> [@matt-drummer](#):
>
> he has included the heat loss of the lounge twice! He put in the full loss of the room against each radiator rather than halving it. Ooops!

Not even that: If the non-existent party wall dividing the lounge had the same temperature both sides, the heat loss through it would be exactly zero. You would have less than half the loss for each part. It would probably have been more accurate to model one radiator of double the output.

---

<div class="post-metadata">

**Author:** ![TrystanLea](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/trystanlea/32/31_2.png) [@TrystanLea](https://community.openenergymonitor.org/u/TrystanLea)\
**Post date:** [16 November 2023 15:49 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/405 "2023-11-16T15:49:36Z")

</div>

> [@markocoheat](#):
>
> If the default air change rate (assumes that you live in a barn with the doors open) in the MCS calculations wasn’t changed then you’ll probably have far higher assumed ventilation losses than you actually have.

I’ve only recently come to appreciate this, I used air change rates around 1-1.5 in my original heat loss. In actual fact it’s more likely that my air change rates are more like 0.43 ACH. I had a blower door test done which measured the permeability at 60 Pa = 8.677 m3/h/m2. The divide by 20 rule suggests an air change rate of 0.43 ACH. I’ve since been experimenting with CO2 decay rate monitoring (will do another post about this soon) and am quite reliably getting figures around 0.35 ACH when windows & doors are all closed and it’s not blowing a gale outside. Figures are higher when windy but I think with a little attention to draught proofing I should be able to keep them below \<0.6 ACH.

This makes the difference between 4.5 kW and 3 kW in my case. The maximum continuous heat I’ve put into our house over a 24h period is 2.9 kW.

---

<div class="post-metadata">

**Author:** ![matt-drummer](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/e0b2c6/32.png) [@matt-drummer](https://community.openenergymonitor.org/u/matt-drummer)\
**Post date:** [16 November 2023 15:52 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/406 "2023-11-16T15:52:38Z")

</div>

Yep,

When it is really cold I would isolate the conservatory for a lot of the day.

I estimated my heat loss at somewhere between 4 and 5kW based on our gas consumption.

I don’t think it is far off.

---

<div class="post-metadata">

**Author:** ![matt-drummer](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/e0b2c6/32.png) [@matt-drummer](https://community.openenergymonitor.org/u/matt-drummer)\
**Post date:** [16 November 2023 15:54 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/407 "2023-11-16T15:54:59Z")

</div>

Hi Robert,

I’m sorry I don’t understand your comment?

The heat loss of the lounge was calculated as accurately as any of the others. He just added it in twice into the schedule of radiators.

As Marko suggests, it’s a manual operation and therefore subject to human error.

He did not include an extra room as you seem to be suggesting?

---

<div class="post-metadata">

**Author:** ![TrystanLea](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/trystanlea/32/31_2.png) [@TrystanLea](https://community.openenergymonitor.org/u/TrystanLea)\
**Post date:** [16 November 2023 15:55 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/408 "2023-11-16T15:55:09Z")

</div>

I should add I do think there’s a need to be careful not to sail too close to the wind with sizing (unless you have some form of additional backup heat). What I dont feel I have a clear grasp of yet is what is the real world capacity reduction of heat pumps under freezing fog conditions that are a regular occurrence in the UK. How much spare capacity should we build in to deal with this? I have a lot of spare room on my 5kW heat pump so it’s not been an issue for me. @ColinS has some interesting analysis on this which Im sure he will share soon.

---

<div class="post-metadata">

**Author:** ![Robert.Wall](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/robert.wall/32/38246_2.png) [@Robert.Wall](https://community.openenergymonitor.org/u/Robert.Wall)\
**Post date:** [16 November 2023 16:07 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/409 "2023-11-16T16:07:39Z")

</div>

By adding the room twice, once per radiator, he got **more than** the correct heat loss for two radiators each heating half the room.  
For the sake of simplicity, let’s say that your lounge is completely symmetrical, so that when you divide it into two, each part is a mirror image of the other, each with one radiator. The temperature of each half is the same, so there’s no heat transfer between the two halves. You then calculate the heat loss for each half, but the hypothetical 4th side that’s common to both halves transfers no heat to the other side - it is lossless, perfect insulation. So the heat loss for one half is less than half the heat loss for the two halves added - i.e. less than the loss for the whole room.

