OK, I’ve thrown away my emonLibCM library that I was working on and compiled the V1.7 sketch with this emonLibCM: “Version 2.03 25/10/2019”. As far as I am concerned, that is the current release.
Here’s what I get, starting from power-up:
emonTx V3.4 EmonLibCM Continuous Monitoring V1.70
OpenEnergyMonitor.org
No EEPROM config
Settings:
Group 210, Node 15, Band 868 MHz
Calibration:
vCal = 268.97
i1Cal = 90.90
i1Lead = 4.20
i2Cal = 90.90
i2Lead = 4.20
i3Cal = 90.90
i3Lead = 4.20
i4Cal = 16.67
i4Lead = 6.00
datalog = 9.96
pulses = 1
pulse period = 100
temp_enable = 1
Temperature Sensors found = 0 of 1
Temperature measurement is NOT enabled.
RF on
RFM69CW only Node: 15 Freq: 868MHz Group: 210
POST.....wait 10s
'+++' then [Enter] for config mode
NO CT's detected
AC missing
No EEPROM config
Settings:
Calibration:
vCal = 268.97
i1Cal = 90.90
i1Lead = 4.20
i2Cal = 90.90
i2Lead = 4.20
i3Cal = 90.90
i3Lead = 4.20
i4Cal = 16.67
i4Lead = 6.00
datalog = 9.96
pulses = 1
pulse period = 100
temp_enable = 1
RF on
POST.....wait 10s
Entering config mode...
Available commands for config during start-up:
b<n> - set r.f. band n = a single numeral: 4 = 433MHz, 8 = 868MHz, 9 = 915MHz (may require hardware change)
g<nnn> - set Network Group nnn - an integer (OEM default = 210)
i<nn> - set node ID i= an integer (standard node ids are 1..30)
r - restore sketch defaults
s - save config to EEPROM
v - show firmware version
w<x> - turn RFM Wireless data on or off:
- x = 0 for OFF, x = 1 for ON, x = 2 for ON with whitening
x - exit and continue
? - show this text again
Available commands only when running:
k<x> <yy.y> <zz.z>
- Calibrate an analogue input channel:
- x = a single numeral: 0 = voltage calibration, 1 = ct1 calibration, 2 = ct2 calibration, etc
- yy.y = a floating point number for the voltage/current calibration constant
- zz.z = a floating point number for the phase calibration for this c.t. (z is not needed, or ignored if supplied, when x = 0)
- e.g. k0 256.8
- k1 90.9 2.00
l - list the config values
m<x> <yy> - meter pulse counting:
x = 0 for OFF, x = 1 for ON, <yy> = an integer for the pulse minimum period in ms. (y is not needed, or ignored when x = 0)
p<xx.x> - xx.x = a floating point number for the datalogging period
t0 <y> - turn temperature measurement on or off:
- y = 0 for OFF, y = 1 for ON
t<x> <yy> <yy> <yy> <yy> <yy> <yy> <yy> <yy>
- change a temperature sensor's address or position:
- x = a single numeral: the position of the sensor in the list (1-based)
- yy = 8 hexadecimal bytes representing the sensor's address
e.g. 28 81 43 31 07 00 00 D9
N.B. Sensors CANNOT be added.
Erasing EEPROM...
Done. Sketch will now restart using default config.
No EEPROM config
Settings:
Calibration:
vCal = 268.97
i1Cal = 90.90
i1Lead = 4.20
i2Cal = 90.90
i2Lead = 4.20
i3Cal = 90.90
i3Lead = 4.20
i4Cal = 16.67
i4Lead = 6.00
datalog = 9.96
pulses = 1
pulse period = 100
temp_enable = 1
RF on
<<< I wasn’t quick enough with “+++” - had to physically reset >>>
POST.....wait 10s
NO CT's detected
Settings:
Calibration:
vCal = 268.97
i1Cal = 90.90
i1Lead = 4.20
i2Cal = 90.90
i2Lead = 4.20
i3Cal = 90.90
i3Lead = 4.20
i4Cal = 16.67
i4Lead = 6.00
datalog = 9.96
pulses = 1
pulse period = 100
temp_enable = 1
Temperature Sensors found = 2 of 3, with addresses...
28 81 43 31 7 0 0 D9
28 8D A5 C7 5 0 0 D5
Temperature measurement is enabled.
RF on
AC missing
No EEPROM config
Settings:
Calibration:
vCal = 268.97
i1Cal = 90.90
i1Lead = 4.20
i2Cal = 90.90
i2Lead = 4.20
i3Cal = 90.90
i3Lead = 4.20
i4Cal = 16.67
i4Lead = 6.00
datalog = 9.96
pulses = 1
pulse period = 100
temp_enable = 1
RF on
POST.....wait 10s
k<x> <yy.y> <zz.z>
- e.g. k0 256.8
- k1 90.9 2.00
RF off
Continuing...
NO CT's detected
AC missing
MSG:1,Vrms:3.24,T1:22.62,T2:22.12,pulse:0
MSG:2,Vrms:0.43,T1:22.62,T2:22.12,pulse:0
MSG:3,Vrms:0.43,T1:22.62,T2:22.12,pulse:0
MSG:4,Vrms:0.42,T1:22.62,T2:22.12,pulse:0
Powering down the emonTx, then restarting with no interaction, I see
No EEPROM config
Settings:
Calibration:
vCal = 268.97
i1Cal = 90.90
i1Lead = 4.20
i2Cal = 90.90
i2Lead = 4.20
i3Cal = 90.90
i3Lead = 4.20
i4Cal = 16.67
i4Lead = 6.00
datalog = 9.96
pulses = 1
pulse period = 100
temp_enable = 1
RF on
POST.....wait 10s
NO CT's detected
AC missing
and then nothing (as expected). But my trusty emonGLCD and debugging sketch shows two temperatures being measured and reported by radio: