Thank you very much for the replies @Timbones @KnightPhoenix and @johncantor
I will address the points in order
@johncantor Yes, the blue straight line is the flow rate, steady at 24lpm as normal. I never see any issues here.
I also have the simulated carnot heat output showing on the graph here.
My flow and return temperatures do converge and meet perfectly every time the compressor is off
I see no issues with the heat meter and I am confident that the electricity meter is recording correctly as it corresponds to other data from my solar inverter.
I think my data is accurate.
I may be able to check the temperature on the discharge pipe as I do have clip on thermometers.
@KnightPhoenix Hi Zak, hope you are OK.
I have not hooked up ESPAltherma or P1P2 serial yet, but I really should.
I never see a dT of 5c on the DHW although I got the impression from the Daikin engineer that this is what it should be and he thought there was some adjustment but I have never seen it and haven’t really looked for it.
I haven’t noticed any space heating when DHHW is running and I sit right next to a radiator that I do feel a surge of heat from when the 3 way valve switches back to space heating at the end of the DHW cycle.
There is no change in pipework or lagging. I would think the heat meter would still pick up any heat lost though?
Generally.
The problem is intermittent, some days fine, other days not.
The DHW seems erratic even when working normally.
The heat pump seems to lack a bit of punch at the beginning of a DHW or space heating cycle, it doesn’t feel like it did at the beginning if that makes sense.
I first noticed the issue on 14 September 2024 with space heating, loads of electricity and not much heat. The graph is at the top of the page.
The heat pump is generally running well, although as I said, it `feels’ different to it did before the summer.
It did have a firmware update in May 2024.
One other thing I have noticed. I run a fixed lwt and just set it wherever the heat pump runs best. This used to be 31c when colder and 32c when a bit warmer, say +10c and over.
Now the heat pump is running best at 33c flow.
The issue when running DHW is odd and intermittent but when it goes wrong it seems to follow the same pattern, something seems to `release’ as the flow temperature builds and I if I notice the problem I can correct it by ending the DHW cycle and restarting it.
The only thing that has changed recently is I fitted an OEM DHW sensor module on 22 August 2024. Maybe something is interfering with the operation of the 3 port valve.
I will recheck my work 