Hot Water Cylinders for smaller heat pumps - surface area and standing losses

I’m planning to order an ASHP in the next week. It’s likely to be a 3.5 kW Vaillant aroTHERM Plus v2, or a 4 kW Grant Aerona 290. Family of 4, with 2x showers (both with drain water heat recovery at ~50% end-to-end efficiency) and 1x bath.

What DHW Cylinder options are there?

I’m looking for medium-to-large coil size, but also good standing losses. See below for reasons, but here is the table:

Make/Model Capacity (l) Coil (m²) Heat Loss (W)
Grant QR2SC180 168 3.2 50
Newark HG200A4 187 4.0 76
Newark custom 100mm ins 187 4.0 ~40
Vaillant VIH RW 175/5 B ES 173 1.85 58
Gledhill PLUHP180 158 2.5 49
Joule TCIMVH-0170LFB 168 2.5 58
McDonald EcoFlow 180 180 3.0 59
Telford TSMI170/HP 168 2.0 81
Telford TSMI200/HP 194 3.0 77
OSO DGC 200 191 2.6 43

Notes - McDonald and Newark both offer customisation options which would allow for more insulation. There are lots of other options, but with the exception of the Vaillant I have ignored anything with a coil under 2 m².

  • More efficiency is good (unless it never pays back - then the same money can do more good spent elsewhere!).
  • The heat pump is small, and will probably be in silent/ECO mode most or even all of the time (dense urban area) e.g. for the Grant this means an output power of 3.0 kW.
  • The showers use much less hot water than in a usual house due to the heat recovery - instead of 55 litres of DHW draw-off for a 10 minute shower, it only needs about 37 litres (and the cold water entering the bottom of the DHW tank is at about 24°C instead of 10°C).
  • Since incoming water at bottom of the tank will be relatively warm, that favours a larger coil to maintain heat transfer.
  • We only have one or two baths per week (no heat recovery on baths unless someone showers immediately after someone else has bathed - i.e. bath is drained as shower takes place).
  • We are on the Octopus Agile tariff (and likely to stick with it), so being able to raise the tank to a high temperature when electricity is free and perhaps skip a DHW run the following day sounds like a good idea.
  • A large coil size will allow higher cylinder temperature (for a given HP flow temperature), and good insulation will retain it for longer.
  • Our heating season is short (highly insulated house, and the cylinder will be in the SW facing kitchen with a lot of solar gain), so the lost heat from the DHW cylinder is even less useful than in most houses, and a nuisance for most of the year.

I’m thinking something around 180 litres (150 litres may well be OK too, but restricts the options further and allows less multi-day storage), does that sound about right?

The platinum option would probably be a Newark/HG Cylinder custom made with 100mm insulation, but I suspect the cost would never pay back (with a big heat pump and/or higher DHW demand it probably would, but we have neither). Considering their cost, I’m surprised the Newark/HG cylinders have such poor standing losses in their default specs.

Although a different situation (larger tank, and heat pump) this topic is also relevant: Newark HG DHW Cylinder ROI

Any other thoughts or make/model suggestions very welcome!

Plenty on here think I am mad, but I used a heat pump to heat DHW for several years. But tried doing a DHW heat by immersion for a few days, and about 11 months later it’s still set that way, driven by a simple immersion timer, outwith the control of the heat pump. It charges in cheap ToU tariff periods and via solar when the sun’s out. A direct cylinder is peanuts to buy compared to a heat pump cylinder, you don’t need a diverter valve and plumbing is really simple. If you want you can then heat pump heat in cheap cosy slots only until temp drop sub 6 degs, without have to to do DHW also via the heat pump.

A HG cylinder gives a great CoP, but takes an age to heat with a small heat pump and it’s it worth the £2000 over and above a direct cylinder - NO.

If you really want a heat pump cylinder just get a 3m² coil one in stainless steel or duplex material.

Thanks, but as I already said I don’t expect the HG cylinder to pay back, and thus I’m unlikely to go that route. With a direct cylinder, today I would have the option of heating with mains electricity at 25p / kWh or foregoing my solar export at 14p / kWh. Comparing the Gledhill above (2.5m² + 49W) with an equivalent Gledhill direct cylinder, the saving is £300. The payback period for the indirect cylinder is about 12 years and I would hope the cylinder would last longer than 12 years. It also wouldn’t qualify for the BUS grant.

But you said you were on Agile, immersion heat and house heating can be done at the same period. On eco mode doing DHW you could be doing that alone in a cheap period especially if you are chasing high temperatures.

