Your other option would be to try increasing the modulation as that should lower the flow temperature off of the weather dependent curve as you reach the desired room temperature.

Fair warning mine is back in 5 as I found it a bit hit and miss from my experimenting but I am still waiting 4 replacement radiators so will be playing again in a few weeks.

---

<div class="post-metadata">

**Author:** ![swayze](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/s/ba9def/32.png) [@swayze](https://community.openenergymonitor.org/u/swayze)\
**Post date:** [28 February 2024 22:58 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/22 "2024-02-28T22:58:49Z")

</div>

Hi all, recently had a EDLA08 installed with the Madoka but no additional monitoring as yet.

Have been playing with different settings but with the wild changes in temperatures recently I’m struggling to figure out whether LWT or tweaks I make are any improvement.

Would you mind sharing the latest weather curve settings you’re using to give me a fresh starting point?

---

<div class="post-metadata">

**Author:** ![KnightPhoenix](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/knightphoenix/32/28571_2.png) [@KnightPhoenix](https://community.openenergymonitor.org/u/KnightPhoenix)\
**Post date:** [29 February 2024 16:48 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/23 "2024-02-29T16:48:58Z")

</div>

I will upload an export from my MMI after I have finished another Air purge. That should show you all of the settings I currently have configured.

Just remember that your WDC should be based on heat loss calculations and the minimum Radiator output and then fine tuned to suit your requirements / how hot you like the property.

While you can just copy settings from another unit this will likely not be suitable for your house and could leave you with a worse COP.

Be sure to take a copy of the MMI Export (from the installer menus) before making changes so that you are able to revert if needed.

---

<div class="post-metadata">

**Author:** ![KnightPhoenix](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/knightphoenix/32/28571_2.png) [@KnightPhoenix](https://community.openenergymonitor.org/u/KnightPhoenix)\
**Post date:** [29 February 2024 16:53 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/24 "2024-02-29T16:53:45Z")

</div>

@mortstar

Interesting item I have found this afternoon, Dropping the DT from 5 to 3 has given me a more consistent run with higher flow rate and less of the bouncing up and down in modulation when running.

My run at 14:20 stabilized around 15:30 and then until I started an air purge at 16:40 it was consistently better with modulation in flow rate (actually running above minimums 6-7l/m) and stable DT.

The house still seems warm and the COP is higher and more stable. May be worth looking into for the smaller Daikin Units.

---

<div class="post-metadata">

**Author:** ![mortstar](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/76d3ee/32.png) [@mortstar](https://community.openenergymonitor.org/u/mortstar)\
**Post date:** [29 February 2024 17:44 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/25 "2024-02-29T17:44:53Z")

</div>

Ahhh interesting finding, I did experiment with both larger and smaller dTs previously (+/- 1C from 5C which is my default), but to be honest I was changing other settings at the same time, so my tinkering was not that scientific, as it seemed that a change in dT didn’t make a difference to the “saw-tooth” power usage that I saw of my system.

I spotted yesterday that the [6kW Altherma in Whitchurch](https://heatpumpmonitor.org/system/view?id=80) (same size as my HP) was running with dT of ~3C and was also able to run flow temps ~28C consistently with draw of ~300W, getting long-runs with COP around 5. My system cycles as soon as I set below 31C and a draw of ~420W seems to be my minimum level at the moment, will experiment with a lower dT and see if my heat pump settles like yours.

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/b/f/bf07a34e48bd164c6fc072de8d753d8e6f64a53d.png)

The upcoming forecast is really good for experiments with this system with highs around 10C and lows down to -2C for the next couple of days in my area.

---

<div class="post-metadata">

**Author:** ![KnightPhoenix](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/knightphoenix/32/28571_2.png) [@KnightPhoenix](https://community.openenergymonitor.org/u/KnightPhoenix)\
**Post date:** [6 March 2024 13:37 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/26 "2024-03-06T13:37:28Z")

</div>

Sorry for the delay here,

My current settings are attached here.

This includes the DT 0f 3 but I have yet to see how this behaves fully on the coldest days.  
[Farnborough,Hampshire\_March06-EDLA08E2v3\_DaikinMMI-export.txt](https://community.openenergymonitor.org/uploads/short-url/uM3dqpE9n4O5PvLsogPBcL3gUie.txt) (6.8 KB)

Again this is what is currently working well in my house, please do not take this and just copy paste as it may not be suitable for everyone.

Before making changes please backup your settings and make notes so you can revert them if this breaks anything.

---

<div class="post-metadata">

**Author:** ![KnightPhoenix](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/knightphoenix/32/28571_2.png) [@KnightPhoenix](https://community.openenergymonitor.org/u/KnightPhoenix)\
**Post date:** [6 March 2024 13:38 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/27 "2024-03-06T13:38:15Z")

</div>

@mortstar,

How did you get on with updating the DT, di this help in your situation at all?

