Hi everyone,

I’m looking for some advice regarding unusual compressor modulation behaviour on my Samsung EHS heat pump.

I’ve been monitoring the system through ESPHome using the Samsung HVAC NASA interface, with historical data stored in Home Assistant/InfluxDB.

The heat pump generally works well, but I’ve noticed a significant difference in compressor modulation under very similar outdoor conditions.

Sometimes the compressor modulates smoothly down to 15–25 Hz. On other occasions, it remains at almost exactly 35 Hz for four to five hours, even when the water outlet temperature significantly exceeds the calculated Water Law target.

I’m trying to understand whether this is normal Samsung control behaviour, an internal compressor limitation, or something else.

1. My system configuration

Heat pump:

  • Samsung EHS AE160ANYDGH/EU

  • 12–16 kW system

  • Samsung wired controller (2022 generation)

Heating configuration:

  • Heating mode: Auto / Water Law

  • Standard Temperature: Water Outlet

  • FSV 201*: Outdoor temperature +15 °C / −10 °C

  • FSV 203*: Water outlet temperature 37 °C / 48 °C

  • FSV 2041: WL2-FCU

  • FSV 2093: 1 (Room Temp only)

  • Room temperature setpoint: 22 °C

  • External thermostats FSV 2091/2092: Not used

Hydraulic system:

Heat pump → small buffer tank → radiators → underfloor heating → return.

The radiators and underfloor heating are connected in a series hydraulic circuit.

The Samsung room temperature control works as expected. Based on historical observations, heating starts when the measured room temperature drops to approximately 21.9 °C and stops when it reaches approximately 22.9 °C.

This behaviour has been verified using historical data.

No controller settings were changed between the periods described below.

2. The compressor modulation problem

In September, the compressor regularly modulated down to 15–25 Hz during long heating cycles.

However, during several recent heating cycles in October, the compressor remained at 35 Hz almost continuously.

What concerns me is that the water outlet temperature continued increasing well above the calculated Water Law target, without any corresponding reduction in compressor frequency.

For example, during the night of 12 October, the calculated Water Law target was approximately 40 °C, while the actual outlet temperature reached approximately 48 °C.

Despite this, the compressor continued operating at 35 Hz.

Both the reported target compressor frequency and actual compressor frequency were 35 Hz.

This suggests that the compressor was following the controller’s frequency request rather than failing to reduce its speed.

3. Comparison of three heating cycles

I compared three long heating cycles at almost identical outdoor temperatures.

Parameter 26 Sep 2026 28 Sep 2026 12 Oct 2026
Heating duration 257 min 241 min 290 min
Average outdoor temperature 7.43 °C 7.49 °C 7.72 °C
Average compressor frequency 24.13 Hz 25.97 Hz 34.92 Hz
Minutes at ≤25 Hz 160 116 1
Minutes at exactly 35 Hz 40 62 288
Average outlet water temperature 37.78 °C 38.96 °C 44.98 °C
Calculated Water Law target 40.33 °C 40.31 °C 40.20 °C
Average water flow 19.7 l/min 20.9 l/min 25.2 l/min
Average electrical power 1,341 W 1,478 W 2,214 W
Estimated COP 3.77 3.72 3.41

The Water Law target in this table is calculated from my configured heating curve. It is not a confirmed internal target value read directly from the Samsung controller.

The difference is quite surprising.

At almost the same outdoor temperature, the September cycles showed normal modulation and relatively low outlet water temperatures.

In October, the compressor remained at 35 Hz, with much higher outlet water temperature and electrical power consumption.

4. DHW operation has been excluded

I specifically checked whether domestic hot water heating could explain the differences.

All three reference cycles were verified against the minute-by-minute Samsung NASA data.

For each cycle:

  • Space heating was active throughout the cycle.

  • DHW heating was inactive.

  • The DHW three-way valve remained in the space-heating position.

  • Operating-state data was available for every recorded minute.

  • No DHW operation was detected during the 10 minutes preceding the cycle.

Therefore, the comparison is based on space heating only, not DHW operation or transitions between heating modes.

5. What I have already investigated

I’ve also reviewed historical data from September and October 2026, as well as data from the previous heating season.

Some observations:

The compressor can operate well below 35 Hz.

I have repeatedly observed stable operation at 15–25 Hz.

