_“An ASHP won’t work in your house.”_

Solid stone, rural Scotland. Two levels and rooms in the roof, 420 m² habitable space. No wall or floor insulation. Built in 1874. Heated with a 37 kW LPG combi boiler. You’d better keep a boiler.

That was the first answer, and it was unanimous. When I pushed, the answer shifted but not in my favour: _“You’d need a heat pump the size of your current boiler. 37 kW. And you’d have to rip out the pipework. And replace every radiator.”_ Which, translated, meant _don’t bother_.

I found I couldn’t quite accept that. Not out of stubbornness, but because nobody telling me this had actually properly surveyed the house. The 37 kW figure wasn’t derived from our walls, our windows, our air changes, our house geometry and location. It was derived from our existing boiler — which had itself been sized by someone doing the same thing a decade earlier. A chain of assumptions, each one rounding up for safety, ending in a number nobody had ever checked against reality.

So I started doing the sums myself. I had to learn and understand from scratch about house heating engineering and search for old Victorian houses.

The first assumption worth questioning was the U-value. Industry guidance for solid stone walls lands somewhere around 2.1 W/m²K — a figure generous enough to make any heat loss calculation look terrifying. But our walls aren’t generic solid stone. They’re whinstone rubble with sandstone dressings, roughly 600 mm thick, with lime plaster on lath on the inside. That construction behaves differently from the textbook assumption. Working through it properly — thermal conductivity of the stone, the decoupling effect of the plaster-on-lath cavity, the actual wall thickness — I got to **1.2 W/m²K**. Not insulated-standard by any stretch, but not the disaster the rule of thumb suggested either.

The second assumption was air changes. Old houses leak — that’s true. But _how much_ they leak is a measurable property, not a folk belief, and the default of 1.0 ACH or higher gets applied to buildings it has no business being applied to. Our house has had its windows done, its chimneys sealed where they’re not in use, and isn’t drafty in the way a Victorian tenement might be. Measured and cross-checked, it sits closer to **0.5 ACH**.

Two assumptions corrected, the heat demand calculation fell out differently. Not 37 kW. Not anywhere near it. **11.94 kW** at design conditions. I specified a 12 kW Vaillant aroTHERM Plus. Measured peak demand a year later: **11.6 kW** , inside 3% of the paper calculation.

That was the first answer to the first “no”.

The main runs pipework did need upgrading — heat pumps move twice the flow for the same heat — so I replaced the arteries with 28 mm copper myself before the installer arrived. The capillaries were fine. The radiators didn’t need replacing either; they needed to be _used properly_ at low flow temperatures. That’s a control problem, not a hardware problem. ESP32 fan boosters on the lukewarm rooms, seventeen smart TRVs calibrated and held to a minimum opening to protect the design flow rate (~2,014 L/h), one TRV repurposed as a compensating valve.

Two “no”s down. The third one was the one the industry was least prepared to lose.

After a full heating season, measured against the same house under LPG: **68% less energy, 46% cost reduction, 57% more heat delivered, sCOP 4.21** — the numbers that tell the full story. These are meter totals, from a monitoring stack — Home Assistant, ebusd on the Vaillant’s internal bus, InfluxDB, EmonCMS — built to surface bad news as readily as good. A two-layer control architecture (coarse heat-curve adjustment plus cycle-by-cycle flow-temperature trim, derived by reverse-engineering the manufacturer’s own sensitivity formula) is what delivered those numbers.

Along the way the house became a laboratory. Heat loss coefficient: **0.540 kW/K**. Fabric–ventilation split: **0.496 / 0.037** — internal insulation matters, draught-chasing does not. Air changes per hour: **0.167–0.174** , derived unexpectedly from CO₂ decay curves on the upstairs air-quality monitor. Thermal mass: **~8 kWh/K** , matching first-principles physics for whinstone of this thickness and density. Three numbers, three methods, cross-checked.