---

<div class="post-metadata">

**Author:** ![matt-drummer](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/e0b2c6/32.png) [@matt-drummer](https://community.openenergymonitor.org/u/matt-drummer)\
**Post date:** [16 November 2023 16:13 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/410 "2023-11-16T16:13:40Z")

</div>

Hi Robert,

I thought that was what you were saying but that isn’t what he did I don’t think.

He calculated the heat loss of the lounge.

Then he just included that figure twice so the total heat loss was overstated by the heat loss of the lounge.

He didn’t include it as two separate rooms getting the calculation of each of them wrong by ignoring or adding walls.

---

<div class="post-metadata">

**Author:** ![matt-drummer](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/e0b2c6/32.png) [@matt-drummer](https://community.openenergymonitor.org/u/matt-drummer)\
**Post date:** [16 November 2023 16:17 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/411 "2023-11-16T16:17:30Z")

</div>

You would have thought there would be alarm bells going off all over the place with this.

First the size of the house and the EPC rating?

Second, what they fit to similar houses?

Third, my lounge represented 37% of the total heat loss even though it is only 16% of the total floor area?

---

<div class="post-metadata">

**Author:** ![Robert.Wall](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/robert.wall/32/38246_2.png) [@Robert.Wall](https://community.openenergymonitor.org/u/Robert.Wall)\
**Post date:** [16 November 2023 17:02 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/412 "2023-11-16T17:02:59Z")

</div>

> [@matt-drummer](#):
>
> He calculated the heat loss of the lounge.
> 
> Then he just included that figure twice so the total heat loss was overstated by the heat loss of the lounge.

I agree “alarm bells”. Could this possibly be down to a lack of experience, methinks?

My point comes down to the surveyor should have a method to deal with more than one radiator per room. The obvious ways (to me) are either take the room as one space and add up all the radiators to get one big one, or divide up the room to give one space per radiator, with zero (or only a very small, if you accept a “cold end” and a “warm end”) heat loss on the sides adjacent to another heated space. And to my engineer’s brain, two small radiators spaced apart should be more effective than a single large one (based on ‘Why did you have two in the first place?’), therefore you actually need less than 2&nbsp;× radiators of the size he used in the calculation.

---

<div class="post-metadata">

**Author:** ![marko](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/dbc845/32.png) [@marko](https://community.openenergymonitor.org/u/marko)\
**Post date:** [16 November 2023 17:03 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/413 "2023-11-16T17:03:43Z")

</div>

> [@TrystanLea](#):
>
> This makes the difference between 4.5 kW and 3 kW in my case

That’s for 1-1.5 ACH vs 0.6 ACH?

Or for the (ridiculous) 3 ACH that MCS defaults to and the clueless clowns don’t change vs 0.6 ACH?

---

<div class="post-metadata">

**Author:** ![TrystanLea](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/trystanlea/32/31_2.png) [@TrystanLea](https://community.openenergymonitor.org/u/TrystanLea)\
**Post date:** [16 November 2023 17:05 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/414 "2023-11-16T17:05:08Z")

</div>

> [@marko](#):
>
> That’s for 1-1.5 ACH vs 0.6 ACH?

Yes this one!

> [@marko](#):
>
> Or for the (ridiculous) 3 ACH that MCS defaults to and the clueless clowns don’t change vs 0.6 ACH?

I know!

---

<div class="post-metadata">

**Author:** ![John](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/john/32/26233_2.png) [@John](https://community.openenergymonitor.org/u/John)\
**Post date:** [16 November 2023 17:37 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/415 "2023-11-16T17:37:00Z")

</div>

> [@TrystanLea](#):
>
> I should add I do think there’s a need to be careful not to sail too close to the wind with sizing (unless you have some form of additional backup heat). What I dont feel I have a clear grasp of yet is what is the real world capacity reduction of heat pumps under freezing fog conditions that are a regular occurrence in the UK. How much spare capacity should we build in to deal with this? I have a lot of spare room on my 5kW heat pump so it’s not been an issue for me. @ColinS has some interesting analysis on this which Im sure he will share soon.

