Monitoring a Mitsubishi Ecodan R290 10kW Monobloc

Hi all,

I’ve been using OpenEnergyMonitor for years, including monitoring my home Daikin heat pump with an emonPi, emonTx and hacked-together ESPAltherma data. However I’ve never done it “properly” with an emonHP.

We’re about to get a new heat pump installed in a communal building, a Mitsubishi Ecodan R290 10kW Monobloc (PUZ-WZ100VAA). I’m not the only person looking after this system, so I want it to be “standard” and easy to use, and have the flexibility to build a more advanced control system later.

I’m considering emonHP as a cheaper, better, more open alternative to the Mitsubishi official EMP3-M-1PH level 3 monitoring system. However I’m confused by the options available on the shop page, and I’m not finding good documentation for this system, only forum posts and a PDF, and I would greatly appreciate your advice.

Heat meters

The installer wants to sell us a 10 kW heat pump. It may be oversized, but this is a large building (500 m2 floor area). I think he said the primary pipework would be 28 mm, and the fluid is fernox (he says that’s glycol? I’m not sure.)

I’m not sure what heat meters are compatible. The bundle options are Axioma DN20, Axioma DN25, Axioma DN32 and Sontex 789. It says the Sontex is glycol compatible, so I guess the Axiomas are not? But the Sontex is for smaller systems (7 kW max). Do I have any other options? Does it matter that the meter is DN20 when the pipework is 28mm? Should I go for the Sontex Supercal5 instead?

The shop page for both Sontex meters says “Antifreeze (Leave blank if not used): Glycol product and percentage. MUST BE SET PRIOR TO SHIPPING.” What happens if we don’t know, or if the percentage changes due to us refilling the system with water?

Plumbing fittings

I don’t understand what “Plumbing Fittings” I will need. The PDF says I need a DN20 to 3/4" BSP adaptor (presumably two) for a DN20 heat meter, but no such thing is listed on the bundle page. And I suppose I also need (two) 3/4" BSP to 28mm compression fittings? The bundle doesn’t seem to offer two of these so perhaps it doesn’t line up with reality? The Sontex Superstatic 789 ordering page says it has a “3/4” BSP Connection (DN20)“, so maybe no adaptor is required for it? Or is that only for copper pipes, and plastic pipes always need a compression adaptor? Do I also need 2 x 28mm compression 1/2” sensor tee for the temperature probes (the bundle options seem limited to only one)?

Electricity metering

The heat pump apparently does not include a backup heater, but there will be a booster/immersion heater in the DHW cylinder. What are the “indoor pumps” in “2x single-phase 45A (Required if indoor pump(s)” electricity metering? Is that for circulation pumps not included in the heat pump itself? If so then I guess I need “3x single-phase 45A (Required if booster heater)”? We already have Socomec power metering which will cover these circuits and is accessible by Modbus over TCP. I don’t suppose I can make emonHP read from that, rather than installing duplicate metering?

Low loss header

The installer says he needs to install a low loss header (which Heat Geek advises against) in order to ensure minimum flow rate if all radiators are off, and compatibility with the existing circulation pumps. I’m worried about the heat and efficiency losses caused by this header, and also I don’t know on which side to install the heat meter - before or after the header? Ideally we would have both, to measure the losses in the header, but I don’t think I can justify the extra cost.

Configuration

From my emonPi experience, there must be a ton of setup of inputs and feeds to collect the data from the M-Bus heat meter, the Modbus electricity meters and the DHW tank and valve sensors, calculate the heat generated and COP, and send them to heatpumpmonitor.org, but the only instructions I can find are here, is this the best source?

Modbus interface to HP

Should we also get the Mitsubishi PAC-IF082B-E (standalone FTC7 master controller, Modbus BMS ready) and/or the Procon MelcoBEMS MINI (A1M+) to collect additional data from the heat pump and control it by Modbus in future?

Many thanks again!

Chris.