The three “no”s that opened this story were not the product of bad faith. The installers I spoke with were not lying, and most of them were competent. They were answering a different question than the one I was asking, which was _what does our house actually need?_

The house I live in now is the same house I moved into — same stones, same lath-and-plaster, same 1874 floor plan. Nothing about the fabric has fundamentally changed. What has changed is what I know about it. That accumulated knowledge is the real project. The 12 kW Vaillant is almost incidental — it’s the machine that made the investigation necessary. The investigation is what made the house tractable.

If the opening of this story was a wall of received wisdom, the end of it is the quieter observation that received wisdom is what you get when nobody has bothered to measure. You have to keep score. Eventually the score speaks for itself.

**The heat pump works. The house works. The monitoring works. The laboratory is open, and it will stay open.**

**PS: Thank you for open energy monitor forum and the emoncms team, you have been a great source of learning.**

Next:

> [@A Heat Pump That Thinks for Itself](https://community.openenergymonitor.org/t/a-heat-pump-that-thinks-for-itself/29930):
>
> Previously: Every heat pump ships with an answer to the same question: given the weather outside, how hot should the water going to the radiators be? The answer is a line on a graph — cold outside means hot water, warm outside means cool water — and the slope of that line, the heat curve. The factory default, in almost every case, is wrong for your house. Not badly wrong, but wrong enough that the gap between a default heat curve and a correctly-tuned one is the difference between a heat pump …

---

<div class="post-metadata">

**Author:** ![borpin](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/borpin/32/193_2.png) [@borpin](https://community.openenergymonitor.org/u/borpin)\
**Post date:** [19 April 2026 11:27 UTC](https://community.openenergymonitor.org/t/the-house-that-couldn-t-have-a-heat-pump/29921/2 "2026-04-19T11:27:03Z")

</div>

You can never beat measurement.

---

<div class="post-metadata">

**Author:** ![HeatStig](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/heatstig/32/33602_2.png) [@HeatStig](https://community.openenergymonitor.org/u/HeatStig)\
**Post date:** [19 April 2026 12:03 UTC](https://community.openenergymonitor.org/t/the-house-that-couldn-t-have-a-heat-pump/29921/3 "2026-04-19T12:03:08Z")

</div>

That’s brilliant 👍

Should be on the Radio 4s Evan Davis Heat Pump Challenge programme and You and Yours - total myth buster

---

<div class="post-metadata">

**Author:** ![muzza](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/muzza/32/18714_2.png) [@muzza](https://community.openenergymonitor.org/u/muzza)\
**Post date:** [19 April 2026 12:31 UTC](https://community.openenergymonitor.org/t/the-house-that-couldn-t-have-a-heat-pump/29921/4 "2026-04-19T12:31:09Z")

</div>

Well that was an impressive first post 👏

---

<div class="post-metadata">

**Author:** ![PjH](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/p/f19dbf/32.png) [@PjH](https://community.openenergymonitor.org/u/PjH)\
**Post date:** [23 April 2026 06:24 UTC](https://community.openenergymonitor.org/t/the-house-that-couldn-t-have-a-heat-pump/29921/5 "2026-04-23T06:24:05Z")

</div>

Excellent analysis and outcome. Thanks for sharing your heat pump journey.

I also live in Rural Scotland and have an aroTherm Plus 12kw. Would you mind sharing the heat curve setting you use and the target room temperature you set in the Vaillant sensoComfort?

---

<div class="post-metadata">

**Author:** ![abidamr](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/a/ea666f/32.png) [@abidamr](https://community.openenergymonitor.org/u/abidamr)\
**Post date:** [23 April 2026 20:50 UTC](https://community.openenergymonitor.org/t/the-house-that-couldn-t-have-a-heat-pump/29921/6 "2026-04-23T20:50:01Z")

</div>

I have a post about our house heat curve setting \* [A Heat Pump That Thinks for Itself](https://community.openenergymonitor.org/t/a-heat-pump-that-thinks-for-itself/29930) \*. The post describes the heat curve and our emitters control. I would be more than happy to share the code associated with it should you need it and adapt it to your house.

---

<div class="post-metadata">

**Author:** ![PjH](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/p/f19dbf/32.png) [@PjH](https://community.openenergymonitor.org/u/PjH)\
**Post date:** [24 April 2026 07:54 UTC](https://community.openenergymonitor.org/t/the-house-that-couldn-t-have-a-heat-pump/29921/7 "2026-04-24T07:54:25Z")

</div>

Thank you for the link to your control system development.

