Hi Sarah,
I thought I had changed everything and therefore assumed it would reset;
- The Samsung ASHP (Monobloc Outside unit) itself changed from a 16kW to a 5kW.
- The MIM-E03 PCB changed
- The Indoor Wired Controller (MWR-WW10) changed
- I tried the Energy reset from the Wired Controller as you suggested, did it the other day
I assumed all counters would start afresh, but I don’t think anything was refreshed.
100000_energy_consumption (NASA msg Id $8414)…reading 339kW
100000_energy_generation (NASA msg Id $4427)…reading 13,309kW.
Its not so important really, I was just wanting the lifetime COP not to be skewed by erroneous figures, just wanted to refresh it and start again, but its no big issue.
DHW settings?
Anyway, would like to pick you brains briefly to confirm my DHW settings resemble something sensible. Initially I don’t want to include any Immersion heating, as I want to see if the 5kW ASHP can produce sufficient Hot water for me in the 300l Tank.
This was my main task tonight, trying to set up DHW scheduling and settings, as I have never used the ASHP for anything but heating before.
So I’ve gone for the following which is pretty much Default I think;
#3011 = 1
#3021 = 55
#3022 = 2
#3023 = 10
Via the Wired Controller, I’ve set the DHW Water Setpoint to be 50C.
I’ve also set up a Daily schedule, one for the evening and also in the middle of the night and for both I set DHW “ON” and have chosen “Standard mode” as I assume it will obey the Hysteresis of #3022 and #3023, although I am not sure whether “Eco mode” is the really the correct choice here, maybe standard mode just runs the DHW cycle regardless and Eco mode obeys the Hysteresis parameters.
I am hoping that during DHW scheduled times, the system will check actual Water tank temp and if below (Setpoint) 50C - 10C (Lower Hysteresis) = 40C this will result in a DHW run and hot water run should end at (Setpoint) 50C + 2C (Upper Hysteresis) = 52C?
However, I think when the DHW schedule kicked in and the DHW function was enabled, it just started, I don’t think it waited for Water temp to drop 10C below setpoint of 50C, it just started and ended once the Water Tank temp was at 50C, so I didn’t see any hysteresis parameters come into play, so whether Standard mode or Eco mode I don’t think the Hysteresis parameters ie DHW On/Off’s were obeyed?
Not sure why, must be a setting that I’ve got wrong, maybe #3011 should be something other than 1?
The LWT seems to be up at around 57C during the DHW run, so that seems to be chugging away nicely and well capable of achieving my desired setpoint of 50C + 2C hysteresis.
Regards
David