Low outdoor temperature alone does not explain the behaviour.

On 26 September, the compressor operated at or below 25 Hz for 160 minutes, with an average outdoor temperature of 7.4 °C.

On 12 October, at an average outdoor temperature of 7.7 °C, it remained at 35 Hz for 288 out of 290 minutes.

The problem is not permanent.

On 10 October, the compressor again modulated normally, reaching approximately 15–20 Hz.

Therefore, it does not appear to be a permanent restriction preventing the compressor from operating below 35 Hz.

Room temperature control appears to work normally.

With FSV 2093 = 1 and a room target of 22 °C, heating continues until the room reaches approximately 22.9 °C.

However, during the problematic cycles, the outlet water temperature can be significantly above the calculated Water Law target for several hours before the room thermostat eventually stops heating.

Water flow is also different.

During the well-modulated cycles, average flow was approximately 20 l/min.

During the prolonged 35 Hz cycle, average flow was approximately 25 l/min.

I don’t know whether this is a cause or a consequence of the different operating behaviour.

6. My questions

I’d really appreciate any insight from people familiar with Samsung EHS compressor control and NASA protocol data.

1. Has anyone experienced similar behaviour?

A Samsung EHS compressor remaining at approximately 35 Hz for several hours, even though the water outlet temperature is significantly above the calculated Water Law target?

2. Are there internal compressor operating modes or limitations that can temporarily prevent modulation below 35 Hz?

For example, minimum frequency restrictions depending on operating conditions, outdoor temperature, refrigerant conditions or other internal control parameters?

3. How should compressor modulation behave with FSV 2093 = 1?

My understanding is that Water Law still determines the target outlet water temperature, while the Samsung room thermostat determines when heating is switched off.

Should the compressor normally reduce its frequency when the outlet water temperature approaches or exceeds the Water Law target, even if the room thermostat continues requesting heat?

4. Is there a Samsung NASA register that exposes the actual internal Water Law target?

This would be particularly useful.

Currently, I calculate the expected Water Law target from the configured heating curve, but I would like to verify what target the Samsung controller is actually using.

I’m also interested in any available registers for compressor limitations, control mode, or reasons for a particular target compressor frequency.

5. Could water flow affect this behaviour?

Could the difference between approximately 20 and 25 l/min explain why the compressor sometimes modulates normally and sometimes remains at 35 Hz?

7. Available data

I have extensive minute-by-minute historical data collected through ESPHome and the Samsung HVAC NASA interface, including:

  • Actual compressor frequency

  • Target compressor frequency

  • Outdoor temperature

  • Water outlet and return temperatures

  • Water flow

  • Calculated thermal output

  • Electrical power consumption

  • Space heating status

  • DHW status

  • Three-way valve status

  • Room temperature

  • Calculated Water Law target

I can provide detailed graphs comparing a normal modulation cycle with a prolonged 35 Hz cycle, or share relevant CSV excerpts.

I haven’t changed any settings yet because I’d prefer to understand the control logic before experimenting.

Has anyone investigated this type of behaviour, or does anyone know which internal Samsung parameters might explain it?

Thanks in advance for any advice!

Update – Samsung Water Law target found via NASA protocol

Since posting, I’ve managed to read an additional Samsung NASA register:

  • 0x427F – Water Law Target

  • 0x4247 – Water Outlet Target (exact role still under investigation)

The value reported by 0x427F matches my independently calculated Water Law target within approximately 0.1 °C.

For example:

  • Calculated Water Law target: 39.3 °C

  • Samsung NASA Water Law target: 39.4 °C

I’ve also confirmed that 0x427F continues reporting the heating Water Law target during DHW operation, while 0x4247 remains at 31.0 °C, even when the outlet water temperature rises above 46 °C during DHW heating.

I haven’t yet captured a complete space-heating cycle with these new registers.

The next step is to verify whether 0x427F remains around 40 °C when the compressor stays at 35 Hz and the outlet water temperature rises significantly above that value.

I’ll share the results once I have a complete heating cycle.

Hi @minjos, and welcome. I can offer one or two insights to your questions, but probably not your main one.

