I missed those. That’s one more reason NOT to link to third party sites, but to post all pictures here.
In that case, disconnecting the line inside the C.U. is possible, and a ring-core c.t. will be significantly smaller for the same rated current.
If space is at a premium inside the C.U, then knowing the maximum current you will see is important. There’s this range from RS https://uk.rs-online.com/web/p/current-transformers/7754903 which appear to be directly usable, but the maximum rated current is 50 A, so check the hole size as well as the outside dimensions (and note, if you fit one of these, it MUST be shorted while not connected, else it might be destroyed as there is no protection across the secondary winding).
I am going to open the consumer unit tomorrow and get some photos. I was looking at sensor above - it looks like I would need to connect it to a 3.5mm audio jack right, and possibly extend the cable in order to connect it to the emonPi.
You’re correct there. As the lead is only 120 mm long, you’ll almost certainly need to have a connector of some sort and further length of twisted flex to your jack plug - connect to tip and sleeve, there’s no connection to the ring (a mono plug should do too). As there’s no phase information on the c.t. data sheet, I can’t tell you which colour goes where, but note, the tip of the plug is “earthy” to a.c. but sits at 1.65 V d.c. above the emonTx or emonPi ground, and the true signal is the plug sleeve and body. I don’t advise using screened audio cable connected conventionally with the screen to the plug sleeve.
Note that if you’re using screwed terminals or crimps, then for reliability you must cut the tinned ends of the wires off.
Pictures of the consumer unit below as discussed. Looks like there should be enough room in there alright. Couple of points of note:-
Main Switch
External Heat Unit (collection fan)
Internal Heat Unit
I have two CT Sensors, so ideally I would like to monitor both the incoming supply to get the total, and the Thermia Air-to-water Heat Pump separately. Not sure how to monitor the Air-to-water system since it is split into two, which is the more important the internal or external unit?
Simple - pass both brown wires through the same c.t. The magnetic fluxes will add in the c.t., and you’ll see the total current. Just check what the actual ratings are - I can see one is a 32 A MCB and the other is a 40 A RCD - but I’m betting the total is not 72 A, though it might be too much, especially on the hole size, for the smaller 50 A AZ-1000 c.t. and you need the physically bigger ACX-1075. It’s hard to see how much space is available behind the breaker mounting rails - have a good look and measure (with a wooden or plastic ruler!).
So what I have are 2 x SCT013 that are rated for 50mA → 100A, these are what I got with the EmonPi. I doubt I am going to be able to squeeze both brown wires for the heat unit through the SCT013’s hole. I didn’t think to pull out the plastic calipers - but I was thinking/hoping I might get away with the SCT019? As there appears to be a good bit of room above the trips, it should be ok …
The ACX-1075, looks like I would need to make up a cable right?
I marked up the image with where I think I ought to be putting the C.T.'s, can you confirm that I am on the right track pls.
For the heat exchanger, those are the wires.
I’d have thought you would certainly get those 2 wires through a SCT-013-000. It’s hard to tell the wire size from the photo, a single core BS6004 at 4 mm² is rated at 32 A in conduit (so more than that given the air circulation that you have) and is 4.1 mm diameter overall. Likewise, a 6 mm² is 41 A and 4.6 mm diameter. If the installer went up a wire size, then the 10 mm² is 57 A and 5.8 mm diameter. My maths says a 6 mm² and a 10 mm² is less than 13 mm, which is the hole size you have.
For the main switch, the c.t. needs to go on wire into the bottom of the main switch, which should be the tail coming from the meter box outside.