3 LED
const byte DS18B20_PWR= 19; // DS18B20 Power
const byte DIP_switch1= 8; // Voltage selection 230 / 110 V AC (default switch off 230V) - switch off D8 is HIGH from internal pullup
const byte DIP_switch2= 9; // RF node ID (default no chance in node ID, switch on for nodeID -1) switch off D9 is HIGH from internal pullup
const byte battery_voltage_pin= 7; // Battery Voltage sample from 3 x AA
const byte pulse_countINT= 1; // INT 1 / Dig 3 Terminal Block / RJ45 Pulse counting pin(emonTx V3.4) - (INT0 / Dig2 emonTx V3.2)
const byte pulse_count_pin= 3; // INT 1 / Dig 3 Terminal Block / RJ45 Pulse counting pin(emonTx V3.4) - (INT0 / Dig2 emonTx V3.2)
#define ONE_WIRE_BUS 5 // DS18B20 Data
//Setup DS128B20
OneWire oneWire(ONE_WIRE_BUS);
DallasTemperature sensors(&oneWire);
byte allAddress [MaxOnewire][8]; // 8 bytes per address
byte numSensors;
//-----------------------RFM12B / RFM69CW SETTINGS----------------------------------------------------------------------------------------------------
#define RF_freq RF12_433MHZ // Frequency of RF69CW module can be RF12_433MHZ, RF12_868MHZ or RF12_915MHZ. You should use the one matching the module you have.
byte nodeID = 8; // emonTx RFM12B node ID
const int networkGroup = 210;
typedef struct {
int power1, power2, power3, power4, Vrms, temp[MaxOnewire];
unsigned long pulseCount;
} PayloadTX; // create structure - a neat way of packaging data for RF comms
PayloadTX emontx;
//Random Variables
//boolean settled = false;
boolean CT1, CT2, CT3, CT4, ACAC, debug, DS18B20_STATUS;
byte CT_count=0;
volatile byte pulseCount = 0;
unsigned long pulsetime=0; // Record time of interrupt pulse
void setup()
pinMode(LEDpin, OUTPUT);
pinMode(DS18B20_PWR, OUTPUT);
pinMode(pulse_count_pin, INPUT_PULLUP); // Set emonTx V3.4 interrupt pulse counting pin as input (Dig 3 / INT1)
emontx.pulseCount=0; // Make sure pulse count starts at zero
digitalWrite(LEDpin,HIGH);
Serial.begin(9600);
Serial.print("emonTx V3.4 Discrete Sampling V"); Serial.print(version*0.1);
#if (RF69_COMPAT)
Serial.println(" RFM69CW");
#else
Serial.println(" RFM12B");
#endif
Serial.println("OpenEnergyMonitor.org");
Serial.println("POST.....wait 10s");
//READ DIP SWITCH POSITIONS
pinMode(DIP_switch1, INPUT_PULLUP);
pinMode(DIP_switch2, INPUT_PULLUP);
if (digitalRead(DIP_switch1)==LOW) nodeID--; // IF DIP switch 1 is switched on then subtract 1 from nodeID
if (digitalRead(DIP_switch2)==LOW) USA=TRUE; // IF DIP switch 2 is switched on then activate USA mode
if (USA==TRUE){ // if USA mode is true
Vcal=Vcal_USA; // Assume USA AC/AC adatper is being used, set calibration accordingly
delay(10);
rf12_initialize(nodeID, RF_freq, networkGroup); // initialize RFM12B/rfm69CW
for (int i=10; i>=0; i--) // Send RF test sequence (for factory testing)
emontx.power1=i;
rf12_sendNow(0, &emontx, sizeof emontx);
delay(100);
rf12_sendWait(2);
emontx.power1=0;
if (analogRead(1) > 0) {CT1 = 1; CT_count++;} else CT1=0; // check to see if CT is connected to CT1 input, if so enable that channel
if (analogRead(2) > 0) {CT2 = 1; CT_count++;} else CT2=0; // check to see if CT is connected to CT2 input, if so enable that channel
if (analogRead(3) > 0) {CT3 = 1; CT_count++;} else CT3=0; // check to see if CT is connected to CT3 input, if so enable that channel
if (analogRead(4) > 0) {CT4 = 1; CT_count++;} else CT4=0; // check to see if CT is connected to CT4 input, if so enable that channel
if ( CT_count == 0) CT1=1; // If no CT's are connect ed CT1-4 then by default read from CT1
// Quick check to see if there is a voltage waveform present on the ACAC Voltage input
// Check consists of calculating the RMS from 100 samples of the voltage input.
