> [@Telepathic\_Walrus](#):
>
> The load was what i described earlier so defiantly not a ideal resistive load.

In that case, I wouldn’t worry about your c.t.

To show you the sorts of waveshapes that are possible, here’s a very spiky current waveform (Washing machine brushless d.c. motor on spin by @dBC [Phase measurement and correction in IoTaWatt - #17 by dBC](https://community.openenergymonitor.org/t/phase-measurement-and-correction-in-iotawatt/5811/17))

 ![spin](https://community.openenergymonitor.org/uploads/default/original/2X/e/e91b4689643cd1f465619909189f451b5ed135d8.gif)

And there’s a picture of a most distorted channel made up of a “boat load” of CFLs here  
[The importance of continuous sampling - #5 by dBC](https://community.openenergymonitor.org/t/the-importance-of-continuous-sampling/9659/5)

---