Sorry for the delay, was busy in other stuffs and after I could dedicate time to this.

Thanks @calypso_rae, but that’s what I want to avoid, the need to use TX for size reasons, meanwhile smaller is easier to install in any cabinet.

@Robert.Wall I solved the issue… There was a broken link between neutral and the DC step that I’m using as reference, I installed a wire bridge, and now it is measuring ok, when there is a voltage terminal to air (not connected) it measures 1.3V, and the other two phases measures 118V (the same measure when the three voltage terminals are connected), and when I attach it to neutral measures 0.35V (other two phases remains 118V), I know that it should measure a big 0, haven’t applied the recomendations of your previous post, but at this point I’m satisfied with the results.

Thanks again.