Test 3
- Outside temperature back of the unit 0.84C
- Metoffice: 0.7C
- Metoffice dew point: -1.3C
- Metoffice relative humidity: 87%
- Average heat output 4.57 kW
The datasheet suggests that capacity should be 5 kW at 2C ambient and 4.5 kW at -7, so about 4.94 kW at 0.84C. So ~7.5% less than the data sheet output in this test.
- 1st cycle: 4.4 kW, outside temp 0.86C
- 2nd cycle: 4.5 kW, outside temp 0.27C
- 3rd cycle: 4.8 kW, outside temp 1.34C