# Infer radiator spec and system volume using the MyHeatpump app

**URL:** <https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798>\
**Category:** Emoncms\
**Tags:** heatpumpmonitor\
**Created:** [16 November 2023 13:17 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798 "2023-11-16T13:17:06Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![TrystanLea](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/trystanlea/32/31_2.png) [@TrystanLea](https://community.openenergymonitor.org/u/TrystanLea)\
**Post date:** [16 November 2023 13:17 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/1 "2023-11-16T13:17:06Z")

</div>

I’ve added an experimental feature to the MyHeatpump app to try and infer radiator spec and system volume.

This can be found at the bottom of the power view, DETAIL section:

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/4/9/49a253d3af78c7df16f3ef0a8f9db611bb9f81c1.png)

**How to use it**

**Indoor temperature sensor & feed required:** These calculations require indoor temperature data to work.

1. Select a period with continuous stable output, flow and return temps need to be stable and not increasing during this period e.g 17:20 to 17:30 in the example below:

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/b/4/b437eee9ad863152d1b38a8975f0d792a8c6c198.png)

selected section:

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/2/e/2e47690468d441021cc943fb430adf9313294a19.png)

Emitter spec result: 15.6 kW @ DT50 (My heat loss calculation suggests it should be 15.0 kW, so not bad! considering there’s probably a few hundred watts emitted from pipes etc). Not expecting super accuracy here, this is very much ballpark figure. **The accuracy is impaired by needing to know an accurate picture of average indoor temperature, a single sensor in the living room is not necessarily representative of the whole house!**

DT50 here refers to the standard radiator datasheet output at 70C mean water temperature and 20C room temperature, a difference in temperature of 50K. I know that does not relate to heat pump temperatures but it’s the input required for the radiator output equation [https://docs.openenergymonitor.org/heatpumps/basics.html#radiator-output](https://docs.openenergymonitor.org/heatpumps/basics.html#radiator-output).

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/0/7/07f783c251a8817f570af5746025c266bfd56d76.png)

1. Click on ‘Use for volume calc’ to save this emitter output value. Zoom out and find a heat pump cycle where the system is warming up (a portion of the heat is going to heating the system volume):

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/e/7/e793b40f55378849797f1450ea3ef0f3257ad2f3.png)

Zoom in to select a part of the cycle where DT is fairly uniform:

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/2/b/2b360e671116ffc42efecbd2ae386b389be08bb0.png)

During this example period the average flow temperature was 30.3C and return temp 23.9C a mean water temperature of 27.1C. The average heat output according to the heat meter was 4.9KW.

My radiator system cannot output anywhere near 4.9 kW at 27.1C, the actual heat output to the room should be 15.6×((27.1-20)÷50)^1.3 = 1.23 kW. This means that 3.7 kW is going to heating the water, copper and steel in the system.

The 3.7 kW increases the system water temperature by 4.3K over ~10mins

```
system volume = heat input (Joules) / (4150 J/K.L x 4.3K)  
(3700×60×10.1)÷(4150×4.3) = ~125L

```

We can use this value to work out the effective system volume, which in this case the calculation suggests is about 125 Litres… Now my own calculation suggests that my system volume should be closer to 73L, not including the volume in the heat pump heat exchanger itself or the heat capacity of the copper pipe and steel radiators.

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/c/3/c32f2367f6d0d42ec4b5690aa3a65d70336f82ca.png)

Given the wide spread of system volume values that come out of this (for mine 100-134L is fairly typical), it’s not super accurate, it’s more of a rough indication.