Yes, much as the “rubbish COP in warmer conditions” situation is galling, at least the place is warm. Having the nominally oversized Daikin lose its composure completely at -2 because it’s covered in ice is, from a domestic politics PoV, a Big Deal, especially as it would contrast strongly with the other end of the performance envelope. @ColinS 's analysis of the defrost cycle would be most instructive, even if it means we have to dump this HP - but for which one?? There’s a comment on this or a related Daikin thread about a “well-respected” German manufacturer whose real-world defrost performance is abysmal!

---

<div class="post-metadata">

**Author:** ![matt-drummer](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/e0b2c6/32.png) [@matt-drummer](https://community.openenergymonitor.org/u/matt-drummer)\
**Post date:** [16 November 2023 17:44 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/416 "2023-11-16T17:44:59Z")

</div>

Hi Robert,

Lack of experience?

I’ll tell you about Doug the surveyor.

He freely admitted he knew nothing about heat pumps, he was an ex BG employee

He couldn’t draw the floor plan of the house, I had to do it for him.

He was already in trouble with his employer for drawing the floorplans back to front, they needed to be looking at the house from the front, he could only do them backwards and got yet another telling off from the office at my survey.

He originally calculated over 12kW of heat loss and wasn’t in the least bit surprised even though I told him I expected around 5kW.

The office laughed at him when he submitted the calculation for verification and told him off yet again, I could hear the conversation as it was on speaker phone.

He had put the house down as solid walls.

I did inform Octopus that I knew he was clueless and had no faith in his work and my comments were duly noted.

What were they thinking sending somebody of that quality to do the most important part of the job?

He was a nice guy though.

Two weeks before the installation I had a visit from an installer to make sure everything was OK, I questioned the choice of heat pump and heat loss but still no alarm bells.

That visit was from someone who was leaving the employment that week I subsequently found out.

And no questions from any of the five employees that were present during the install, two installers, two electricians and a few visits from a supervisor to check the quality of the work.

Two further visits post installation, I was laughed at when I asked about OEM monitoring and told that I really didn’t need it and if it was his house he would just use it.

The second installation quality auditor seemed to think my heat pump was doing quite well even though I showed him all the other heat pumps here. Again I questioned the install but still no response.

How did I know it was the wrong heat pump, I’m an accountant, these people do this all day every day, you would have thought one of them would notice?

---

<div class="post-metadata">

**Author:** ![marko](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/dbc845/32.png) [@marko](https://community.openenergymonitor.org/u/marko)\
**Post date:** [16 November 2023 17:46 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/417 "2023-11-16T17:46:59Z")

</div>

> [@TrystanLea](#):
>
> I should add I do think there’s a need to be careful not to sail too close to the wind with sizing (unless you have some form of additional backup heat). What I dont feel I have a clear grasp of yet is what is the real world capacity reduction of heat pumps under freezing fog conditions that are a regular occurrence in the UK. How much spare capacity should we build in to deal with this? I have a lot of spare room on my 5kW heat pump so it’s not been an issue for me. @ColinS has some interesting analysis on this which Im sure he will share soon.

Zero!

Design it down to the wire and rely on other crutches if you need to.

- Wear an extra jumper on the odd occasion it’s actually that cold for a sustained period.

- Low temperature radiators are handy when it gets cold. Drop your room temperature to 17C from 20C (say because it couldn’t quite keep up with the heat loss) and your rad output at a given flow temperature will pop up.

I laughed out loud when doing the calc for “frost mode” (could the heat pump stop the place from freezing when it’s -20C out - which is design condition here) and "reheat from frost mode (if flow temp at steady state design condition is 40C but you’re starting with a room at 5C not 20C the rads really kick out more heat)

- Plan on the insulation of the property getting better not worse over time. It’s unlikely that this is the only measure you’ll take.

- Any fix any stuffups with…an AC. We have fitted one of these to knock the edge off in summer. (a fortnight of 30C and 100% humidity knocked back to 24C and DRY is bliss). Noddy basic (doesn’t even have an electronic expansion valve; just a capillary tube) 9000 BTU class minisplit.