---

<div class="post-metadata">

**Author:** ![meatballs](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/meatballs/32/20896_2.png) [@meatballs](https://community.openenergymonitor.org/u/meatballs)\
**Post date:** [7 March 2024 23:39 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/28 "2024-03-07T23:39:54Z")

</div>

Is the settings export standard on the MMI? I don’t think I’ve ever seen that in my installer menu - do you need to plug in a USB?

---

<div class="post-metadata">

**Author:** ![KnightPhoenix](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/knightphoenix/32/28571_2.png) [@KnightPhoenix](https://community.openenergymonitor.org/u/KnightPhoenix)\
**Post date:** [8 March 2024 00:42 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/29 "2024-03-08T00:42:12Z")

</div>

It is at the bottom of the installer menu. You need to plug in a usb stick that is fat 32 formatted and you can save the configuration but cannot re import a configuration file.

---

<div class="post-metadata">

**Author:** ![tiger\_cook](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/tiger_cook/32/27858_2.png) [@tiger\_cook](https://community.openenergymonitor.org/u/tiger_cook)\
**Post date:** [8 March 2024 08:13 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/30 "2024-03-08T08:13:02Z")

</div>

I think it works thanks @KnightPhoenix, just one change setting the DT to 3 - after one heat cycle with similar outside temps the COP appears smoother and higher -

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/3/f/3fc8f035e60229b650271c2b3bb8165ab486dd65.png)

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/7/4/74f28f3009099c5e9224611d0968a3c914983d92.png)

---

<div class="post-metadata">

**Author:** ![mortstar](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/76d3ee/32.png) [@mortstar](https://community.openenergymonitor.org/u/mortstar)\
**Post date:** [8 March 2024 22:23 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/31 "2024-03-08T22:23:43Z")

</div>

> [@KnightPhoenix](#):
>
> How did you get on with updating the DT, di this help in your situation at all?

Yes I did make the change to a dT of 4 (from 5) and I would say that it has slightly improved COP and slightly reduced energy consumption which is definitely a win:win!

As you mentioned, I see my 6kW unit modulate flow rate much more readily with this lower dT, before it would just stick at the lowest possible flow ~6.75 l/min.

I’d like to further reduce to a dT of 3, to see what impact that has. But before making that change, it’d be really useful if the ability to [compare a system on heatpumpmonitor.org](https://community.openenergymonitor.org/t/heatpumpmonitor-org-tips-comparing-a-system-to-itself/25271/2) was working again (to empirically compare the data of the system to itself, rather than going from gut-feel and assumption).

---

<div class="post-metadata">

**Author:** ![swayze](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/s/ba9def/32.png) [@swayze](https://community.openenergymonitor.org/u/swayze)\
**Post date:** [8 March 2024 22:56 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/32 "2024-03-08T22:56:11Z")

</div>

Thanks for sharing Zak. Ours is a retrofit and I’m having to judge things from the Daikin controller and our solar setups electricity usage monitoring which seems less than ideal.

I had noticed that my flow rate sticks at 7-8, thought it might be that the filter was full, it needed a bit of a clean but wasn’t too bad. Dropping dT to 3 has doubled flow rate, efficiency looks better though energy usage up.

Any recommendations for running pump as continuous or sample? If sample is the 60% setting the consensus?

---

<div class="post-metadata">

**Author:** ![KnightPhoenix](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/knightphoenix/32/28571_2.png) [@KnightPhoenix](https://community.openenergymonitor.org/u/KnightPhoenix)\
**Post date:** [9 March 2024 00:41 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/33 "2024-03-09T00:41:45Z")

</div>

Don’t worry, I am on heat pump 2 and in the middle of doing a lot of renovations to the house.

I have not set any pump restrictions and you will be able to check this from the export above, all of the codes in the export are listed in the installer reference guide available from Daikin (or Google “Daikin edla04-08ev3 installer reference guide”).

My only concern with the lower DT is how the system will perform on cooler days. Hy hope is that as it is in fancoil the system will just let the DT spread as needed and keep the house warm but unless I get another cold day this year it may be a while before I can confirm.

Still seems to be running a bit high as the room temperature is still creeping up (all be in by 0.1°c an hour or so) so may have to dial in the WDC some more.

---

<div class="post-metadata">

**Author:** ![Fallingdownhouse](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/fallingdownhouse/32/32521_2.png) [@Fallingdownhouse](https://community.openenergymonitor.org/u/Fallingdownhouse)\
**Post date:** [13 December 2024 13:53 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/34 "2024-12-13T13:53:07Z")

</div>

Hi Afraid I’m asking a question rather than answering yours! I have the same heat pump as you, how do you get such good data out of it? I pressume its a 3rd party software as all I get is hourly energy usage. Would be great to get the sort of detail you seem to have.