---

<div class="post-metadata">

**Author:** ![TrystanLea](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/trystanlea/32/31_2.png) [@TrystanLea](https://community.openenergymonitor.org/u/TrystanLea)\
**Post date:** [16 November 2023 13:22 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/2 "2023-11-16T13:22:35Z")

</div>

Here’s an example result from Adam’s (HeatGeek) system which has much more system volume than mine (large cast iron radiators):

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/6/6/66ea333ef3a5d009b0c0a8a28615ba76e08f6658.png)

and system volume:

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/1/e/1ecf582fc2c1d27e18861bf837ac30c0853db12a.png)

---

<div class="post-metadata">

**Author:** ![marko](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/dbc845/32.png) [@marko](https://community.openenergymonitor.org/u/marko)\
**Post date:** [16 November 2023 13:24 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/3 "2023-11-16T13:24:29Z")

</div>

Excellent feature!

“Effective volume” might be a better label - you’re inferring how much water is circulating NOT how much water there is in the system

---

<div class="post-metadata">

**Author:** ![TrystanLea](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/trystanlea/32/31_2.png) [@TrystanLea](https://community.openenergymonitor.org/u/TrystanLea)\
**Post date:** [16 November 2023 13:43 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/4 "2023-11-16T13:43:20Z")

</div>

Thanks @marko yes that makes sense.

---

<div class="post-metadata">

**Author:** ![Timbones](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/timbones/32/20308_2.png) [@Timbones](https://community.openenergymonitor.org/u/Timbones)\
**Post date:** [16 November 2023 13:44 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/5 "2023-11-16T13:44:35Z")

</div>

Very interesting, Trystan. I’ve been playing with this all week and it seems to match [my system](https://heatpumpmonitor.org/system/view?id=1) quite well.

I calculate I have a total radiator output of **16,655 W** , and the app gives me figures around there.  
Some of my radiators have fans fitted to them, and I estimate they increase output by _25%_ on those radiators, taking the total output to **18,000 W**.

This morning started with 2 of the radiator fans not running (17,000W), and switched on at 6am. You can maybe see the effect they had on [this heating cycle](https://emon.cryosphere.co.uk/app/view?name=AirSourceHeatPump&readkey=bb72ba957b02fecf8fb85fb1d2868782&mode=power&start=1700106950&end=1700119570), as the flow temperatures drop in the second half when the fans turn on.

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/6/9/69a0dfe6a8503ebd6c415571a2c79f08d9ecf962.png)

In the flat bit before 6am, **16.8 kW** @ DT50. After the fans turn on the reported size is **18 kW**.

The indoor temp I’m been using is pretty coarse though; I have an alternate feed I might try that gives average house temp, see if that give better numbers.

The estimated volume seems to be about 130 litres. I have no idea if that’s right.

---

<div class="post-metadata">

**Author:** ![TrystanLea](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/trystanlea/32/31_2.png) [@TrystanLea](https://community.openenergymonitor.org/u/TrystanLea)\
**Post date:** [16 November 2023 13:49 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/6 "2023-11-16T13:49:48Z")

</div>

Thanks Tim, that’s great to hear!

Yes definitely take the system volume figure with a pinch of salt for now. I think it may need very specific conditions to be semi accurate. E.g if there is very little temperature rise later in a cycle it can suggest wildly large volumes.

---

<div class="post-metadata">

**Author:** ![Timbones](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/timbones/32/20308_2.png) [@Timbones](https://community.openenergymonitor.org/u/Timbones)\
**Post date:** [16 November 2023 13:55 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/7 "2023-11-16T13:55:09Z")

</div>

> [@Timbones](#):
>
> The indoor temp I’m been using is pretty coarse though; I have an alternate feed I might try that gives average house temp, see if that give better numbers.

