New heat pump Grant R290 - hot water advice

Thanks!

I’ve added a plot showing ‘outlet temperature’ in red and ‘inlet temperature’ in blue which are hopefully the equivalent of LWT and RWT, covering the last four days. The temp sensor seems to be about 1/5th of the way up the tank, so pretty close to the bottom.

Haven’t contacted installer yet - thought I’d have a go at fixing it myself first but failing that I’ll contact them.

Hmm, your poor DHW temperatures look like they may be a result of low/varying LWTs. If you haven’t changed any settings over the period in question, then there’s a problem with the Outdoor Unit.

Inability to reach the higher LWTs associated with DHW heating is a classic symptom of loss of refrigerant, and your observation that the problem appears to be progressive (over several weeks/months) suggests a small leak in your propane circuit.

If there is a leak, then you’ll lose your space heating as well over the next few weeks - not what you want with winter approaching.

I’d say @micks_address is absolutely right - get your installer in asap to check your propane inventory, locate and fix any leak if the inventory is low, and recharge the circuit.

Ok thanks very much for the advice

running last week or so now with pump blockade disable.. curve of 7, shift of 2. room correction 4. It hasnt gotten really cold yet but a lot of time the power usage is around 442 watts which is awesome.. house is plenty warm… probably still a little to warm at times…

I’ve been experimenting with no Room Temperature Correction i.e 0C.

I’ve found it runs a lot smoother without room temp correction. Either way, I would recommend everyone try and run it for a while with room temp correction set to 0C to check if the WC curve is set correctly. Room temp correction can mask an incorrectly set WC curve.

Thanks mine was at zero. I might put I back to that and see how it goes. Seemed to be default out of the box

Mine was 4C out of the box, but I can see from recent version of the Smart controller manual that they have changed this to 0C in recent firmware versions. It looks like they’ve realised that maybe using room temp correction when it’s not needed causes instability and inefficacy and masks an incorrect WC curve.

Thanks that would validate what Grant told me that my unit came with the most recent firmware

Very nice.

Mine seems pretty stable with 2C correction (see below) but I’m confident that my weather curve is set up well. The room temperature hardly varies from the target so there isn’t a difference to correct for.

I’m going to experiment with 0C now.

NB: My comment about setting a mid-value of room temperature correction was related to reverse-engineering the optimum weather curve via the correction algorithm. You would need a moderate value in order to automatically adjust an incorrect curve. I agree that once your curve approaches the right settings, correction can be reduced towards zero.

A couple of questions / observations Glyn:

  1. Your room temperature looks a bit less stable after the switch to 0C correction. Have you noticed any difference?
  2. There are big swings in heat output when you were on 2C correction, but these don’t seem to relate to changes in room temperature (see below). I’m not seeing such big changes in flow temperature associated with equally small changes in room temperature at my house when on the same 2C correction. My understanding is that the algorithm would only adjust flow temperature if there was a difference between room temperature and the target. That difference can’t be changing much, because your room temperature is constant. Plus the outside temperature is fairly stable too.

Could there be another setting that is causing the divergent behavior between our systems? Or a firmware mismatch? I’m on SO24.27.

No, but there have been some sunny days recently. My controller where the temperature is coming from is a room which gets lots of solar gain, that’s the cause of most of the fluctuation.

Interesting. I’m not sure TBH. Having room temp correction enabled seemed to cause some oscillations, I assumed it was some sort of feedback loop. I did have to reduce the WC curve when I turned off room temp correction, so I probably had the curve set a bit high and room temp correction was constantly having to adjust down the flow temperature. Either way, I’ve been running for 1 year with room enabled, and it averaged a SCOP of 4.9 for space heating, so the oscillations don’t seem particularly detrimental.

I’m on SO24.25, I upgraded from SO23.13, but the FW update didn’t have any effect on this. The outdoor unit has never been updated since a Grant engineer visit is required to do this. I don’t know if there’s a way to tell what FW the outdoor unit is running? But a few of the new features introduced in SO24.25 e.g circ pump and fan manual speed control and purge function don’t work since my outdoor unit is running older FW.

That’s interesting to read. I might give that a try myself…

what heat curve/shift are you using now @glyn.hudson ? im on .7 curve with shift of 2 and room correction of 0

Currently, 0.3 curve and 6 shift. Although I’m anticipating needing to increase the curve when it gets colder. The Grant R290 curve simulator tool is useful for visualising this:

Every system and house will be different.

its interesting looking at the curve differences.. at ten degrees outside your target temp is 30 and mines 31.. changes a bit more as approaches zero outside.. im at 37 versus 33