6kw R32 Ecodan ASHP on oversized rads

What makes you think it’s oversized?
What’s your actual heat loss at -2C?

Are all the valves open? Have the radiators been properly balanced?

Looks okay, though cycling sooner than I would expect and COP is less good on those subsequent cycles. There are some settings you can change to adjust the overshoot (but only when using Auto Adapt):

If oversized, it might be worth trying Quiet Mode (on FTC6), which reduces that maximum power output, raising flow temperature less quickly.

Do you have access to the flow rate? Can you calculate heat output? This thread might be useful: Estimating Power from MelCloud data - #2 by Timbones

This is possible, but needs very close monitoring and control, and I found Auto Adapt to work way better (and more reliably) than anything I came up with.

1 Like