Hi David,
I will look at my MMI display when the heat pump is running later and see what my home display shows compared to the actual data from my OEM monitoring system.
I’m not sure what the 29c next to the radiator symbol is actually meant to represent.
Do you have any overshoot or modulation set?
Have you any offset from your WD curve? Check on the Onecta app or the Madoka controller.
We have worked out that this heat pump has a minimum electrical input of 920w and at a COP of 5 as tested when 7c outside the minimum heat output is 4,600w at a flow temperature of 35c.
That needs a lot of heat loss and radiators to cope with it.
Your WD curve does look like the flow should be about 29-30c at 9c outside.
I wonder what they replaced your radiators with?
Do you have the schedule that Octopus produced showing their output?
They will have to be huge to run at 30c flow temperature.
If your bungalow is at 20c indoors and the flow is 30c then you will need something like 35 to 40kWh of radiator output at delta t of 50 or about 20kWh at a delta of 30 which is what Octopus did my radiator schedule at. These are rough calculations that I have done quickly in my head.
I have learnt/been reminded of this earlier in this thread.
I can heat my house at 30c flow and 7c outside but efficiency is bad as my radiators are about 60% of the size they need to be to handle the heat produced by the heat pump. My solution at the moment is to run a higher flow temperature until I replace the radiators.
I am having to run at about 43c on a day like today and aim to go down to 35c. I don’t think this heat pump is very happy below this. Theses are our findings so far.
None of it stops your heat pump working and heating the house, its just not very efficient.
Your MMI should be able to tell you the approximate heat production for heating, DHW and total.l