this is a fascinating one. I have probes top, upper middle, lower middle and bottom so I was able to clearly see the terrible effect of a reheat on a not-very-cold tank. This does seem to be default behaviour in a lot of setups - I rather suspect that the 99% of heat pump installs that donāt have monitoring systems like ours with geeks watching over them must suffer from this.
Iām now optimising for least monetary spend in the following way
- Intelligent Octopus. house battery (40kwh) charges overnight along with 2 cars.
- heat hot water to 55C during early part of cheap overnight period on timer. This takes 1 to 1.5hrs. space heating off in this period is fine, weāre asleep.
although the hot water is heating during the least efficient time for the HP : an example of a really bad one, COP of 1.8 for the HW on 2nd december, -2C, 2 defrosts during the reheat - its also the least cost time. on a warmer day like today (7C) the HW COP was 3, the CH COP was 4. (thanks timbones for the separation code!).
regardless, the factor of low electricity price at night far outweighs the factor of higher efficiency during daytime warmth, and just doing it on timer every night keeps it really simple.
this is done almost entirely using the mfrās timer controls. the extra tweak Iāve done is a blocking relay (controlled by an ESP from HomeAssistant) on the 3-way valve. By default samsung will move the 3 way valve towards the cylinder if space heating is not running and it has decided the water in the outdoor unit and/or the outside temp has got too cold. And thus steal a load of heat from your HW cylinder to warm the outdoor unit up. I force the 3-way to stay on heating outside of the times specifically allocated to HW, so if this kind of anti-freezing measure kicks in, it takes it from the lower grade heat left in the rads (which is more than enough), and protects the hard won higher grade heat in the HW cylinder.
By not needing to do another HW reheat for the entire day then I can use all the house battery capacity to drive space heating, lighting, washing machine, cooking etc. result is that on days above approx 3C , I do not pull any peak rate electricity.
our usage varies depending on a variety of family circumstances but using the whole 300L is not unusual which is why I go to 55. Avoiding a 2nd reheat during the 0530-2330 peak time (which would have to be served from the battery) is key to allowing the battery to serve everything else for the whole day.
If I was on a different tariff with a 2nd off-peak, Iād probably set it up differently, but IO as a tariff is such a no brainer with 2 cars and a substantial battery.
However : the crappy COP from my DHW reheat to 55 at night is pushing me down the heatpumpmonitor COP league table 