Hi everyone,
I am Philipp. This is a great thread and I have already learnt a lot here. I would like to join in and hope to get some help or different perspectives, because I am stuck.
Some questions first before I bore you with the details:
What could be the cause of our bad COP, despite always low flow T and long runtimes of the ASHP?
What could be the reason for a low dT (~1-1.5K) and does this matter for efficiency?
Should the flow rate for the Aerotherms always be the max. (i.e. 850l/h for 5kW, 1205l/h for 7kW unit)?
Could the runtimes actually be too long, and/or the flow T too low?
Could the Vaillant data or internal T measurements just be completely wrong?
Could just be something wrong with the ASHP, despite just having had the annual service?
We have a Vaillant aerotherm plus 7kW installed in March 2023. I didn’t know of the heat pump monitor unfortunately, otherwise I would have chosen an installer that builds this in and guaranteed me a min. SCOP.
Reading the Vaillant data, the SCOP for the first year has only been 2.4.
Until recently, in September 2024, after some insisting, the installer came back and re-piped the then 4-pipe-buffer tank (40L Vaillant) to be a volumiser (in and out). Since then, the COP has been around 3. With the data from the Vaillant app and some extrapolation, I predict the SCOP would also be around 3 now, maximum 3.3.
So a great improvement, looking at the previous SCOP but still not at all satisfying compared to what is possible.
What is bugging me is that I really don’t understand, why this is. I do understand that the ASHP is very likely oversized, but not exactly how that explains the bad COP. That’s why I have not completely lost hope yet to improve the SCOP further.
The heat pump is certainly not short-cycling and using a very low heat curve, the flow T are also on the low end. The unit runs quite long, at low flow T and low compressor speed, actually. Only that it then just doesn’t produce that much heat. The dT is quite low, usually 1-2K only.
Heat curve: 0.4-0.5 (currently 0.5)
Room T mode: inactive (pure weather compensation)
Building Flow rate before buffer-change: 1205l/h / build. pump setting: Auto
Building Flow rate after buffer-change: 990l/h / build. pump setting: 50% / some valve was turned down throttling flow.
I am currently experimenting with the flow rate and pump settings.
My installer says our house would need 650-750l/h flow and I would then get better dT and better efficiency. We tried that by throttling the radiator lock-shield valves and got the flow way down there (pump set to 50%, i.e. min. possible setting). Had that for a few hours. dT I think went closer to 3K. But COP was worse in that time. UrbanPlumber via Youtube comment told me that I shouldn’t do that, so I opened all valves and set pump back to Auto. Tried it again later at around 860l/h with little to no effect to COP.
Currently, Building Flow rate is back to 1205l/h / build. pump setting: Auto, pump running at 61% during heating. COP still not good.
I wonder, if the ASHP just runs best at the max. flow rate. Assuming that somehow heat transfer in the house is better at lower flow rates (e.g. better dT?) , then perhaps the 990l/h have been sort of a compromise between those different optima, i.e. going slower makes it worse for the ASHP, going faster makes it worse for the house. Does that make sense?
If the flow rate is so important, then I wonder how the units can work in any house efficiently that isn’t exactly right for the heat pump size?
When the compressor is shut down after heating, the unit keeps the building circuit pump on at a much lower flow rate. I haven’t seen that behaviour on any other Vaillant aerotherm data I have been browsing through on heatpumpmonitor. Has anyone else noticed this behaviour of their aerotherm+?
Does anyone else notice that the ASHP does a rather loud hissing sound?
I assume that is the refrigerant rapidly expanding, but it does seem really loud to me.
House:
1950s Bungalow in Dorset, semi-detached, around 85sqm, 3 Bedrooms, living room is an extension built in 2008. Cavity wall insulation, loft insulated.
Previous gas usage with room T around 19-21C around 10,000kWh per year.
Degree days rule-of-thumb I think gave me a heat loss of around 3.5kW. Installer survey was 5.5kW.
Heating usually set to 20C. Currently timed with setback of 17.5C at night and during working hours. The house never cools down below 19C anyway during those times.
Heating:
Vaillant aerotherm plus 7kW
2m outside pipes to room with the cylinder (Mixergy) and up into the loft to the volumiser. 28mm primary pipes between ASHP, cylinder and volumiser. From the volumiser 22m plastic pipes over the joists in the loft, down as 15mm copper pipes to each radiator. All new pipework, specifically installed for the ASHP. All new radiators as well!
The installer piped the volumiser on the flow side, whereas all schematics put it on the return. I assume it doen’t really matter where that is?
Days in operation: 625 days
Compressor hours: 5144 hours
Compressor starts: 4110
Average runtime per start (5144 hours/ 4110): 1.25 h/start
Building pump hours: 8651 hours
Building pump starts: 782
4-port Valve hours: 11 hours
4-port Valve operations: 153
Fan operating hours: 5314 hours
Fan starts: 4296
EEV steps (El. Expansion valve steps): 43431
No. switch ops: 15
Thanks all!
Philipp