I’m planning to order an ASHP in the next week. It’s likely to be a 3.5 kW Vaillant aroTHERM Plus v2, or a 4 kW Grant Aerona 290. Family of 4, with 2x showers (both with drain water heat recovery at ~50% end-to-end efficiency) and 1x bath.
What DHW Cylinder options are there?
I’m looking for medium-to-large coil size, but also good standing losses. See below for reasons, but here is the table:
| Make/Model | Capacity (l) | Coil (m²) | Heat Loss (W) |
|---|---|---|---|
| Grant QR2SC180 | 168 | 3.2 | 50 |
| Newark HG200A4 | 187 | 4.0 | 76 |
| Newark custom 100mm ins | 187 | 4.0 | ~40 |
| Vaillant VIH RW 175/5 B ES | 173 | 1.85 | 58 |
| Gledhill PLUHP180 | 158 | 2.5 | 49 |
| Joule TCIMVH-0170LFB | 168 | 2.5 | 58 |
| McDonald EcoFlow 180 | 180 | 3.0 | 59 |
| Telford TSMI170/HP | 168 | 2.0 | 81 |
| Telford TSMI200/HP | 194 | 3.0 | 77 |
| OSO DGC 200 | 191 | 2.6 | 43 |
Notes - McDonald and Newark both offer customisation options which would allow for more insulation. There are lots of other options, but with the exception of the Vaillant I have ignored anything with a coil under 2 m².
- More efficiency is good (unless it never pays back - then the same money can do more good spent elsewhere!).
- The heat pump is small, and will probably be in silent/ECO mode most or even all of the time (dense urban area) e.g. for the Grant this means an output power of 3.0 kW.
- The showers use much less hot water than in a usual house due to the heat recovery - instead of 55 litres of DHW draw-off for a 10 minute shower, it only needs about 37 litres (and the cold water entering the bottom of the DHW tank is at about 24°C instead of 10°C).
- Since incoming water at bottom of the tank will be relatively warm, that favours a larger coil to maintain heat transfer.
- We only have one or two baths per week (no heat recovery on baths unless someone showers immediately after someone else has bathed - i.e. bath is drained as shower takes place).
- We are on the Octopus Agile tariff (and likely to stick with it), so being able to raise the tank to a high temperature when electricity is free and perhaps skip a DHW run the following day sounds like a good idea.
- A large coil size will allow higher cylinder temperature (for a given HP flow temperature), and good insulation will retain it for longer.
- Our heating season is short (highly insulated house, and the cylinder will be in the SW facing kitchen with a lot of solar gain), so the lost heat from the DHW cylinder is even less useful than in most houses, and a nuisance for most of the year.
I’m thinking something around 180 litres (150 litres may well be OK too, but restricts the options further and allows less multi-day storage), does that sound about right?
The platinum option would probably be a Newark/HG Cylinder custom made with 100mm insulation, but I suspect the cost would never pay back (with a big heat pump and/or higher DHW demand it probably would, but we have neither). Considering their cost, I’m surprised the Newark/HG cylinders have such poor standing losses in their default specs.
Although a different situation (larger tank, and heat pump) this topic is also relevant: Newark HG DHW Cylinder ROI
Any other thoughts or make/model suggestions very welcome!