# Question for the electrically minded: single-phase 230 V air-to-water heat pump on a 230 V phase-to-phase supply with no neutral

**URL:** <https://community.openenergymonitor.org/t/question-for-the-electrically-minded-single-phase-230-v-air-to-water-heat-pump-on-a-230-v-phase-to-phase-supply-with-no-neutral/30580>\
**Category:** Hardware\
**Created:** [3 November 2026 13:14 UTC](https://community.openenergymonitor.org/t/question-for-the-electrically-minded-single-phase-230-v-air-to-water-heat-pump-on-a-230-v-phase-to-phase-supply-with-no-neutral/30580 "2026-11-03T13:14:27Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![aech22](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/aech22/32/39547_2.png) [@aech22](https://community.openenergymonitor.org/u/aech22)\
**Post date:** [3 November 2026 13:14 UTC](https://community.openenergymonitor.org/t/question-for-the-electrically-minded-single-phase-230-v-air-to-water-heat-pump-on-a-230-v-phase-to-phase-supply-with-no-neutral/30580/1 "2026-11-03T13:14:27Z")

</div>

My house in Spain is fed from a 3x230 V network: 230 V between two phases, each conductor at ~133 V to earth, no neutral conductor at all (same as Norway’s IT network). The brand’s local post-sales team says the unit “needs a neutral” and wants an isolation transformer, but their only justification is the terminal drawing showing L, N and PE. The service handbook shows no N-to-PE sensing.

In your experience, is there anything in a modern inverter heat pump (outdoor unit with PFC/inverter board, indoor hydraulic module with pump, 3-way valve, backup heater relay) that actually cares whether N is at earth potential? I can think of: zero-cross or phase detection referenced to PE, Y-capacitor leakage, single-pole internal fuse (covered by an external 2-pole MCB), surge arrester ratings. Anything else? Has anyone run a 230 V unit phase-to-phase and seen a fault code?

Thanks!

---

<div class="post-metadata">

**Author:** ![Robert.Wall](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/robert.wall/32/38246_2.png) [@Robert.Wall](https://community.openenergymonitor.org/u/Robert.Wall)\
**Post date:** [3 November 2026 13:34 UTC](https://community.openenergymonitor.org/t/question-for-the-electrically-minded-single-phase-230-v-air-to-water-heat-pump-on-a-230-v-phase-to-phase-supply-with-no-neutral/30580/2 "2026-11-03T13:34:47Z")

</div>

In theory, and in UK practice, the neutral and the Protective Earth should be kept separate as the Neutral is (in the UK) regarded as a live conductor, even though it is _usually_ only a few volts at most different from earth potential. The only components you might have connected Line to Earth or Neutral to Earth would be those you mention for interference and noise suppression, and these should be rated for the full line voltage anyway.

However, I would strongly recommend you either go back to the post-sales team and ask them to get a definite ruling from the designers, who may well need to refer the question to the suppliers of the various components (particularly the inverter); or you ask a local professional electrician or electrical engineer, or you ask your local government body which regulates electrical installations.

> [@aech22](#):
>
> Has anyone run a 230 V unit phase-to-phase and seen a fault code?

I doubt if anyone here has. As I understand it, the system you have (3-phase 230 V Line-Line) is gradually being removed wherever possible in the few places it remains.