Thanks  
Ben

---

<div class="post-metadata">

**Author:** ![tiger\_cook](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/tiger_cook/32/27858_2.png) [@tiger\_cook](https://community.openenergymonitor.org/u/tiger_cook)\
**Post date:** [13 December 2024 14:09 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/35 "2024-12-13T14:09:03Z")

</div>

Hi Ben, check out -

> [@Daikin Altherma, ESPAltherma & Home Assistant with OpenEnergyMonitor](https://community.openenergymonitor.org/t/daikin-altherma-espaltherma-home-assistant-with-openenergymonitor/25057):
>
> Hi, I’ve started a thread to gather all the information needed to integrate a Daikin Altherma, ESPAltherma & Home Assistant with OpenEnergyMonitor I am a little disappointed with the Daikin Stats (SCOP and COP) from the API and display, I have tried speleolontra/daikin\_residential\_altherma integration from HACS… any useful guides or snippets of information would be fab, thanks @squarepeg77 @matt-drummer @Stephen_Crown slight_smile

---

<div class="post-metadata">

**Author:** ![KnightPhoenix](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/knightphoenix/32/28571_2.png) [@KnightPhoenix](https://community.openenergymonitor.org/u/KnightPhoenix)\
**Post date:** [31 December 2024 15:39 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/36 "2024-12-31T15:39:32Z")

</div>

Hey @Fallingdownhouse,

I personally use the heat pump monitor level3 kit and it is absolutely brilliant and while you need a plumber and electrician to install it is very well built and the team really do provide top notch customer support.

For a quicker / cheaper option you can use the ESPAltherma/ P1P2SERIAL route but this grabs data from the ASHP and as such you are relying on the data from the ASHP being accurate (no telling how far out it could be) and not external MID certified meters, where the accuracy is guaranteed to be within a specific tolerance.

Either will give you a good idea of where your unit is at and an approximate COP but the OEM kit is more helpful for the fine tuning and tweaking once you get down to granular system optimisation (is dt3 or DT10 better for my system, how does an unbalanced system behave as opposed to a fully balanced system etc.).

---

<div class="post-metadata">

**Author:** ![scigulinsky](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/scigulinsky/32/32962_2.png) [@scigulinsky](https://community.openenergymonitor.org/u/scigulinsky)\
**Post date:** [5 January 2025 22:31 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/37 "2025-01-05T22:31:41Z")

</div>

Hi @mortstar Sam. I am a fellow ashp user from Oxfordshire (Banbury) and just found your discussion with Zak @knightphoenix. I have been first time trying to tweek my pump after £10 bill for Friday 🫣 it’s 8kw installed in June by octopus, I have espaltherma running with HA and bought some feeds just can’t get them to work yet. Zak kindly provided me with a link to some instructions but still stuck.  
Now question, what is your settings currently. I have reduced my curve to 40 at -3 from 50 at -8 and I can see huge difference already. I have modulation at 3 or 4. Still learning the terms. Sorry for long post

---

<div class="post-metadata">

**Author:** ![mortstar](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/76d3ee/32.png) [@mortstar](https://community.openenergymonitor.org/u/mortstar)\
**Post date:** [6 January 2025 15:35 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/38 "2025-01-06T15:35:06Z")

</div>

Hi @scigulinsky, the settings for my system are described in my system notes at [HeatpumpMonitor.org](https://heatpumpmonitor.org/system/view?id=162)

Obviously you should adjust the WDC to your own property; what works for mine, may not be accurate for yours. Having said that, unless you have **a lot** of heat emitting capacity (like @matt-drummer) you will almost certainly not be able to run your LWT below 30C without a lot of cycling.

I’ve tuned my system for most cost-effective running rather than aiming to be Top of the SCOPs. My goal is to have a comfortably warm house with abundant hot-water for a family of 4 (young kids who are still having baths rather than showering 🛁), which is what we get from our setup.

---

<div class="post-metadata">

**Author:** ![scigulinsky](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/scigulinsky/32/32962_2.png) [@scigulinsky](https://community.openenergymonitor.org/u/scigulinsky)\
**Post date:** [6 January 2025 20:21 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/39 "2025-01-06T20:21:59Z")

</div>

![Screenshot_20250106-195556](https://community.openenergymonitor.org/uploads/default/original/3X/d/d/dd96969ffe6cf8c0e2b696171d5701bd51deef74.png)  
I will check your setting, so far I have tweaked it a bit and the efficiency is so much better already without compromising the heat (we do like to have house at 21-22 degrees) and same foe water as family of 5. I am surprised that small changes can make massive difference. I have digital trv on most radiators but my best indicator is happy wife 🤣

---

<div class="post-metadata">

**Author:** ![Rharrod](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/r/d26b3c/32.png) [@Rharrod](https://community.openenergymonitor.org/u/Rharrod)\
**Post date:** [27 January 2025 23:42 UTC](https://community.openenergymonitor.org/t/pushing-for-cop-5-on-daikin-edla08e2v3/25446/40 "2025-01-27T23:42:42Z")

</div>

Hi Zak, my install of the same 8kw Daikin as yourself started today, I’ve been very impressed with your Scop over the last 12 months or so and I was just wondering what flow temps your able to run at? What do you have your weather compensation set to (max/min)? Wondering if you’ve tweeted them since jan last year in your first comment on this post?  
I know my system is likely to be different to yours but I’ve managed to get Octopus to install much larger rads across my house so there’s a very good chance I can drive my flows significantly lower than the original design.  