Understand you are chasing the BUS grant, but why. Will it save you any money in reality? I chose to go DIY, heat pump cost me £2050 incl. VAT and pretty much, just ties into the UFH and MVHR heating coil.

Cylinder size is governed by number of bedrooms in the house, so MCS will define the size minimum, you can ask for larger not smaller.

Pipe routing and it’s insulation will more of a governing factor than cylinder jacket heat losses to overall area heat gains.

Yes - the cheapest quote I have had is £150 after the grant is accounted for.

If you are getting that cost great. My quotes were stupid and demanded a heat pump 3x bigger than I need - quoting 12kW, I have installed a 4kW

How many bedrooms/bathrooms/shower rooms do you have?

You’ve stated 4 people, which under MCS guidelines is going to result in a recommendation of either 210L or 250L cylinder (maybe even 300L if you interpret your 1 bath and two showers as three separate ‘bathrooms’ or does one of the showers also occupy the bathroom?) making all of those under consideration ineligible for the BUS grant (as MCS certification is a requirement, I believe). You need to be looking at larger cylinders for that size of heat pump / number of occupants if you want the grant.

See the relevant MCS docs here:

Also linked here for convenience:

I’ll have a read of the MCS docs you linked, thanks. It’s 3 bedrooms, 1 bathroom (8 litre per minute shower over bath) in use. There is also an en suite in the loft which has a toilet and basin at the moment, with future provision for a shower e.g. plumbing installed, but no shower actually installed as yet (the space is being used as a cupboard until I build the garden office next year with no tiling, or fixtures), so I might be OK? The shower waste water heat recovery reduces the hot water demand quite considerably (summer gas consumption for dhw is about 35 kilowatt hours per month). That’s under 50 liters per day, so having a 210 litre cylinder feels excessive.

There is only two of us in the house, we have a 210L, when heated by ASHP it was the right size heated to 47 degs, any smaller capacity would not have been big enough. Family of 4 would be looking at 210L as a very minimum 250 to 300L would be better if you want to heat once per day.

Your daily hot water demand is the greater of number of bedrooms + 1 (3+1=4) or number of people (also 4) times 45L = 4 x 45L = 180L

For the purposes of MCS certification, you may be able to get away with 180L as a 2-3 bed with one standard bath or shower.

We have a 160L tank with two people and reheat once per day. If 4 people were showering daily, it would not be big enough.

I tried that with 210L - wife most unhappy with luke warm water at the end of the day. Tried all different time of the day couldn’t get it to last a while day, so went to heat twice a day. Discussion on other forums state if you have two kids they will soon be teenage and get ready for a 300L to be depleted often.

Thanks. With shower waste water heat recovery at 50% end-to-end efficiency, our shower is relatively light on water usage.

Here’s a reasonable summary article: “Waste water heat recovery for showers - P&H Engineering”.

With a shower outlet temperature of 39°C, and an incoming mains water temperature of 7°C (Feb/March) the recovered-heat water is at about 23°C. This water is consumed by both the shower mixer’s cold intake, and the cylinder intake. With a store temperature of 50°C, an 8 l/min shower consumes 4.8 litres per minute of stored water (i.e 4.8 litres from the cylinder + 3.2 litres of heat-recovered water).

180 litres of stored water is then sufficient for 38 minutes of showering. 210 litres would do 44 minutes. It takes about a minute for the heat recovery to get to steady state, so say 34 minutes / 40 minutes, so with 4 showers in one day that would allow 8.5 minutes (180l cyl) and 10 minutes (210l cyl) per shower each.

250 litres would allow nearly 50 minutes of showering, which seems like a lot.

In summer I’d estimate about 20% longer would be possible (lower shower temperature and higher incoming water temperature).

Additionally, the bottom of the cylinder will be at 23°C instead of 7°C, so the heat pump only has to put in 66% of the energy as it would without the heat recovery (although the higher starting temperature will impact CoP a little) when reheating the cylinder.

These DHW requirements seem enormous to me. We currently have a 114l cyclinder which is absolutely loads. There are 2 of us, one bathroom. Nominally 3 beds, but 2 are offices, so actually only 1 bed. We never use more than about 35l of hot water in a day.

If I work out DHW usage over the year it’s 14l/person/day (1.6kWh/day) assuming 55C tank temp 10C. That does mean our demand is about the same size as the daily loss from these tanks in the standardised tests.

We currently just heat it with a top immersion - takes 20 mins to get a bath or 2-showers-worth of hot water.

