I´ve update to the new Continuous Monitoring firmware in my EmontxV3.4, i enable in the firmware to show current for calibration. All 4 CT´s show the same current after calibration but P1 is always 15w higher than P2,P3 and P4 is lower 30w of P2-P3.
MSG:13,Vrms:233.17,I1:1.57,I2:1.56,I3:1.57,I4:1.57,pf1:0.7637,pf2:0.7237,pf3:0.7326,pf4:0.6592,P1:279,P2:264,P3:268,P4:241,E1:10,E2:9,E3:10,E4:9,pulse:288
MSG:14,Vrms:232.34,I1:1.57,I2:1.57,I3:1.57,I4:1.57,pf1:0.7636,pf2:0.7240,pf3:0.7329,pf4:0.6597,P1:279,P2:264,P3:268,P4:241,E1:11,E2:10,E3:10,E4:9,pulse:288
MSG:15,Vrms:231.87,I1:1.58,I2:1.58,I3:1.58,I4:1.59,pf1:0.7649,pf2:0.7254,pf3:0.7346,pf4:0.6616,P1:281,P2:266,P3:270,P4:243,E1:12,E2:11,E3:11,E4:10,pulse:309
MSG:16,Vrms:232.81,I1:1.59,I2:1.58,I3:1.59,I4:1.59,pf1:0.7655,pf2:0.7266,pf3:0.7354,pf4:0.6621,P1:283,P2:268,P3:271,P4:245,E1:12,E2:12,E3:12,E4:11,pulse:336
MSG:17,Vrms:232.74,I1:1.59,I2:1.59,I3:1.59,I4:1.60,pf1:0.7677,pf2:0.7286,pf3:0.7373,pf4:0.6646,P1:285,P2:270,P3:273,P4:247,E1:13,E2:12,E3:13,E4:11,pulse:364
MSG:18,Vrms:233.07,I1:1.58,I2:1.57,I3:1.58,I4:1.58,pf1:0.7650,pf2:0.7251,pf3:0.7337,pf4:0.6610,P1:281,P2:266,P3:270,P4:243,E1:14,E2:13,E3:13,E4:12,pulse:389
I´ve plugged in a SONOFF-POW to compare and I have values like P2-P3…
What is reading wrong to get these different values on the Power??
What is the “float i4Lead” values for in firmware??