Sleepy::loseSomeTime(10000); //wait for settle
digitalWrite(LEDpin,LOW);
// Calculate if there is an ACAC adapter on analog input 0
//double vrms = calc_rms(0,1780) * (Vcal * (3.3/1024) );
double vrms = calc_rms(0,1780) * 0.87;
if (vrms>90) ACAC = 1; else ACAC=0;
if (ACAC)
for (int i=0; i<10; i++) // indicate AC has been detected by flashing LED 10 times
digitalWrite(LEDpin, HIGH); delay(200);
digitalWrite(LEDpin, LOW); delay(300);
else
delay(1000);
digitalWrite(LEDpin, HIGH); delay(2000); digitalWrite(LEDpin, LOW); // indicate DC power has been detected by turing LED on then off
//Setup and for presence of DS18B20
digitalWrite(DS18B20_PWR, HIGH); delay(100);
sensors.begin();
sensors.setWaitForConversion(false); // disable automatic temperature conversion to reduce time spent awake, conversion will be implemented manually in sleeping
numSensors=(sensors.getDeviceCount());
if (numSensors > MaxOnewire) numSensors=MaxOnewire; //Limit number of sensors to max number of sensors
byte j=0; // search for one wire devices and
// copy to device address arrays.
while ((j < numSensors) && (oneWire.search(allAddress[j]))) j++;
delay(500);
digitalWrite(DS18B20_PWR, LOW);
if (numSensors==0) DS18B20_STATUS=0;
else DS18B20_STATUS=1;
if (Serial) debug = 1; else debug=0; // if serial UART to USB is connected show debug O/P. If not then disable serial
if (debug==1)
Serial.print("CT 1 Cal "); Serial.println(Ical1);
Serial.print("CT 2 Cal "); Serial.println(Ical2);
Serial.print("CT 3 Cal "); Serial.println(Ical3);
Serial.print("CT 4 Cal "); Serial.println(Ical4);
delay(1000);
Serial.print("RMS Voltage on AC-AC is: ~");
Serial.print(vrms,0); Serial.println("V");
if (ACAC) {
Serial.println("AC-AC detected - Real Power measure enabled");
Serial.println("assuming pwr from AC-AC (jumper closed)");
if (USA==TRUE) Serial.println("USA mode active");
Serial.print("Vcal: "); Serial.println(Vcal);
Serial.print("Phase Shift: "); Serial.println(phase_shift);
} else {
Serial.println("AC-AC NOT detected - Apparent Pwr measure enabled");
Serial.print("Assuming VRMS: "); Serial.print(Vrms); Serial.println("V");
Serial.println("Assuming power from batt / 5V USB - power save enabled");
if (CT_count==0) {
Serial.println("NO CT's detected");
} else {
if (CT1) Serial.println("CT 1 detected");
if (CT2) Serial.println("CT 2 detected");
if (CT3) Serial.println("CT 3 detected");
if (CT4) Serial.println("CT 4 detected");
if (DS18B20_STATUS==1) {
Serial.print("Detected Temp Sensors: ");
Serial.println(numSensors);
} else {
Serial.println("No temperature sensor");
#if (RF69_COMPAT)
Serial.println("RFM69CW");
#else
Serial.println("RFM12B");
#endif
Serial.print("Node: "); Serial.print(nodeID);
Serial.print(" Freq: ");
if (RF_freq == RF12_433MHZ) Serial.print("433Mhz");
if (RF_freq == RF12_868MHZ) Serial.print("868Mhz");
if (RF_freq == RF12_915MHZ) Serial.print("915Mhz");
Serial.print(" Network: "); Serial.println(networkGroup);
Serial.print("NODE CT1 CT2 CT3 CT4 VRMS/BATT PULSE");
if (DS18B20_STATUS==1){Serial.print(" Temperature 1-"); Serial.print(numSensors);}
Serial.println(" ");
delay(500);
else
Serial.end();
if (CT1) ct1.current(1, Ical1); // CT ADC channel 1, calibration. calibration (2000 turns / 22 Ohm burden resistor = 90.909)
if (CT2) ct2.current(2, Ical2); // CT ADC channel 2, calibration.
if (CT3) ct3.current(3, Ical3); // CT ADC channel 3, calibration.