Like Tim I am in the process of speccing a heatpump setup with a modern tank (The current one is so old it doesn’t have any built-in insulation - just one of those ‘petal-style’ jackets (and a lot of duvets)), (and it sprang a leak in 2008 which I epoxied up as a temporary fix just till we got a new tank, ‘soon’ !) so it really does need replacing and one that keeps some heat in for a while would be a welcome improvement.

Current favourite plan is a 150L Newark HG tank, with double insulation and a top immersion+temp sensor, encouraged by Glyn getting over a COP of 4 with a similar set-up (I had previously assumed DHW would always be much lower than that). 150l is the smallest tank one can get with the 4m2 coil.

I did look at zip-style heaters and just immersion-heating due to low demand, but that factor of 3-4 means it’s always better to use the (expensive) heat pump one has bought than any form of direct heating.

A very nice option I did see is Conga do a direct Gledhill tank with a PHE+controller and pump (and 5 temp sensors down the side of the tank) that allows stratified top-loading. The owners (2 people) are getting a COP of 3 on the DHW part with that (and Vaillant 5kW HP) and finding 120l tank to be plenty. Main problem with that is you’d have to DIY it if your installer is not Conga.

4 is a better COP than 3, but with much lower DHW usage, a smaller heat pump (3.5kW Arotherm) and a smaller tank, ours will be different. A £750 tank is clearly much better value than £2000-odd, but our installer is not offering the direct+PHE option. Just Vaillant or Newark. Or I could pick something like the Grant 150l with a 3.2m2 coil and much lower quoted heat-loss than Vaillant despite same insulation thickness, which is much better value, but no option for top immersion or temp sensor. I’ve also not really looked at the Newark Mini cyclinders which oddly don’t seem to quote a coil area.

Are there any examples in the monitored systems of small HPs with large-coil smallish tanks to see what COPs people are getting in reality?

I have a 5 bedroom, two bathroom house, and at the time of installation three occupants, one of which was our daughter, we have another daughter that comes to stay occasionally, both in their young twenties. We got the BUS grant.

We have a Vaillant Unitower, which is 190 ltr, only once did my youngest daughter complain about a cold shower, but, my other daughter that was staying said she found she had to turn the mixer temperature up next shower, and the data showed a tank temperature in the low forties IIRC. This is when I changed the reheat to 44°C just to be safe.

I have our hot water set at 50, and to reheat when it reaches 44. On rare occasions that could mean three reheats in a day. There is only two of us at home now, so it usually reheats once a day, or thereabouts. I doubt I’ve got water efficient showers, in fact having recently fitted a water meter connected to HA I think I used 80ltrs.

We have 29 kWh of battery storage, so very rare we use peak rate electricity, hence letting the water reheat whenever.

If the OP is on Agile, then it would make sense to use the immersion at times of negative or low costs, DHW can in certain weather conditions mean more defrosts.

I would also suggest a tank nearer 200lts would be better, two children at home, either are or will become teenagers, and they can use a lot of water.

We were on holiday recently, I set the DHW to 40°c, it took 94 hours to drop to 34°c from 50, house temperature is 21°c although the utility room is likely a little warmer. It did a reheat to 50°c after we left, I then set it to 40°c.

Although I look at systems with a HW CoP of 4.5 with envy, chasing COP for a very small heating demand is not worth it. CoP is like car fuel consumption; it has diminishing returns and if you don’t use much energy the gain is very small.

When I first installed our system I kept the 120l vented cylinder that was already installed. It had 22mm connections so wasn’t capable of taking the flow rate needed for high CoP but it still averaged 2.4 over 2 years. I’ve recently replaced it with a 210L heat pump cylinder with a 3M2 coil (and 28mm connections) bought off ebay for £500. That’s giving a CoP of about 3.5.

Looking at the energy used for hot water over the last 3 years it used 1126kWh with a CoP of 2.4. A CoP of 3.5 would reduce that to 772kWh, a saving of 350kWh or 120kWh per year or £16 p.a. at our average electricity cost, (£32 p.a. at the current price cap.)

Despite the CoP being better, the new cylinder looks to be using more energy, probably because it’s twice the size.

It’s certainly not worth spending £2,500 on a Heat Geek cylinder!

Thanks for that.

An unusual factor is the shower waste water heat recovery, which I think makes a substantial difference - the shower (which is only 8 l/min if you turn the flow rate up to max anyway) then only uses 5 l/min of 50°C water from the cylinder itself (because the shower’s “cold” feed is coming in at over 20°C), and the “cold” water going into the bottom of the cylinder also does-so at > 20°C instead of 7°C, cutting a chunk off the reheat times.

