> [@Timbones](#):
>
> I think the factor you need is `4200 / 60`, or simply `70`.

Worked example:

```auto
( 37.5 C - 31.6 C ) x 10.7 l/min x 70 = 4419 W

```

Which for an input of 995 W gives a COP of about `4.44` which seems about right.

---