> [@Dan\_Nichols](#):
>
> In your experience is auto-adapt good at getting the flow temperature close to the mimumum required to achieve target heat whilst avoiding cycling due to flow temperatures too low for the emitters?

It seems to do a reasonable job of finding the flow temperature necessary to achieve the minimum emitter output, without cycling. For my oversized system with not enough radiators, it typically settles at a flow temp of 37 C, which happens to be what I calculated to be the lowest stable state. Unfortunately, this is usually way more than the rate of heat loss, so I run it in scheduled bursts by adjusting the room temperature setting programatically.

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/f/6/f640e43ef0914d2fb0caf6f248fa343d8ea72d76.png)

I might give “quiet mode” another try, in the hope that it’ll reduce the power used at the start of a cycle, slowing the rise of flow temperature.

I’m not sure auto-adapt is the “best” control method, but does seem to work well and is the simplest out-of-the-box. I think I was getting better COP when I use custom code to tightly control the temperatures, and turning the heat pump off between cycles.

Other anecdotal experiences of auto-adapt over here:

> [@Anyone monitoring a new R32 Ecodan?](https://community.openenergymonitor.org/t/anyone-monitoring-a-new-r32-ecodan/19577/111):
>
> Having played around with our office Ecodan 8.5kW over the last year I now have one at home. It appears to be running more efficiently than the office one but that may be due to it being more appropriately sized for our house and oversized at work. It could also be errors in monitoring as the office one just has a flow sensor attached to the FTC but no electric meters so is estimating whereas at home I have an EmonHP level 3 setup. One thing I have been experimenting with, now that it has star…

---