I’m using the thermostat in the controller as a high point switch but the recent colder weather has reminded me to install a third party stat I have in stock instead. I asked Samsung earlier this year and got these instructions below.
Question is they refer to live and switched live, I was expecting zero volts contacts, if someone has fitted one is it really switching live as in mains 230v?
Thanks
If you wanted to utilise a 3rd party thermostat instead this would need to be hard wired back to the heat pump.
Terminals B19 – Neutral
B20 Live
B22 Switch live for call to heat
You would also need to reconfigure some parameters in the service menu.
In field settings, FSV 2091 will need to be set to “use signal only on / off”.
In indoor zone option, standard temperature will need setting to “water outlet”
Hi, yes the advice from Samsung is correct. That is how my 3rd party thermostat is wired, although I no longer use it. I find the thermostat in the wired remote controller more useful. Note that you can only use one or the other, so I am not sure why you wish to rewire your 3rd party thermostat.
Hi, Yes it’s interesting that you prefer the controller thermostat……It’s the 2 degrees hysteresis I find awkward. I only use it as a top switch off limit as its in the right temperate spot for it but dropping 2 degrees to come on again is a bit much for us.
Reason I ask about 230v is as I’ve capacity in a data cable but if its 230v I’m switching it becomes a bit more difficult and a dedicated cable.
Got this reply from Samsung technical Jan 3rd this year, also just tried again in case I got it wrong…..you never know! .Actual temp 21.7, set to 22 on, set to 20.5 still on, set to 20, still on, set to 19.5 off
The logic in the control is 2 degrees over set point to go thermo off. This is built into the controller for when it is used as a stat and cannot be changed.
There is new firmware to be released shortly (no date has been confirmed yet) that has a plus 1 degree thermos off instead of the 2 degrees currently.
Hysteresis that will be changeable is based on the thermo on control not the thermo off.