When #2093 is set to 1, as LWT approaches/reaches the Water Law target the compressor speed is successively reduced to “minimum”, but the comp keeps running and LWT will exceed WL target. This situation prevails until the roomstat setpoint is reached, at which point the controller stops the compressor. But “minimum” is not a fixed number, and (on my EHS at least) depends on a number of factors including ambient temperature and which controller operating algorithm is in use (e.g. Safety Start, Normal, Defrost etc.). So your observation that LWT exceeds Water Law target is entirely predictable for this #2093 setting. However it does not explain why “minimum” on an extended run is sometimes 35Hz and sometimes 15-20Hz.

To me the biggest clue is your reported LWTs. You are probably shifting a lot more heat in your 12 Oct run - LWT is higher and so is water flow, but as you don’t report the RWTs it is difficult to be sure. If you are, then this would explain the increased required compressor speed and electrical power consumed. (The reduced CoP simply follows from the increased LWT at roughly constant OAT.) Can you think what might have caused an increased energy demand on 12 Oct? Had you turned in more radiators for example? It would help if you gave us your RWTs on the days of your runs.

Incidentally, the increased water flow on 12 Oct rather suggests that you had increased the number of radiators (the circulating pump was running out on its curve due to reduced system pressure drop with the extra radiators). If this is the case, water flow - thus heat pump duty - would be an (indirect) cause of the compressor speed change, rather than an effect.

I cannot comment on your actual minimum compressor speeds - I have a different model which has a minimum of 20Hz for OAT < 7degC and 14Hz for OAT > 7.5degC.

The only FSV setting that I am aware of that changes minimum compressor speed is #6031 (probably not available on a 2022 vintage controller), and in any case you say you didn’t change any settings across your runs.

Although I’ve posted this elsewhere on this forum, I maintain a list of all the NASA message codes relevant to the MIM-E03CN controller (you probably have a different one). My latest version is NASA_Interpreter.xlsx (74.2 KB). You will see in it (Column A) your 0x427F and 0x4247 references with a brief explanation of purpose. The file also includes a tab which decodes incoming NASA packets if you have a sniffer (Python or otherwise) on your controller.

Hope the foregoing helps - happy to clarify on request!

Hi, thank you very much for your detailed explanation and for sharing your NASA Interpreter spreadsheet!

Your explanation of FSV 2093 = 1 is very helpful. I now understand that exceeding the Water Law target is not necessarily abnormal if the compressor has already reached its currently permitted minimum frequency and the room thermostat is still calling for heat.

The main mystery remains why that minimum sometimes appears to be 35 Hz for several hours, while the same unit can operate at 15–25 Hz under similar outdoor conditions.

Regarding your suggestion about increased heat demand:

I haven’t manually changed any radiator valves, circulation pump settings, heating parameters or hydraulic configuration between the September and October observations.

However, I agree that changes in actual heat demand or hydraulic conditions could be important, even without manual intervention.

Fortunately, I have historical minute-by-minute measurements of LWT, RWT, water flow, electrical consumption and calculated thermal output.

I’ll compare the three reference cycles and provide the average return water temperatures, LWT–RWT differences and thermal outputs.

I’ve also reviewed your NASA Interpreter spreadsheet and found it extremely useful.

I can now confirm the following on my system:

  • 0x427F reports the Water Law target and matches my independently calculated value within approximately 0.1 °C.

  • 0x4247 reports 31 °C, which corresponds to the fixed outlet water temperature displayed when I select Indoor Unit Water Temperature instead of Water Law. I have since returned the controller to its original Water Law mode.

  • 0x8237 and 0x8238 report the target and actual compressor frequencies.

I also noticed 0x8236 (Order Frequency1) in your spreadsheet.

Do you know whether this value represents the original compressor frequency request before any internal limitations are applied? Could comparing it with 0x8237 help identify why the compressor sometimes remains at 35 Hz?

One final question: have you ever observed your Samsung remaining at a relatively high minimum frequency for several hours while the LWT continues to rise significantly above the Water Law target?

Thanks again for your help and for sharing your knowledge!

Update – I’ve now calculated the return temperatures and thermal output for the three reference cycles.

Thank you for pointing out the importance of RWT and actual heat transfer. I’ve now checked the original minute-by-minute data, excluding DHW operation.

