Wifi relay three phase power supply problem

How to introduce them, I don’t know any example

Ok, I am seeking diode.

What about this?

http://es.rs-online.com/web/p/diodo-de-conmutacion/7512705/

Thanks

I am a bit lost with the diode problem, it seems to be finally my problem, How to solve it Martin?

Thanks

What’s the nature of that 12V LED supply? Is it a big iron transformer with some diodes, or is it a switch mode power supply?

The power supplies are integrated in the different light points. It depends of the model, but mainly they are like this:

https://es.tvc-mall.com/details/fs-12v-30w-waterproof-electronic-led-driver-transformer-power-supply-sku84001107a.html?c=EUR&utm_source=google&utm_medium=pla&utm_campaign=cse&gclid=CjwKEAjw5vu8BRC8rIGNrqbPuSESJADG8RV0979PMCizBG22dh4UE6TorWJrK5GkcXVZhIYjB8tCHhoCAT7w_wcB

Thanks.

You cannot use a diode when switching a.c!
You need a resistor and capacitor in series - something like this.

(You cannot use any capacitor, it must be “X-rated” for mains use: Papel metalizado X2, 250 Va.c.)

I have to consult an specialist but how much important is this resistor? could be my problem of stop switching or not?

I only made the suggestion. It is for you to decide whether you want to try it, or not.

When you wrote that the relay stopped working for a few seconds when it switched off, I deduced that at that instant, you might have an arc strike as the contacts part, as stored energy in the transformer inside that power supply has nowhere else to go. The arc generates interference that causes the WiFi relay to crash and restart itself.

If you put the component I suggested across the relay contacts, the capacitor allows the fast spike of current to flow and be dissipated harmlessly in the resistor, instead of generating a high voltage and interference.

They look like “electronic transformers”, i.e. not really transformers at all but rather switch mode power supplies. I wouldn’t expect them to present as an inductive load.

Neither would I, in fact I’d expect one of those to appear capacitive with a big splash of current at switch-on rather than at switch-off, but a big splash at switch-off is the only scenario that seems to fit the available evidence, and it’s probably worth trying for the sake of the cost of a contact suppressor.

Thanks everyone for your support.

Finally I am ordering a contact suppressor for my problem but I don’t know exactly which one?

Any help in this decission?

Thanks.

Here: Wifi relay three phase power supply problem - #23 by Robert.Wall

Ok,

My question now is how to install it in the current relay. By connecting pieces, in a board?
I have to connect two wires now (relay only have to control one) and I didn’t before

Thanks!

According to the scheme of a cotact supperssor I have to introduce in the relay wire cables as this scheme shows. That’s right?

Thanks.

My second question

Why not introduce it inside the WIFI RELAY board?

I think it is totally possible and this device will be prepare for any circuit: inductive too.

That’s right isn’t it?

I can solder the 100 nF cappacitor to relay 2 external pins (i am using only NC option for the lighting line)

Could this capacitor damage the board? better outsie? What do you think?

I don’t understand why this component is not installed in the board now!

You must have had two wires before. It is impossible not to have.[quote=“bernamorillo, post:31, topic:1153”]
as this scheme shows. That’s right?
[/quote]

That is correct.[quote=“bernamorillo, post:32, topic:1153”]
Why not introduce it inside the WIFI RELAY board?
[/quote]

There might be a situation where the very small amount of current that passes through the contact suppressor will cause a problem. Therefore, it is impossible to say that the suppressor should always be fitted. It could be the case that a suppressor MUST NOT be fitted.

Are you sure? You ENERGISE the relay to turn the lights OFF?
NO means Normally Open, open when not energised, closed when energised…
NC means Normally Closed, closed when not energised, open when energised.

You put the contact suppressor in parallel with the contacts that you are using.

If you apply too much heat for too long when soldering, you could certainly damage the board. I would connect it to the terminals that go to the relay contacts. Remember to put some insulating sleeving on the bare wires to prevent an electric shock if you touch them.

Ok, everything thats right.

I will introduce the capacitor in the terminals, it is easier.

I am ENERGISE the relay to turn the lights OFF because if the relay doen’t works the user could use thermal protection as a switch on-off button (as they are using now)

Is there any problem with this solution? Could it increase the problem or something?

If I connect the wires in NC position as you say if the relay fail they can turn lights on manually.

Thanks a lot Robert.

I have 2 wires of course, but they are from the same line, I didn’t explain it properly, I was asking about the use of the second wire of the line (Neutral and Phase in AC 220V line).

Now I am controlling one wire with relay (logically) and the other wire goes directly to lighting line from thermal protection.

Previously I didn’t understand the capacitor conection scheme, now this question is not interesting.

Thanks.

I still working on that.

Finally we have check that:

  • The 240V to power the unit is the problem. We have 250V connection (electrical company issues) and after some uses the relay stop to work. You can hear how it try to move but it sounds very quiet, it is like a very tiny “click”
  • We are trying to solve introducing directly 5V in the board trought an external transformer.

I will keep you informed. Tomorrow we finish the work.