My experience of weather effects has shown that wind has a marked effect on required heat curve settings i.e. heat loss. The concern I would have in including temperature forecasts is that the forecasters are not accurate with predicting temperature in Highland Perthshire.

Do you experience much defrosting and how does that affect your control model?

Can you advise how much electricity your heat pump uses per year?

Do you use the Vaillant for DHW and is that part of your CoP of 4.2?

---

<div class="post-metadata">

**Author:** ![abidamr](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/a/ea666f/32.png) [@abidamr](https://community.openenergymonitor.org/u/abidamr)\
**Post date:** [24 April 2026 09:31 UTC](https://community.openenergymonitor.org/t/the-house-that-couldn-t-have-a-heat-pump/29921/8 "2026-04-24T09:31:45Z")

</div>

I agree with you that weather forecasts are not always correct. To reduce that variability, I have generated my own Home Assistant weather forecast using the OpenMeteo API. I’d be more than happy to share my code for you to adapt to your location. It’s not perfect, but it gives me a good trend in terms of temperature, wind speed, wind direction, etc.

In terms of defrosting, for me it starts at 4.7°C and below. It can be around 8 defrost cycles per 24 hours, going up to 14 on a very humid day at 0°C.

The heat pump uses around 8,300 kWh of electricity per year for an average indoor temperature of 19.5°C. Yes, we use the heat pump for DHW, and the 4.2 includes the DHW.

Highland Perthshire tends to be much colder than Argyll and Bute, as you’re more exposed to easterly weather whereas we’re more exposed to Atlantic weather.

---

<div class="post-metadata">

**Author:** ![OldSurferDude](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/oldsurferdude/32/27511_2.png) [@OldSurferDude](https://community.openenergymonitor.org/u/OldSurferDude)\
**Post date:** [24 April 2026 20:44 UTC](https://community.openenergymonitor.org/t/the-house-that-couldn-t-have-a-heat-pump/29921/9 "2026-04-24T20:44:38Z")

</div>

I am really impressed by the great work done here!

My heat pump problem is totally different. I live in coastal southern California. If I set my thermostat to 65°F (18°C) and 75°F (24°C) my heater only turns on during 4 months of the year and the air conditioner twice during the year. The rest of the time, when it is idling, it uses 2 to 3 kWh per day! Which means the heat pump is using about 60kWh/mo for no benefit.

Here’s the question. Is it bad to completely turn off the heat pump?

Yes, I know how lucky I am to have this problem. But, does one optimize one’s heat pump to save money or to mitigate climate change? I am of the latter ilk, trying to do my part. (Electric energy costs here are approaching $1/kWh during peak periods, though non-peak are “only” ~$0.60/kWh.)

My trivial problem aside, I bow in awe to @abidamr .

---

<div class="post-metadata">

**Author:** ![abidamr](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/a/ea666f/32.png) [@abidamr](https://community.openenergymonitor.org/u/abidamr)\
**Post date:** [24 April 2026 22:27 UTC](https://community.openenergymonitor.org/t/the-house-that-couldn-t-have-a-heat-pump/29921/10 "2026-04-24T22:27:53Z")

</div>

On the climate angle: you’re absolutely right that displacing fossil-fuel heating with a heat pump on a renewables-heavy grid is the bigger win. 60 kWh/month of phantom load is worth eliminating, but the real prize is making sure the heat pump runs efficiently the months it does work.

Regarding the 2–3 kWh/day idle, that is significant. Someone more knowledgeable than me about could hopefully help you track it down. Worth checking whether it’s a crankcase heater or an auxiliary element idling.

---

<div class="post-metadata">

**Author:** ![OldSurferDude](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/oldsurferdude/32/27511_2.png) [@OldSurferDude](https://community.openenergymonitor.org/u/OldSurferDude)\
**Post date:** [24 April 2026 22:43 UTC](https://community.openenergymonitor.org/t/the-house-that-couldn-t-have-a-heat-pump/29921/11 "2026-04-24T22:43:53Z")

</div>

I was told that the heat pump would idle at 100W. I have confirmed this average, but it is in bursts, cycling on and off every 10 minutes.

