No, you want the process “Wh accumulator” and look at the 'Help" associated with that:
Wh Accumulator: Use with emontx, emonth or emonpi pulsecount or an emontx running firmware emonTxV3_4_continuous_kwhtotals sending cumulative watt hours.
This processor ensures that when the emontx is reset the watt hour count in emoncms does not reset, it also checks filter’s out spikes in energy use that are larger than a max power threshold set in the processor, assuming these are error’s, the max power threshold is set to 60 kW.
[Apologies for the rather misleading punctuation.]
You may keep “Log to feed” if you wish (if you want to keep the raw pulse count) and add “Wh accumulator” and a separate feed that will retain the accumulated value. I think the accumulators handle decimal values, so you can add a scaling factor above the accumulator if your pulse does not represent 1 Wh.