# Power1pluspower2 calibration in Emonhub

**URL:** <https://community.openenergymonitor.org/t/power1pluspower2-calibration-in-emonhub/14341>\
**Category:** Emoncms\
**Tags:** emonhub\
**Created:** [31 May 2020 15:49 UTC](https://community.openenergymonitor.org/t/power1pluspower2-calibration-in-emonhub/14341 "2020-05-31T15:49:42Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![PhilSprague](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/philsprague/32/10444_2.png) [@PhilSprague](https://community.openenergymonitor.org/u/PhilSprague)\
**Post date:** [31 May 2020 15:49 UTC](https://community.openenergymonitor.org/t/power1pluspower2-calibration-in-emonhub/14341/1 "2020-05-31T15:49:42Z")

</div>

I have calibrated the two CTs that I have connected into power1 and power2 channels and put the calibration values in the Emonhub. I have been using the power1pluspower2 input to calculate the house load and then used that in the MySolar app. Can anyone tell me if I need to calibrate the power1pluspower2 input in emonhub as well or does it take the values needed for each CT from the respective Emonhub power1 and power2 inputs ?

Sorry if this is already written up somewhere but I couldnt find it.

---

<div class="post-metadata">

**Author:** ![Robert.Wall](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/robert.wall/32/38246_2.png) [@Robert.Wall](https://community.openenergymonitor.org/u/Robert.Wall)\
**Post date:** [31 May 2020 16:06 UTC](https://community.openenergymonitor.org/t/power1pluspower2-calibration-in-emonhub/14341/2 "2020-05-31T16:06:35Z")

</div>

Unfortunately, you cannot calibrate ‘power1pluspower2’ accurately. It is derived in the front end Atmel '328P sketch before the data reaches emonHub. Any calibration you apply in emonHub will therefore be a compromise, because it won’t know the proportion to allocate to the two parts.

I suppose, if you’re really keen, you could apply the calibration inside emonCMS - on the inputs page, by adding a tiny fraction of power1 and a different fraction of power2 to the sum. It should work.

The reason for sending the sum value was because the two inputs could end up separated by 5 s due to timing differences. If you add the correction in emonCMS, that could apply to the correction, but it’s a second-order effect, so it might not worry you.

> [@PhilSprague](#):
>
> Sorry if this is already written up somewhere but I couldnt find it.

Don’t worry, I doubt very much that it’s written anywhere.

---

<div class="post-metadata">

**Author:** ![PhilSprague](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/philsprague/32/10444_2.png) [@PhilSprague](https://community.openenergymonitor.org/u/PhilSprague)\
**Post date:** [31 May 2020 16:11 UTC](https://community.openenergymonitor.org/t/power1pluspower2-calibration-in-emonhub/14341/3 "2020-05-31T16:11:34Z")

</div>

Thanks Robert. I think I’ll just use the two separate inputs and ignore power1pluspower2. I’m not sure I’m going to be particularly bothered by a few seconds difference between the two values.