I did measurements again using the average house temperature, which is about 1 C higher, and got figures **18.2 kW** and **19.8 kW** for the same heating period. 🤷‍♂️

---

<div class="post-metadata">

**Author:** ![TrystanLea](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/trystanlea/32/31_2.png) [@TrystanLea](https://community.openenergymonitor.org/u/TrystanLea)\
**Post date:** [16 November 2023 13:58 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/8 "2023-11-16T13:58:51Z")

</div>

It would be interesting to see how well the standard radiator output equation matches the data:

```
Delta_T = Mean water temperature (MWT) - Room temperature
Heat_output = Rated_Heat_Output x (Delta_T / Rated_Delta_T) ^ 1.3

```

[https://docs.openenergymonitor.org/heatpumps/basics.html#radiator-output](https://docs.openenergymonitor.org/heatpumps/basics.html#radiator-output)

---

<div class="post-metadata">

**Author:** ![TrystanLea](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/trystanlea/32/31_2.png) [@TrystanLea](https://community.openenergymonitor.org/u/TrystanLea)\
**Post date:** [16 November 2023 14:03 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/9 "2023-11-16T14:03:24Z")

</div>

I’d like to build a test setup in the office here at some point with a radiator, an inline variable output electrical heating element, say 200-1000W (to give an accurate known heat input). A heat meter for heat meter accuracy validation. Pressure sensors, variable speed pump. option to add pressure drop, option to add a volumiser. Option to turn fans on on the radiator and so on.

Would make for an easier way to validate some of these things!

---

<div class="post-metadata">

**Author:** ![Zarch](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/zarch/32/7947_2.png) [@Zarch](https://community.openenergymonitor.org/u/Zarch)\
**Post date:** [16 November 2023 14:39 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/10 "2023-11-16T14:39:43Z")

</div>

Tried this from this morning data, after completing the balancing/opening up of rads the other day.

Inferred emitter spec: 18.5kW @ DT50  
Inferred system volume: 98 Litres

That’s amazing, as I calculated rads and pipework to come to approx 95 Litres!! 😍

Rad sizes I can be sure of, but the pipework isn’t always going to be to the exact metre.

---

<div class="post-metadata">

**Author:** ![Timbones](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/timbones/32/20308_2.png) [@Timbones](https://community.openenergymonitor.org/u/Timbones)\
**Post date:** [16 November 2023 14:42 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/11 "2023-11-16T14:42:22Z")

</div>

> [@TrystanLea](#):
>
> It would be interesting to see how well the standard radiator output equation matches the data:

I’ve been working the other way: adjusting the heating parameters to match the equations:

> [@Calculating the optimal weather compensation curve](https://community.openenergymonitor.org/t/calculating-the-optimal-weather-compensation-curve/24799):
>
> Continuing the discussion from [Infer radiator spec and system volume using the MyHeatpump app](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/8) I’ve been combining the [formulas for radiator output](https://docs.openenergymonitor.org/heatpumps/basics.html#radiator-output) with my calculations of [heat loss coeffiecient](https://protonsforbreakfast.wordpress.com/2022/12/11/cold-weather-measurements-of-heat-transfer-coefficient/) to produce the optimal weather compensation curve for my property: Radiator output at Δ50: 18,000W Target room temperature: 19 C Heat loss coefficient: 260 W/K + 880 W Minimum heat pump output: 4,000 W (though this varies with COP) Flow - return delta: 5 K My calculations: Heat loss = (out…

---

<div class="post-metadata">

**Author:** ![TrystanLea](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/trystanlea/32/31_2.png) [@TrystanLea](https://community.openenergymonitor.org/u/TrystanLea)\
**Post date:** [16 November 2023 14:43 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/12 "2023-11-16T14:43:11Z")

</div>

> [@Zarch](#):
>
> That’s amazing, as I calculated rads and pipework to come to approx 95 Litres!! 😍

I wish it was that accurate on yours 😂 I was just trying to get reasonable values earlier and was getting numbers all over the shop 🤯

---

<div class="post-metadata">

**Author:** ![marko](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/m/dbc845/32.png) [@marko](https://community.openenergymonitor.org/u/marko)\
**Post date:** [16 November 2023 19:44 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/13 "2023-11-16T19:44:58Z")

</div>

> [@TrystanLea](#):
>
> Would make for an easier way to validate some of these things!

Where’s the fun in making it took easy. 😉

It doesn’t matter what the theory is. You have the actual “effective volume” and “effective emitter” outputs. Discrepancy is mostly imbalance.

