> [@bontwoody](#):
>
> Long term is it worth looking at getting rid of it and switching to a direct circuit?

I’m not sure if it will be worth it. One experiment here concluded it made no difference:

- [Heat Pump Experiment | Protons for Breakfast](https://protonsforbreakfast.wordpress.com/2024/06/17/heat-pump-experiment/)

Broader thoughts in this topic:

- [Removing Low Loss Header on Samsung Gen6 System](https://community.openenergymonitor.org/t/removing-low-loss-header-on-samsung-gen6-system/25863)

It may be easier to balance the two pumps instead.

> [@bontwoody](#):
>
> Is 13 lt/m a bit on the low side for a 12 kW unit?

This is near the bottom of the range, but should still be good enough for it to operate.

> [@bontwoody](#):
>
> From data and a heat punk survey I did, I think the actual heat loss might be about 6-7 kW

What’s the total radiator output at DT50?

---