(Paul)
2
This part is the key point being made.
Since the Owl devices do not sense voltage, instead they use a preset fixed value e.g. 240 volts for the UK, 2 amps x 240 volts = 480 watts which is not correct for low power factor loads (or anything other than unity PF 1).
The same would be true of OEM devices IF an a.c. adapter isn’t used, but the emonPi and emonTx’s all have the ability to measure real power by monitoring voltage amplitude and phase relative to the current measurement. It is strongly advised, to the point of being “the norm” to sample voltage as well as current.
So long story, short. No this doesn’t ordinarily apply to OEM devices, a correct reading should be possible with CT’s.
1 Like