Youâre using the same sketch as before?
Which version of emonLib?
Have you checked voltages?
The 5 V rail from your Arduino?
The midpoint - the junction of R1 & R6, with and without a plug inserted?
Is the 33 Ω burden present & correct?
Robbrad
(Rob)
23
Yep same sketch as before and same sketch as the working shield but different channel.
Iâm not using the 5v rail from the Arduino, Just usb power.
Ct sensors work on port 2 3 and 4, see screenshot but port 1 is the one reading high.
Resistance on main resistors looks good
R5 to R16 reads 33k
How do I check the mid point
Iâm not sure what you mean there - R16 is a placeholder to give the holes for a wire-ended component to replace R5 if the burden needs changing. R5 should be 33 Ω.
Measure the voltage from R5 (either end) to GND. It should be zero without a plug inserted. Youâll need to insert a plug to remove the âinnerâ connection to GND on the socketâs switch contacts to read a voltage, which should then be half-supply, 2.5 V
Also check that voltage makes it to the Arduino itself. Or check continuity. We have known broken tracks.
Robbrad
(Rob)
25
Let me check that.
Bit more info for you
Without the 9v ac connected I get solid zero readings on serial monitor
Soon as I connect the ac 9v I get the high reading
Robbrad
(Rob)
26
R5 to GRD with no plug is zero
With plug itâs 2.5
That doesnât mean too much. The a.c. input is obviously zero, or close, and anything multiplied by zero is zero. So the sketch is doing what it should under those conditions. So I conclude itâs seeing rubbish on the current input pin, to give the big numbers. The maximum reading should be around 24 kW (100 A @ 240 V), so itâs less than that.
Check the pcb for whiskers of copper, because the tracks for the a.c. input and Channel 1 are adjacent. But the favourites are a broken track, dry joint or faulty connector.
Robbrad
(Rob)
28
There is definitely something up with the ct1 spot
When starting up the settle period is zero for it
I wouldnât expect much. The latest emonLib uses a low pass filter, which is initialised to half-rail, to extract the bias voltage, which is then subtracted. So it only has to move from the nominal bias point to the actual bias point, which should be only a few counts.
Robbrad
(Rob)
30
Iâm stumped. I tested a lot of the continuaty nothing looks out of sorts.
Itâs got to be something so stupid that it canât possibly be wrong - yet it is.
Iâm assuming youâre using the same Arduino, which you know is OK - is that correct?
It looks to me as if the ADC input is floating and not held down by the burden & bias network. Itâs very high impedance and Iâm suggesting itâs picking up enough of the a.c. adapter voltage from the adjacent track or pin to give you numbers. Did you check continuity of this input from R5 right through to the Arduino board itself?
If that still looks OK, can you check the raw numbers coming from the ADC? Load one of Robin Emleyâs test sketches, they are all listed at Robin's Mk2 Code variants and associated tools. | Archived Forum
Either âRaw samplesâ or âMin and maxâ, should show a steady half-scale with the c.t. plugged in but no current. (Have the a.c. voltage present.)
Sorry I havenât come back, finally had chance to try the shield on another Arduino. Same issue
I think the shield must have an issue or my soldiering somewhere.
Iâm just gonna leave it for now. I have resurrected the old shield with the CT sensor ports on the wrong side, re-soldered them and itâs working fine.
I might test it again but for now Iâm happy. Thank you for your help @Robert.Wall
I have managed to push the data to Graphite and Grafana. The dashboard is beautiful.