The Sontex 789 that we recommend for up to 7kW heat pump will be fine for your 5kW system. To deliver 5kW at DT5 your flow rate will be maximum about 15L/min (0.87 m^3/hr). The maximum flow rate quoted on the datasheet for your heatpump will be the maximum flow rate the heatpump can handle without getting sustaining damage!

At 15l/min the Sontex 789 has a pressure drop of 0.25m which is negligible.

It’s great you’re considering adding monitoring to your Acond ASHP, this is a very interesting unit, a European manufactured R290 heatpump. How are you finding the control system?