> **[Oro kondicionierius Midea Xtreme Save 2,6/2,93 kW Internetu](https://airway.lt/preke/midea-xtreme-save-26-293-kw/)**
>
> Oro kondicionierius Midea Xtreme Save 2,6/2,93 kW Internetu gera kaina, greitas pristatymas, platus asortimentas. Paprastas ir saugus pirkimas vienoje vietoje

€630 inc VAT minsplit. Vac pump, gauges, flaring tool, and heated diode leak detector another €250 inc VAT if you don’t have these already. Lineset, cable, drain hose, floor mounts say €200 inc VAT. A round €1000 worth of bits. Call it €2000 fitted if you didn’t DIY it.

Eurovent figures?

[https://www.eurovent-certification.com/en/catalog/program/certificate/participant/model/show/201398767](https://www.eurovent-certification.com/en/catalog/program/certificate/participant/model/show/201398767)

> **[AC
     | Eurovent Certita Certification](https://www.eurovent-certification.com/en/third-party-certification/certification-programmes/ac)**
>
> Scope of the programme
> 
> The Eurovent Certified Performance (ECP) programme scope for Air Conditioners (AC) applies to factory-made units intended to produce either only cooled ai...

On paper it’ll chuck in 2.1 kW at -7C with a COP of just over 3 (need not worry about defrost at that temperature); 1.3 kW @ +2C with a COP of 4.6; 0.8 kW @ +7C with a COP of 5.5

Bit chilly at design condition (or beyond?)

Blast that into the house somewhere and open the doors and you’ll be fine.

Bit sticky in June/July?

1.1 kW of cooling @ 25C for an EER (COP) of 10.8; 1.75 kW @ 30C for an EER of 6.6 - hardly a criminal amount of electricity and at a time of year when it’s easy to offset against PV

Wanna heat back up from frost setting faster?

Crack it on at 2.9 kW at +7C with a COP of 4.5 (the COP drops at full load vs part load)

[https://www.eurovent-certification.com/en/catalog/program/certificate/participant/model/show/201398767](https://www.eurovent-certification.com/en/catalog/program/certificate/participant/model/show/201398767)

Better IMO to size the wet system to the wire (to maximise the everyday performance of it) and rely on being able to fudge it in extremis with an minisplit.

Put the split in the living room NOT the conservatory. That way you can heat the house with it with conservatory doors shut; and it’s no problem if you open the doors to the conservatory for the cold air to get into the conservatory if for some bizarre reason you wanted to use that in the summer rather than sitting in the garden under the shade of some PV panels / vines.

Not all is plain sailing mind.

Bolt it in. Flare up the pipework. Hook up the wires. Light the woodburner to warm up the indoor unit so that moisture evaporates at a sensible temperature. Vacuum it down. Release the refrigerant. Leak check.

Balls. Thought I’d made a bad flare until I realised that the unit was leaking from an internal braze (and the gas coming down the insulation sleeve) rather than my flare:

[![](https://img.youtube.com/vi/_15Dsbf-jGQ/maxresdefault.jpg "6 November 2023") ](https://www.youtube.com/watch?v=_15Dsbf-jGQ)

Those sniffers detect leaks down to 3g/year. (about what leaks from a car AC compressor rotating seal even by design). Cracking bits of kit for £60 or so. Don’t bother with soapy water etc. Nitrogen pressure test is nicer but lots more kit to have for the odd installation; and wouldn’t have made identifying the location of the (tiny) leak and showing it to the supplier easy.

Shut the liquid line, fun the split in full cooling override until you’ve drawn the refrigerant back into the outdoor unit, shut the vapour line and knock the power off. Call the supplier.

Local distributor to be fair took one look at the vid and asked whether I’d like to pickup a new indoor unit myself or for them to come swap it and weight out the refrigerant/weight in the correct amount in the event that a material quantity had leaked.

Not easy then but can’t grumble at that on a €630 widget.

Shouldn’t really do that in the UK because F-Gas regs. (you need a certificate to know that you shouldn’t let all the gas out before you’re allowed to touch these) Rest of Europe and the USA are less fussed. Can buy the units and the kit to fit them properly at B&Q. Don’t be irresponsible though and do get the tools including one of those heated diode detectors if you are fitting them.

---

<div class="post-metadata">

**Author:** ![marko](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/dbc845/32.png) [@marko](https://community.openenergymonitor.org/u/marko)\
**Post date:** [16 November 2023 17:52 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/418 "2023-11-16T17:52:21Z")

</div>

It’s nuts eh @TrystanLea?