Parameter 26 Sep 28 Sep 12 Oct
Average OAT 7.43 °C 7.49 °C 7.72 °C
Average LWT 37.78 °C 38.96 °C 44.98 °C
Average RWT 33.98 °C 35.10 °C 40.58 °C
Average LWT–RWT ΔT 3.80 K 3.86 K 4.40 K
Average water flow 19.73 l/min 20.90 l/min 25.24 l/min
Average calculated thermal output 5.05 kW 5.49 kW 7.56 kW
Average Samsung-reported thermal output 4.95 kW 5.42 kW 7.52 kW
Average electrical input 1.34 kW 1.48 kW 2.21 kW
Average compressor frequency 24.13 Hz 25.97 Hz 34.92 Hz

You were right that the October cycle transferred substantially more heat to the heating circuit – approximately 50% more than on 26 September.

The flow rate and LWT–RWT temperature difference were both higher.

However, I haven’t manually changed the radiator valves, circulation pump settings or hydraulic configuration.

What remains unclear to me is whether the increased heat transfer reflects a higher demand from the heating system, or is mainly a consequence of the compressor remaining at 35 Hz and producing hotter water.

In particular, I would be interested in whether the higher return water temperature (40.58 °C versus 33.98 °C) provides any clues about the controller’s modulation behaviour.

Does this comparison suggest anything about why the Samsung might maintain 35 Hz rather than reducing its frequency further?

Thanks again for your help!

Hello @minjos I am also trying to understand the control logic of those samsung systems, there are a lot of mysteries going on there.

Anyhow, in my opinion, what you have observed is just your whole house demanded more heat as it cooled down from september to october, in september you had some of your outputs closed as their TRV were shut, since the space cooled off those TRV opened, that is why you also noted that lpm jumped from 20 to 25, at least that how I see it.

Those are my speculations, I am in no way an expert, just another lost soul into this samsung mystery.

Hi again @minjos,

FWIW here is my perspective on the Samsung controller strategy (which hopefully addresses some of your queries):

  1. On most Samsung heat pumps there are two main dependent variables (compressor suction and discharge pressure) and two independent variables (compressor speed and EEV position). Samsung seek to maximise efficiency by maximising suction pressure consistent with full evaporation of the refrigerant (with just a couple of degC of superheat) and minimising discharge pressure consistent with full condensation of the refrigerant (with just a couple of degC of subcool). This strategy not only maximises CoP, but also minimises equipment sizing (so makes the OU cheaper to build). (On the HTQ series, this simple picture is clouded somewhat by the presence of the economiser circuit, which introduced more dependent and independent variables :squinting_face_with_tongue:.)
  2. But Samsung have not made public details of the controller algorithms that determine just how the 2 independent variables are manipulated in any given situation. (This is to maintain their competitive advantage, I guess). And they are difficult to reverse engineer because they appear to contain software clamps and timers which themselves vary under different operating conditions.
  3. So it is never going to be easy to answer questions like “why is the compressor speed x in one situation and y in another?” We can only hope that the Samsung Application Engineers have written the controller code such as to result in the most efficient operation. In other words, it is probably more meaningful to study your electricity bill than your compressor speed.
  4. The controller MICOM code appears to run as a clocked parser, in which the sensors (e.g. current temperatures, pressures, valve positions etc.) are polled, and new values for the outputs (e.g. compressor motor inverter frequency, EEV/SOV positions etc.) calculated and applied. For example, Samsung have told us that for the circulating pump, after 20 minutes of operating at 100% PWM output, the new PWM output(%) = current PWM output(%) + [(LWT - RWT - FSV#4052) * FSV#4053].
  5. Most outputs appear to be revised immediately, but the compressor is an exception. The SNET-Pro2 output displays three inverter frequencies labelled Target, Order, and Current. I infer from the data that the Order Frequency reflects the raw parser calculation, to which a 2- or 3-term control is applied to give the new Target Frequency. This smooths the rate-of-approach and protects the compressor from sudden inverter frequency changes. To illustrate this, here’s a recent SNET output showing the switch from the Safety Start algorithm to the Normal Operation algorithm (excuse the poor tab line-up):
    Time Target Order Current
    10:03:55 40 40 40
    10:03:58 40 40 40
    10:04:01 40 40 40
    10:04:04 39 30 40
    10:04:07 36 30 38
    10:04:10 34 30 36
    10:04:13 30 30 32
    10:04:16 30 30 30
    10:04:19 30 30 30
    10:04:22 30 30 30
    The switch occurs at 10:04:04 (the Order Freq drops from 40 to 30Hz - quite a large change), and over the next 10 secs or so the calculated Target Freq drops gradually over the same range, with the measured frequency (Current Freq) matching the Target Freq with a ~3s delay.