if (CT4) ct4.current(4, Ical4); // CT ADC channel 4, calibration. calibration (2000 turns / 120 Ohm burden resistor = 16.66) high accuracy @ low power - 4.5kW Max @ 240V
if (ACAC)
if (CT1) ct1.voltage(0, Vcal, phase_shift); // ADC pin, Calibration, phase_shift
if (CT2) ct2.voltage(0, Vcal, phase_shift); // ADC pin, Calibration, phase_shift
if (CT3) ct3.voltage(0, Vcal, phase_shift); // ADC pin, Calibration, phase_shift
if (CT4) ct4.voltage(0, Vcal, phase_shift); // ADC pin, Calibration, phase_shift
attachInterrupt(pulse_countINT, onPulse, FALLING); // Attach pulse counting interrupt pulse counting
for(byte j=0;j<MaxOnewire;j++)
emontx.temp[j] = 3000; // If no temp sensors connected default to status code 3000
// will appear as 300 once multipled by 0.1 in emonhub
} //end SETUP
void loop()
unsigned long start = millis();
if (ACAC) {
delay(200); //if powering from AC-AC allow time for power supply to settle
emontx.Vrms=0; //Set Vrms to zero, this will be overwirtten by CT 1-4
// emontx.power1 = 1;
// emontx.power2 = 1;
// emontx.power3 = 1;
// emontx.power4 = 1;
if (CT1) {
if (ACAC) {
ct1.calcVI(no_of_half_wavelengths,timeout); emontx.power1=ct1.realPower;
emontx.Vrms=ct1.Vrms*100;
} else {
emontx.power1 = ct1.calcIrms(no_of_samples)*Vrms; // Calculate Apparent Power 1 1480 is number of sample
if (CT2) {
if (ACAC) {
ct2.calcVI(no_of_half_wavelengths,timeout); emontx.power2=ct2.realPower;
emontx.Vrms=ct2.Vrms*100;
} else {
emontx.power2 = ct2.calcIrms(no_of_samples)*Vrms; // Calculate Apparent Power 1 1480 is number of samples
if (CT3) {
if (ACAC) {
ct3.calcVI(no_of_half_wavelengths,timeout); emontx.power3=ct3.realPower;
emontx.Vrms=ct3.Vrms*100;
} else {
emontx.power3 = ct3.calcIrms(no_of_samples)*Vrms; // Calculate Apparent Power 1 1480 is number of samples
if (CT4) {
if (ACAC) {
ct4.calcVI(no_of_half_wavelengths,timeout); emontx.power4=ct4.realPower;
emontx.Vrms=ct4.Vrms*100;
} else {
emontx.power4 = ct4.calcIrms(no_of_samples)*Vrms; // Calculate Apparent Power 1 1480 is number of samples
if (!ACAC){ // read battery voltage if powered by DC
int battery_voltage=analogRead(battery_voltage_pin) * 0.681322727; // 6.6V battery = 3.3V input = 1024 ADC
emontx.Vrms= battery_voltage;
Sleepy::loseSomeTime(50);
for(int j=0;j<numSensors;j++)
sensors.setResolution(allAddress[j], TEMPERATURE_PRECISION); // and set the a to d conversion resolution of each.
sensors.requestTemperatures();
Sleepy::loseSomeTime(ASYNC_DELAY); // Must wait for conversion, since we use ASYNC mode
for(byte j=0;j<numSensors;j++)
emontx.temp[j]=get_temperature(j);
if (pulseCount) // if the ISR has counted some pulses, update the total count
cli(); // Disable interrupt just in case pulse comes in while we are updating the count
emontx.pulseCount += pulseCount;
pulseCount = 0;
sei(); // Re-enable interrupts
if (debug==1) {
Serial.print(nodeID); Serial.print(" ");
Serial.print(-1*emontx.power1); Serial.print(" ");
Serial.print(emontx.power2); Serial.print(" ");
Serial.print(emontx.power3); Serial.print(" ");
Serial.print(emontx.power4); Serial.print(" ");
Serial.print(emontx.Vrms); Serial.print(" ");
Serial.print(emontx.pulseCount); Serial.print(" ");
for(byte j=0;j<numSensors;j++){
Serial.print(emontx.temp[j]);
Serial.print(" ");
Serial.println("");
delay(50);
if (ACAC) {digitalWrite(LEDpin, HIGH); delay(200); digitalWrite(LEDpin, LOW);} // flash LED if powered by AC
send_rf_data(); // *SEND RF DATA* - see emontx_lib
unsigned long runtime = millis() - start;
unsigned long sleeptime = (TIME_BETWEEN_READINGS*1000) - runtime - 100;
if (ACAC) { // If powered by AC-AC adaper (mains power) then delay instead of sleep
delay(sleeptime);
} else { // if powered by battery then sleep rather than dealy and disable LED to lower energy consumption
// lose an additional 500ms here (measured timing)
Sleepy::loseSomeTime(sleeptime-500); // sleep or delay in seconds
void send_rf_data()
rf12_sleep(RF12_WAKEUP);
rf12_sendNow(0, &emontx, sizeof emontx); //send temperature data via RFM12B using new rf12_sendNow wrapper
rf12_sendWait(2);
if (!ACAC) rf12_sleep(RF12_SLEEP); //if powred by battery then put the RF module into sleep inbetween readings
double calc_rms(int pin, int samples)
unsigned long sum = 0;
for (int i=0; i<samples; i++) // 178 samples takes about 20ms
int raw = (analogRead(0)-512);
sum += (unsigned long)raw * raw;
double rms = sqrt((double)sum / samples);
return rms;
// The interrupt routine - runs each time a falling edge of a pulse is detected
void onPulse()
if ( (millis() - pulsetime) > min_pulsewidth) {
pulseCount++; //calculate wh elapsed from time between pulses
pulsetime=millis();
int get_temperature(byte sensor)
float temp=(sensors.getTempC(allAddress[sensor]));
if ((temp<125.0) && (temp>-55.0)) return(temp*10); //if reading is within range for the sensor convert float to int ready to send via RF