No problem at all, that is looking much better.
We have the same EDLA06E2V3 unit (you can find my system data here), having a larger overshoot value does help the system to achieve longer runs.
Although the system can be set to flow temperatures as low as 25C, a number of us have found the system can’t really modulate that low. For my system the lowest leaving water temperature I can target is 29C, lower than that and the system just cycles more trying to achieve a target temperature it can’t reach.
Another value that is worth experimenting with is the deltaT, default for underfloor or fancoil emitters is 5C, but you might want to try with 4 or 3C to see if that improves runtimes and COP. There’s conversation about that in this thread: Pushing for COP 5 on Daikin EDLA08E2V3
Obviously now isn’t great time for testing as it isn’t heating season. You’ll be able to experiment fully with these settings, as well as your WD Curve, once the temperatures drop.