I think @Maksimilian is correct in saying that your observed change in compressor speed is a reflection of increased house heat demand (quite likely from your TRVs opening) and the heat pump’s normal (programmed) response to this, so you probably don’t need to worry :upside_down_face:.

Hi Sarah,

Thank you again for taking the time to explain the Samsung control strategy in such detail. Your SNET-Pro2 example showing the relationship between Order, Target and Current Frequency was particularly helpful!

I’ve now added NASA register 0x8236 (Order Frequency) to my ESPHome monitoring, alongside 0x8237 (Target Frequency) and 0x8238 (Current Frequency).

The new register is reporting values, although I haven’t yet captured a complete heating cycle with all three frequencies.

Regarding your point about increased heat demand and TRVs opening, I think you and @Maksimilian may well be right.

I’ve compared the three reference cycles again, including the return water temperatures and calculated thermal output:

Parameter 26 Sep 28 Sep 12 Oct
Average OAT 7.43 °C 7.49 °C 7.72 °C
Average LWT 37.78 °C 38.96 °C 44.98 °C
Average RWT 33.98 °C 35.10 °C 40.58 °C
Average flow 19.73 l/min 20.90 l/min 25.24 l/min
Average thermal output 5.05 kW 5.49 kW 7.56 kW
Average compressor frequency 24.13 Hz 25.97 Hz 34.92 Hz

The October cycle clearly transferred substantially more heat to the heating circuit, approximately 50% more than on 26 September.

I haven’t manually changed any radiator valves or hydraulic settings, but I understand that the TRVs could have opened automatically in response to changing room conditions.

What I’m still trying to understand is whether the higher heat transfer was primarily caused by increased demand from the heating system, or whether it was partly a consequence of the compressor operating at 35 Hz and producing hotter water.

I also agree with your point that overall efficiency and electricity consumption matter more than compressor frequency alone.

My main concern has been the significantly higher LWT and its impact on COP, rather than the 35 Hz itself.

For now, I’ll leave all settings unchanged and collect more data, particularly the three compressor frequency values during the next heating cycle.

Thank you again for your help. Your explanations have been extremely valuable in understanding how this controller behaves!

Thanks for sharing this info.

@minjos Just to add a possible explanation from my own experience. Long after my system was installed, I discovered that the installers had set Quiet Mode to come on at some point during the night. At OATs below 9-10C, during Quiet mode, LWT would ignore the Water Law setting and increase steadily towards 50C until the thermostat turned the compressor off. At higher OATs, Quiet Mode followed the Water Law settings. I reported this to one of the Samsung engineers that I met at the Heat Pump show. He asked for the graphics I had taken, but I never heard from him after that. No-one else appears to have seen anything similar, but even if it does not explain your particular issue, it illustrates the fact that the Samsung can do strange things which no-one is ready to explain!

@MikeJH I have observed the same behaviour with my Samsung Gen6 ASHP and Quiet Mode, but I had not made the association to it only happening for OATs below 10C (so thank you for that).

If you want a reduced power ‘quiet mode’ that works with water law, then you can activate (USE) #5051 which will limit the compressor frequency to 50%

Hi @MikeJH,

Thank you very much for sharing this! Your observation is particularly interesting because it closely matches some of the strange behaviour I’ve been seeing on my Samsung EHS.

After reading your post, I checked my controller and discovered that Quiet Mode had also been scheduled automatically from 22:00 to 06:00! I hadn’t realised this was enabled.

Looking back at my historical data, one of my most problematic heating cycles occurred entirely during this period, with an outdoor temperature around 7–8°C. The compressor remained at 35 Hz for several hours, while LWT rose to approximately 48°C despite a Water Law target of around 40°C.

That’s remarkably similar to what you described.

I’ve now disabled the automatic Quiet Mode schedule (19 October) and will monitor the next heating cycles to see whether the behaviour changes.

I’m currently testing FSV 2093 = 4 (Water Pump 3), so the control strategy is different from my earlier tests with FSV 2093 = 1. I’ll keep that distinction in mind when comparing the results.