That was pushing me towards a 180 l cylinder instead of a 210 l.

The counter-argument being that you get no (or at least very little) heat recovery when having consecutive baths.

Both kids are already teenagers, but one will almost certainly moving out in September for the next academic year (already has an offer), but will probably still be around for ~3 months per year after then.

Unfortunately standing losses scale with cylinder size (although not quite linearly on average). Perhaps the OSO is the best bet if I can get it for a decent price - 191 litres and only 43 W of standing losses.

edit: I have some spare phenolic insulation boards, so I’ve also considered insulating the cylinder’s cupboard, but it’s better to have the insulation on the cylinder itself of course.

But your arguments that make sense to most people, has zero to do with MCS rules, their rules are related to you moving and selling the house, and everything the tax payer has paid for being suitable for that owner and their family.

If you want to customise you will need to a friendly installer that is willing to go against the rules or not go the BUS/MCS grant route.

That is the best route to go and the losses become almost zero, as the enclosed space gets warm and acts as a boundary to heat loss to room/house.

I asked Google AI how my 5 bedroom 2 bathroom house got approval with a 190 litre tank.

It said:

If you have a Vaillant uniTOWER in a 5-bedroom, 2-bathroom house, it means your installer used a clever “all-in-one” technical loophole built right into the Vaillant ecosystem to perfectly pass the Boiler Upgrade Scheme (BUS) guidelines.
Here is exactly how you ended up with the uniTOWER despite the general 250L+ rule of thumb:

  1. The uniTOWER is an Integrated System, Not Just a Tank

The Vaillant uniTOWER isn’t just a regular unvented cylinder; it is a compact indoor unit (about the size of a fridge-freezer). It houses:
• A 190-litre hot water cylinder.
• The expansion vessels, three-way valves, a decoupling module, and the necessary heat pump controller electronics.

  1. High-Performance Design Overrides Volume (The Tech Loophole)

The standard MCS rules state that if a cylinder is smaller than the standard bedroom allowance, it must prove it can regenerate hot water quickly enough to prevent the home from running out.
The uniTOWER is specifically engineered with an incredibly high-performance internal heat exchanger coil optimized for Vaillant’s aroTHERM plus heat pump. Because the coil transfers heat rapidly and uses a highly efficient reheating cycle, MCS software accepts its 190L capacity as equivalent to a standard 250L standalone cylinder. Vaillant formally rates the uniTOWER as capable of delivering enough hot water for a family of five using multiple rain showers.

I haven’t fact checked this, but with a 7kW heat pump it does reheat pretty quickly in just over 20 minutes.

So there may be scope within the rules for the OP to go for a smaller tank.

I disagree. The BUS grant itself just says that the system must be “capable of meeting the full space heating and hot water heating demands of that property”.

MCS MIS 3005-D (Section 3.5) says:

MCS Guidance Document MGD 007 references the old BS 6700, and gives a minimum cylinder size for a house with 1 bathroom and a 3 kW heat pump of 122 litres.

MGD 007 also notes that the manufacturer’s requirements should be followed (e.g. if these give different rules for cylinder sizing) and gives an example of such a manufacturer’s sizing table (which in the example given recommends either a 180 or 210 litre cylinder when a 3 kW to 6 kW heat pump is used for a 3 bedroom house with 1 bathroom).

… so all three methods that MCS reference also say that 180 litres is OK.

Whilst going below these minimums limits may require justification (albeit that they are described as “guidance” i.e. not mandatory) I am not proposing that, and none of them account for waste water heat recovery.

The MCS documents do note that an installer may (with justification) depart from the guidance, as an example a smaller cylinder may be used if there is insufficient space for the calculated cylinder size.

BS EN 12831-3 is yet another method for sizing hot water storage, and does allow for taking waste water heat recovery systems into consideration, and whilst I haven’t done a full calculation to that standard (which is complex!), I have looked at it sufficiently to see that it would base its calculations on 2.75 occupants (calculated from the house’s floor area).

When I move house it seems unlikely that I (or any subsequent owners) will instruct the movers to rip out the shower and/or waste water heat recovery device and stick them in the van, so taking these into consideration as relevant factors in the design seems reasonable in my opinion.

I have a 160l cylinder in a 4 bed house. One bathroom with electric shower over bath and a seperate shower room served by the cylinder.

Assessed by the MCS chappie who raised no objection to the cylinder size.