My plan is to have the company that installed it to do the turn on in the fall, ensuring that it is all up to par.

Thanks for your thoughts. 🙂

---

<div class="post-metadata">

**Author:** ![Jacques\_x](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/jacques_x/32/37840_2.png) [@Jacques\_x](https://community.openenergymonitor.org/u/Jacques_x)\
**Post date:** [16 August 2026 15:56 UTC](https://community.openenergymonitor.org/t/the-house-that-couldn-t-have-a-heat-pump/29921/12 "2026-08-16T15:56:26Z")

</div>

Fascinating thread, i though i was alone with my experiment to try to run a non-suitable house on heat pump.  
My house has 600m2 living space. Built 1900 in Switzerland at 800m height. The climate in comparison has a mean of -6° in comparison to Scotland. The Roof was isolated with 18cm, the windows changed 30 years ago. Wall insulation is impossible, it would destroy the outer appearance of this house. 65 cm Stone Wand. Oil heating Valiant 24KW.  
We installed 25 years ago a thermic sun installation 30m2, with a 3’800l tank.  
Without solar thermic, the oil consumption is 5’000l/year, with 3’800l/year. Still a lot.  
But normally in my region, with the assumption from partly isolated houses, the consumption is 110-140Kwh/m2/year. I’m at 75 (assuming 90% efficacy of the oil heating). It confirms what the author of the threads write, the official assumptions are wrong. But why, the author thinks the isolation is better than naked stone. I have an alternative hypothesis.

The story is that i wanted to install a heating pump, but not with a bad COP. And i made a few subjective observations:

- If i use a steeper heating curve, i had the impression the extra power just disappear in the short term

- I had the impression the house is keeping the summer heat through the beginning of the winter

This gives the idea i could use a high inertia house to have a better COP

Therefore, i conceived with the help of an AI a program to run the heating curve differently than usual.

As the author i use an ESP32, Home Assistant and a raspberry to host locally the HA.

The regulation is the following:

- If a cold period is announced in the meteorologic prevision. The T° of the Inlet heating is augmented. The idea using a good COP period to load with thermal energy the house.
- Doing exactly the contrary if a warm period is coming.
- Lowering the outlet Temperature if a sunny day is coming, using the passive heating through the windows and the wall.
- Using the lowest possible heating curve (determined by testing)
- All thermostats are fully open to assure a constant flow in the heating circuits (entirely different from the author)

The sensors:

- T° sensor 10cm in the outside wall.
- T° sensor on the in an outlet from the heating circuit
- T° in different rooms
- T° outside, wind and sun protected

Then, i have simulated a heating pump, letting my oil heating running exactly with the inlet temperature as a heating pump would do. And calculating the theoretical COP from the inlet temperature and outside temperature.

The result is:

- COP 3.7
- -59% in costs
- From 80Kwh/m2 to 17 Kwh/m2 (this is the huge number)

---

<div class="post-metadata">

**Author:** ![Jacques\_x](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/jacques_x/32/37840_2.png) [@Jacques\_x](https://community.openenergymonitor.org/u/Jacques_x)\
**Post date:** [16 August 2026 18:07 UTC](https://community.openenergymonitor.org/t/the-house-that-couldn-t-have-a-heat-pump/29921/13 "2026-08-16T18:07:01Z")

</div>

But the analysing of the sensors provides another insight. The idea of seasonality is real.

The first graph shows the relationship between the difference outdoor indoor temperature vs heating power, seems on a regression line.

But it is not correct. If i decompose it for every month this relationship, it is not constant. In fact clearly they is a carry over from the summer and i refined the analysis with the passive sun contribution.  
And this gives an interesting picture:

- Until January the house is using the energy stored during the summer.
- Then the sun begins to load the house
- It represents like 10’000KWh a season

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/c/6/c6f491e30a5753941c3d0897f0a8128779ad7d1c.png)