Your experience has given me a very useful lead, and I really appreciate you taking the time to share it.

I’ll report back once I have some meaningful data without Quiet Mode.

Thanks again!

Hi @Old_Scientist,

Thank you for confirming this behaviour on your Samsung Gen6!

It’s particularly interesting because I’ve just discovered that my own Samsung EHS also had Quiet Mode automatically scheduled from 22:00 to 06:00, without me realising it.

Some of my problematic heating cycles occurred during this period at outdoor temperatures around 7–8°C, with LWT rising significantly above the Water Law target.

I’ve now disabled Quiet Mode to investigate whether it was contributing to this behaviour.

I also checked my controller and confirmed that FSV 5051 (Frequency Ratio Control) is available, currently set to “Not Use”.

My system is an older Samsung EHS 12 kW (AE120AXEDGH/EU, 2022).

Do you know whether enabling FSV 5051 provides the same 50% compressor frequency limitation on these older models, or whether that behaviour is specific to Gen6?

I’m not planning to enable it yet, but it could be an interesting option to investigate later.

Thanks again for sharing your experience!

@minjos

There is an excellent post about #5051 here:

Basically, when #5051 is set to USE, a voltage can be applied to limit the maximum compressor frequency.

If you do nothing other than set #5051 to USE, there would be 0v across the pins, which corresponds to a maximum compressor frequency of 50%

I use this setting, in combination with Quiet Mode, for DHW runs to effect a more low and slow approach which does seem to lower the final LWT for any given set point (which presumably is more efficient)

It doesn’t appear to limit the compressor frequency during the first few minutes of a cold start, but it does limit the compressor shortly afterwards meaning that heating will take longer to reach the desired WL temperature.

Hi @Old_Scientist,

Thank you again for your suggestion regarding FSV 5051!

I’ve now read through the discussion about using Frequency Ratio Control as an alternative to Quiet Mode, and found it very interesting.

I can confirm that FSV 5051 is available on my older 12 kW Samsung EHS (AE120AXEDGH/EU, 2022), currently set to “Not Use”.

I’ve also discovered that my controller had Quiet Mode automatically scheduled from 22:00 to 06:00, which may explain some of the strange overnight behaviour I observed.

I’ve now disabled Quiet Mode and will first monitor the results with my current FSV 2093 = 4 (Water Pump 3) configuration.

If the short cycling continues, I may investigate FSV 5051 as a possible way of limiting compressor output, although I understand that limiting maximum frequency may not necessarily improve minimum modulation.

Thanks again for pointing me in this direction. I’ll share the results once I have enough data for a meaningful comparison!

I wouldn’t discard FSV 2093 = 1 too quickly. It would not have explained your LWT rising to 48C and your heat output being well above minimum output. The only time that this setting causes the LWT to rise above target LWT is when your emitters cannot emit the minimum heat output - around 3.6-4 kW for a 12kW or 16 kW Samsung - which only happens in mild conditions eg OAT 12-15C. In this scenario, the LWT rises until the minimum heat output is matched by the emitters. With any other FSV 2093 setting the ASHP would short cycle instead, which is not good for compressor life.

Thanks for confirming this. I was beginning to think that it was just mine.

I use EspHome to control some of my settings, including FSV 5051 (Frequency Ratio Control), but I haven’t worked out how to change from say 50% to 75% in code. I have seen some form of voltage control, but no description of how and where to apply the voltage. When it is very cold, the LWT achieved when FRC is on is insufficient to heat the house. I am also on Cosy and tend to keep to the cheap periods only, so my target LWT is by necessity higher than it would be if I ran the pump 24/7.

@MikeJH I’d just been re-reading your comments on Quiet Mode in this discussion from 2024:

This post shows the two pins (labelled 14) where the voltage should be applied:

and later in that discussion there is a table of voltages and the corresponding frequency ratio. The table shows 2-3v dc corresponds to 70% and 3-4v dc corresponds to 80%. Maybe a 3v (2 x 1.5v) battery connected across the pins would put you in the right ball park to limit maximum compressor frequency to 70-80%. A simple switch would then allow you to switch between 0V (50%) or 3V (70-80%)

If you have Modbus access, I recommend setting it up that way. I have some automation that sends the value from 50 to 150 every 2 minutes. I use it to dynamicly limit the heat pump

Update – First overnight heating cycle with Quiet Mode disabled

Hi everyone,

A quick update following the very helpful suggestions from @MikeJH and @Old_Scientist regarding Quiet Mode.

