Vaillant maximum output capacity testing

A few to start with, variation between units is high.

One issue that may or may not be significant is that we are using MetOffice outside temperature data and while in general agreement is good, especially for longer term averages, looking at the precise outside conditions over x number defrosts some of the variation seen here could reflect deviations in the actual evaporator air in temperature. This is something we want to look at in more detail and perhaps provide the option for a direct outside temperature measurement at the back of the unit as standard.

These are all 7 kW Vaillant Arotherm’s (scroll to the right to see dashboard link):

System ID OutsideT Peak FlowT Mean FlowT Flow rate Peak elec Mean elec Peak output Mean output Datasheet Missing W Missing Cycles Dashboard link
510 -2.7 34.9 31.6 20.3 3080 2475 9306 6583 8800 2217 25% 3 Emoncms - app view
510 -3.2 35.1 31.9 20.3 3131 2451 9305 6385 8800 2415 27% 3 Emoncms - app view
510 -0.3 36.1 33.3 20.3 3224 2543 9636 6712 9500 2788 29% 3 Emoncms - app view
124 0.1 34 31.9 24.6 2734 2099 11470 7727 9500 1773 19% 4 Emoncms - app view
124 -0.1 34.4 32.3 24.5 2980 2474 12442 8290 9500 1210 13% 3 Emoncms - app view
282 -2.8 37.4 35.7 20.3 3229 2778 10071 7391 8800 1409 16% 4 Emoncms - app view
n/a -0.7 38.5 36 20.2 3033 2528 8600 5675 9200 3525 38% 3 Emoncms - app view
284 -2 39.2 36.5 20 3216 2589 8917 5936 8800 2864 33% 4 Emoncms - app view
284 -0.2 37.6 34.4 20.7 3148 2534 10249 6413 9400 2987 32% 3 Emoncms - app view
315 -0.9 47.9 43.9 20.2 3503 2939 8582 6239 9000 2761 31% 5 Emoncms - app view
258 0 34.9 31.8 19.9 3166 2458 9556 6512 9500 2988 31% 3 Emoncms - app view
517 -3.2 46 43 20 3484 3054 8315 6925 9000 2075 23% 2 Emoncms - app view
392 -1.6 36.2 32.2 20.7 3087 2408 9461 6292 9100 2808 31% 4 Emoncms - app view

One of the things we have to be careful with when taking max output measurements is that the unit is really trying to run at max output and that the compressor is not modulating down due to flow temps reaching near the WC flow target. E.g @glyn.hudson set his WC curve to target 90C flow temp at 0C outside to be sure it would try and go to max. Most of the systems here wont be specifically doing that extreme of a test but their compressor electrical consumption curves are very similar indicating that they are not quite meeting their curve target temperatures anyway.

E.g Glyn’s test, we see a characteristic shape here, there’s that peak electric consumption above 8 mins in, then a very slight reduction followed by a flattish period and then a slight curve downwards towards the end.

The same is visible in system id 124 example 1 Emoncms - app view. Are we therefore happy that this period reflects the maximum compressor output? We do see some variation in both the peak and mean electrical consumption for the above examples, some of this is variation in full cycle period length and length of the defrost period itself, providing slightly different duty cycles.