Default assumption: house has no glass in the windows

They should leave it bloody blank in my opinion so that the installing company are forced to put their neck on the line to a degree by estimating a number.

Not that their necks are on the line. Like heck are RECC or MCS are ever going to dare terminate Octopus registrations. Those outfits exist now for the purpose of preventing the smaller players that are good at heating and don’t care for box ticking from entering the market.

I’d REALLY like DESNZ to offer the BUS grant to anybody who can PROVE they’ve fitted the kit correctly via a year’s worth of operating data. Buy the kit outright. (on a 0% card if you have to) Prove it works well. (with OEM etc) Get your VAT back and the BUS at the end of the year.

They don’t need to allocate much funding to that track but imagine the benchmark it would set for installation quality / the look of fear on Ian Rippin’s face if they were to do so. 😃

---

<div class="post-metadata">

**Author:** ![TrystanLea](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/trystanlea/32/31_2.png) [@TrystanLea](https://community.openenergymonitor.org/u/TrystanLea)\
**Post date:** [16 November 2023 17:53 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/419 "2023-11-16T17:53:41Z")

</div>

> [@marko](#):
>
> Zero!
> 
> Design it down to the wire and rely on other crutches if you need to.

Haha, love it 😂

---

<div class="post-metadata">

**Author:** ![Timbones](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/timbones/32/20308_2.png) [@Timbones](https://community.openenergymonitor.org/u/Timbones)\
**Post date:** [16 November 2023 18:50 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/420 "2023-11-16T18:50:03Z")

</div>

> [@marko](#):
>
> €630 inc VAT minsplit.

Can this be fitted (in UK) without planning permission?

---

<div class="post-metadata">

**Author:** ![ColinS](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/c/e56c9b/32.png) [@ColinS](https://community.openenergymonitor.org/u/ColinS)\
**Post date:** [16 November 2023 19:25 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/421 "2023-11-16T19:25:09Z")

</div>

At Trystan’s prompting I’ve put my thoughts and measurements on the defrosting issue in a separate thread. I’d value all input…and corrections!

Hope I’ve got this link right…

> [@ASHP sizing for Freezing Conditions](https://community.openenergymonitor.org/t/ashp-sizing-for-freezing-conditions/24802):
>
> I think this issue is common to alI Air Source makes so would value input from anyone with experience and understanding of what happens with heat pumps in Freezing Conditions and if there is any way to set them to minimize the problem. I don’t think it matters too much - for this issue, whether your emitters are radiators or underfloor, mine is a mix of radiators and convector rads. I have enough emitter capacity to run it at 38c and get the required output at -2c outside. I’ll start by with m…

---

<div class="post-metadata">

**Author:** ![marko](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/dbc845/32.png) [@marko](https://community.openenergymonitor.org/u/marko)\
**Post date:** [16 November 2023 19:29 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/422 "2023-11-16T19:29:45Z")

</div>

> [@Timbones](#):
>
> Can this be fitted (in UK) without planning permission?

Nope.

It’s not an air source heat pump installed by an MCS union member. You’re allowed to fit gas boilers and stinky oil boilers wherever you like. The MCS union successfully lobbied government to make it illegal to fit heat pumps of any description unless you use MCS labour. MCS don’t do air conditioning so it isn’t permitted development.

However if you throw it on the wall anyway and nobody moans for four years it’s effectively legal from a planning consent perspective.

Unless your neighbours are awful people I would, given the price point, install it somewhere that it can’t be seen or heard and roll the dice on planning consent.

---

<div class="post-metadata">

**Author:** ![Gwil](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/gwil/32/29028_2.png) [@Gwil](https://community.openenergymonitor.org/u/Gwil)\
**Post date:** [16 November 2023 19:51 UTC](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/423 "2023-11-16T19:51:57Z")

</div>

> [@Robert.Wall](#):
>
> Seriously though, we really need a good technical writer with knowledge of heat pumps to write a section in ‘Learn’

Yes, absolutely. For now, I would usually point people towards John Cantor’s website - [https://heatpumps.co.uk/](https://heatpumps.co.uk/) - as a fantastic place to start their research. His book is a great read too.