---

<div class="post-metadata">

**Author:** ![redzer\_irl](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/r/7ea924/32.png) [@redzer\_irl](https://community.openenergymonitor.org/u/redzer_irl)\
**Post date:** [13 October 2024 18:49 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/14 "2024-10-13T18:49:23Z")

</div>

@TrystanLea Is there anything specific I need to do to be able to calculate the emitter spec?

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/d/c/dc7d12f0f60525023e48efcdf62c49da5da969d0.png)

---

<div class="post-metadata">

**Author:** ![Timbones](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/timbones/32/20308_2.png) [@Timbones](https://community.openenergymonitor.org/u/Timbones)\
**Post date:** [13 October 2024 19:03 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/15 "2024-10-13T19:03:42Z")

</div>

See first post on how to use this feature.

---

<div class="post-metadata">

**Author:** ![redzer\_irl](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/r/7ea924/32.png) [@redzer\_irl](https://community.openenergymonitor.org/u/redzer_irl)\
**Post date:** [13 October 2024 20:59 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/16 "2024-10-13T20:59:24Z")

</div>

Apologies, I didn’t realise the lines had to be essentially parallel. I have it sorted now.

---

<div class="post-metadata">

**Author:** ![ectoplasmosis](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/e/ba8739/32.png) [@ectoplasmosis](https://community.openenergymonitor.org/u/ectoplasmosis)\
**Post date:** [14 October 2024 06:22 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/17 "2024-10-14T06:22:19Z")

</div>

Would you be up for detailing your radiator fan setup?

---

<div class="post-metadata">

**Author:** ![TrystanLea](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/trystanlea/32/31_2.png) [@TrystanLea](https://community.openenergymonitor.org/u/TrystanLea)\
**Post date:** [24 October 2024 20:33 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/18 "2024-10-24T20:33:03Z")

</div>

Pleased to say the radiator and volume tool has been significantly upgraded. No need to zoom in any more or do a two step process to get a volume calculation. Just enable the tool in the detailed section of the power view and it tries it’s best to analyse the full window!

It also draws the heat output from the radiators in orange, vs heat that is absorbed in the volume:

System 75 example: [HeatpumpMonitor.org](https://heatpumpmonitor.org/system/view?id=75)

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/7/4/741aa83bdfac6419e5a35d5c258c32080497093a.jpeg)

![image](https://community.openenergymonitor.org/uploads/default/original/3X/0/2/02409427f4915b8b2b81e60b90e8518afc0bd333.png)

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/4/4/449d450b30fbea06369aac4c20aece6b2384df08.jpeg)

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/5/d/5dd12883ef0b45f1b6764355993e41243a1c60aa.png)

---

<div class="post-metadata">

**Author:** ![ajdunlop](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/a/6bbea6/32.png) [@ajdunlop](https://community.openenergymonitor.org/u/ajdunlop)\
**Post date:** [24 October 2024 21:33 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/19 "2024-10-24T21:33:14Z")

</div>

I guess you need to have some steady state in the window to give more accurate estimations?

---

<div class="post-metadata">

**Author:** ![ajdunlop](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/a/6bbea6/32.png) [@ajdunlop](https://community.openenergymonitor.org/u/ajdunlop)\
**Post date:** [24 October 2024 21:53 UTC](https://community.openenergymonitor.org/t/infer-radiator-spec-and-system-volume-using-the-myheatpump-app/24798/20 "2024-10-24T21:53:14Z")

</div>

This from today seems a bit unlikely for my system

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/c/1/c1117a66318267f735c1c17c8dc0ad480c7c0067.png)

[https://emoncms.org/app/view?name=MyHeatpump&readkey=9b87718992b6ed5756d94d4288059a6f&mode=power&start=1729638000&end=1729724400](https://emoncms.org/app/view?name=MyHeatpump&readkey=9b87718992b6ed5756d94d4288059a6f&mode=power&start=1729638000&end=1729724400)