On 19 October, I disabled the automatic Quiet Mode schedule (previously 22:00–06:00), leaving all other settings unchanged.

This morning, I recorded a very interesting heating cycle with FSV 2093 = 4 (Water Pump 3):

  • Heating cycle: 02:13–06:51 (279 minutes)

  • Average outdoor temperature: 5.8°C

  • Average compressor frequency: 28.1 Hz

  • Minimum compressor frequency: 15 Hz

  • Time below 35 Hz: approximately 86% of the cycle

  • Average LWT: 39.3°C

  • Average Samsung Water Law target: 41.1°C

  • Maximum LWT overshoot above WL: only +0.6 K

  • Average thermal output: approximately 5.5 kW

The compressor modulated smoothly over a wide frequency range instead of remaining at 35 Hz, and LWT stayed very close to or below the Water Law target throughout the cycle.

This is a significant improvement compared with some of my earlier observations.

Of course, this is only one overnight cycle, and I cannot yet conclude that Quiet Mode was the cause. Heating demand and hydraulic conditions may also have been different.

I’ll continue monitoring with Quiet Mode disabled and FSV 2093 = 4 unchanged.

Thanks again to everyone who suggested checking Quiet Mode. This has been a very useful lead!

Just to add a visual comparison with my previous update.

The first graph shows the frequent short heating cycles observed on 19 October, when the automatic Quiet Mode schedule was still enabled.

The second graph shows the much longer heating cycle on 20 October, after disabling Quiet Mode, with FSV 2093 = 4 (WP3) unchanged.

The difference in compressor modulation and cycling behaviour is quite striking.

This is not yet proof that Quiet Mode caused the problem, as outdoor conditions and heating demand were not identical, but it certainly seems worth investigating further.

Not necessarily so, @MikeJH. If the room temperature is well below roomstat setpoint, as it could be if the owner chooses to operate a substantial setback, then a 48degC LWT may readily be observed. Here’s an output of mine from last February when I experimented with FSV#2093 = 1:


I was operating at the time with a 4degC setback, and at 08:20 (the plot start) the room will have been about 2degC below roomstat setpoint. As you can see, the WL target (yellow line) was about 45degC, the compressor inverter was running at its minimum of 20Hz (magenta line), and the LWT (red line) rose to 50.4degC. The roomstat was finally satisfied at 10:11 and the controller switched the compressor off. All this at an OAT (brown line) of about 6degC.

Whether #2093 =1 is the “best” setting depends on individual circumstances (I summarised some of the relevant considerations in Samsung Gen 6 R32 5kW + Sunamp Thermino (plenty of questions inside) - #8 by SarahH) but would agree with you that #2093 = 1 will almost always result in less cycling than #2093 = 2-4, even if this results in higher operating costs (because LWT may be higher and thus CoP would be lower).

[At the time of the above test, I was on a fixed tariff and my operating economics favoured a large setback, despite the extra cost of running a high LWT to reheat the house afterwards. Unfortunately, minimising operating cost by changing the WL “curve” from a high LWT for initial room heating to a low LWT for the rest of the day was a pain manually or too expensive via HA/RPi, so I changed my electricity provider to one offering TOU tariffs.]

Hi Sarah, we have differed on this in the past. Your example is very persuasive, so I am beginning to understand where you are coming from. From my point of view, I have never seen this behaviour with my Samsung except in mild conditions and I wonder if this is perhaps because we have different models.

However, do you have a record of your heat output during this time? As the house warms, the emitters will emit less heat for a given LWT and there may come a point where the heat emitted is less than the minimum heat output. The LWT would then rise at this point, but heat output would remain at the minimum level. The fact that your compressor frequency was running at its minimum of 20Hz suggests to me that your heat output was close to the minimum that the heat pump could modulate down to. I confess that I am a bit shaky on the relationship of compressor frequency to LWT, heat output and power consumption, but I wonder if your heat pump had reached its minimal modulation despite the OAT of 6C. This would not occur with my Samsung and I wonder if this explains our different experiences and viewpoints?