Hi all, thanks for the replies.
Today I spent 5 hours testing the system and I still think the unit is under sized.
So, outside temp was around 9.5 degrees +/- 1 degree. I set up 6 temperature monitors on the system mainly around the buffer and asked for 30 degree on the sensocomfort. Target temp went to 44 degrees and compressor continued to ramp up throughout the test.
After approx 40mins the unit went through its first defrost. I’ll attach the excel spreadsheet to show figures, I would try and chart them but not exactly up to speed with excel.
From the start of the test to the defrost time was 40 mins and I lost approx 5 degrees temperature from the buffer during the defrost, which doesnt seem terrible?
The unit continued to ramp up targeting the 44 degrees over the next hour where increased from 28 degrees to 36 degrees. Seems slow?
The delta T between the buffer inlet and outlet (points 1 & 2 on the hot side) was negligible all the way up to 36 degrees, averaging less than 0.5 degree. Although I did see an increase in temperature across the buffer on the cold return side back to the heat pump, it was picking up approx 1 degree, which again doesn’t seem too bad, maybe a sensor out of calibration slightly. At this point I had the buffer pump on minimum and the UFH pump on the mid setting.
As the flow temp got closer to the target temp the compressor started to modulate down, at this point I increased the weather curve to MAX 4.0 from 0.4 and increased my max flow temp to 55. The unit then targeted the 55 degrees.
At this point I also did a temp survey across the UFH manifold (results attached) and found that the average delta T was 7.4 degrees (6.2 min, 9 max) which I (maybe incorrectly) thought was too high and the ideal was 5 degrees? So I sped up both the buffer pump and UFH manifold pump to max (to confirm all of the flow valves are already fully open.) After the speed ups the delta T across the UFH circuits decreased to 6.6 degree average (5 min, 7.9 max)
After I increased the pump speeds the Delta T across the circuits got better but caused the delta T across the buffer to worsen. On the original pump speeds I losing less than 0.5 degree across the buffer but this widened to 1.5 degrees.
I also did a survey across the rads which i’ll attach.
Sorry to throw a load of figures at everyone but I think it boils down to this, my design flow temp is 46 degree’s @ -1.79 outside temp. After testing the highest temp I reached was 40.5 degrees @ 9.5 outside temp, that seems well short. The flow temperature seemed to plateaux after 5 hours so I dont think it would ever reach 45 degrees @ 9.5 never mind -1.79!
Day to day the house is fine, it never feels cold. During cold spells (below 2 degree’s) the house loses temperature but again has never felt cold. My weather curve is 0.4.
I have attached a few spreadsheets/drawings to show my findings if anyone is interested and can send any advice my way. I really appreciate your help so far.
A few questions since doing the test:
- Shall I stick with a better delta T across the UFH circuits and a worse delta T across the heat pump or revert the pump speeds back to before?
- I discovered the average delta T across my rads was 2.7 degrees (min 1.0, max 5.3) what should I be aiming for on the rads? They are aluminium if that makes any difference.
- Looking at one of the coldest days of the year so far on the vaillant app (outside temp 2 degrees) my heat generated for that day was 2.5kWh per hour. My calculated heat loss by the designer is 5.5kw, does that mean my heat pump is less than half the size of what I need on a cold day? To compare looking at todays heat generated I averaged 9.2 kwh per hour, but that is at 10 degrees outside temp.
- On my sensocomfort I have 3 circuits. Circuit 1 UFH, Circuit 2 Rads, but I have no idea what circuit 3 is? Is my sensocomfort set up wrong?
- The vaillant temperature sensors for UFH and rad circuits have a discrepancy of approx 3 degrees, they should be exactly the same temperature. Could this cause issues? Miscalculations?
- What is my next step? Does it sound like an undersized unit? Are there any mods I could retrofit to help my situation? (i.e. back up heater) Or do I go down the route of getting the supplier to replace as it doesnt meet the criteria/figures they said it would?
Sorry about the essay, I’ve had a guts full of typing “delta” thats for sure 
Any more help/info is greatly appreciated, thank you all
UFH_Delta_T_Comparison.pdf (47.3 KB)
UFH manifold temperature survey - Sheet1.pdf (30.7 KB)
Rads survey - Sheet1.pdf (33.3 KB)
ASHP testing.xlsx (193.3 KB)