This part would have worked fine with the original Henley block arrangement as it was so that H2 doesn’t include EV because to expand your equation above it would become
EV = PV – (House CU + EV)
when in actual fact it should be
EV = PV – House CU
As the HB’s were (EV on HB1), then yes CT4 can be used directly to ascertain the available power for EV charging which is what I’ve been saying,
Originally 8 days ago on the other thread
. . . and in this thread 3 days ago
Alternatively you could move CT4 to between HB2 and the house CU or maybe some form of feedback value could be used, for example available for EV = PV – (HB2 - used by EV). Whether the EV is removed from the “normal use” by changing the wiring, moving the CT or in the maths, EV must be removed from the basic PV - USE equation.
Otherwise when there is 2KW of spare PV the EV will be told to use 2kW at which point there is no spare PV so the EV will be switched off and then the 2kW spare reappears so the EV is told to use the 2kW etc etc etc
Do you agree with this part before we reintroduce the diverter?
[edit] Looking closer at the diagrams, moving the CT not the wiring seems the easy choice, the change of diagram style confuses comparison between what you had originally and what you have now.