@TrystanLea My EPC rather pessimistically thinks I’ll be using 20,468kWh for heat and 2,975kWh for water heating.
That’s 140kWh/m2 a year for space heating.
At a rough guess, based on what we’ve used since October, it’ll actually be about 4,500kWh consumed and 14,000kWh generated for space heating which is 30kWh/m2 consumed.
Hot water should be about 2000kWh produced. Power consumption is a bit hard to gauge until I’ve been through a summer with the solar + heat pump + solar diverter. I’m expecting it to be about 1000kWh for a year. There are four of us.
Oil with our very old boiler was 2,000 litres a year so that’s 2000l * 10kWh * 70% = 14,000kWh so it’s about on-par with that.
Heat loss is pretty bad because we have uninsulated brick walls in two-thirds of the house. We have about 150m2 of wall and 100m2 of roof - there’s also a lot of quite big windows from the 1980s. I haven’t got a W/K figure yet.
Here’s the relevant radiator info and room area in m2. The one wrinkle is that there’s a room with two radiators in it.
As you can see we now have about 6 times the radiator surface area that we had before.
As you guessed, we have a 14kW Ecodan so the power output can take the radiators to ΔT 25. If we imagine the rooms are at 21 °C then that puts the flow temp at 46 °C. With my compensation curve we’d have a flow that high when it is -5 °C outside.
compCurveValue = int(30 - effectiveOutdoorTemperature / 3)
Of course that’s all theoretical because it’s not 21 °C in the house. Some of the TRVs are at 15 °C and some are at 25 °C. It’s pretty hard to describe a house with occupants in random flux, especially in half-term week.
Clearly we need to stop the walls leaking heat so we can bring the power usage down. We’re in the pre 1900 bit of this…
However, if we look at a “cold” day (by UK standards) the we can see we’re consuming 1.26kW for space heating. When I think of something like my fan heater I used to use in my office which consumes 1.7kW I’m amazed that the heat pump is keeping the entire house warm whilst using less power.
I know the numbers still look bad to everyone here.