# Ground source heat pump - temp monitoring

**URL:** <https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727>\
**Category:** Sustainable Energy\
**Created:** [1 November 2022 16:49 UTC](https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727 "2022-11-01T16:49:35Z")\
**Posts on this page:** 11\
**Page:** 1

<div class="post-metadata">

**Author:** ![raymop](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/raymop/32/14866_2.png) [@raymop](https://community.openenergymonitor.org/u/raymop)\
**Post date:** [1 November 2022 16:49 UTC](https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727/1 "2022-11-01T16:49:35Z")

</div>

I’ve had a ground source heat pump for several years and have been measuring the electrical power. I want to start measuring temperatures to better understand its efficiency.  
Which lines should I add DS18B20s to?  
My options are —

- water/methanol supply line from my yard
- water/methanol discharge line from my yard
- freon line to my heating/cooling coil in the air handler
- freon line from my heating/cooling coil in the air handler

PS: I also —  
measure power used by my air handler.  
measure the electric power used by my AUX electric heating coil.  
I also use superheat to warm my domestic hot water before going into the primary hot water heating tank, but wonder if I should monitor anything here?

P.

---

<div class="post-metadata">

**Author:** ![Vster](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/v/258eb7/32.png) [@Vster](https://community.openenergymonitor.org/u/Vster)\
**Post date:** [2 November 2022 15:29 UTC](https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727/2 "2022-11-02T15:29:50Z")

</div>

Without wanting to sound flippant, if you can, measure everything.  
That way you’ll have a better handle of what’s going on.  
Decent DS18B20 sensors are a couple of quid each, a Pi/EmonTH/ESP8266 isn’t too much either.  
I assume you have a working EmonCMS setup?

---

<div class="post-metadata">

**Author:** ![raymop](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/raymop/32/14866_2.png) [@raymop](https://community.openenergymonitor.org/u/raymop)\
**Post date:** [3 November 2022 00:29 UTC](https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727/3 "2022-11-03T00:29:01Z")

</div>

Thanks. I will do that.  
Question: what do I do with data?

---

<div class="post-metadata">

**Author:** ![Vster](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/v/258eb7/32.png) [@Vster](https://community.openenergymonitor.org/u/Vster)\
**Post date:** [13 November 2022 16:53 UTC](https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727/4 "2022-11-13T16:53:12Z")

</div>

Stuff it all into EmonCMS. Then draw some graphs.  
Then overlay different ‘chunks’ of data and see how things interact. Like external vs internal temperatures, vs energy use, vs HP runtimes/cycling.  
With a few months (or even years of data) patterns may start to emerge.

---

<div class="post-metadata">

**Author:** ![raymop](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/raymop/32/14866_2.png) [@raymop](https://community.openenergymonitor.org/u/raymop)\
**Post date:** [1 December 2022 03:54 UTC](https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727/5 "2022-12-01T03:54:24Z")

</div>

Continuing the discussion from [Ground source heat pump - temp monitoring](https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727):

Some time has passed while I got some measuring gear installed on my GHP.  
I am measuring the methanol/water mixture temperature as it comes from my ground loops and after it exits the heat pump.  
I have 6 ground loops and 2 compressors. It’s about 6 tons or 6.3kW of capacity.  
I monitor the W drawn by the pump and compressors.  
I have not installed a heat meter mainly because it’s $$ and I’d rather not break the lines open and thereby entrap air.  
I have the pump curve showing head pressure vs flow rate for the size impeller I have.  
Installed a pressure gage, not a transducer, yet. I read about 3 psi, which is equivalent to about 36 gpm. Or 6 gpm per ton or 6pm per ground loop. It’s on the high side, but that’s ok. Run well and silent.

Next step is to fill in the feeds for the COP heat pump app.

Since I know the flow rate, the water/alcohol mixture and specific heat, can I use these as input to the COP App?  
If so, I’m lost as to how!!!

---

<div class="post-metadata">

**Author:** ![borpin](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/borpin/32/193_2.png) [@borpin](https://community.openenergymonitor.org/u/borpin)\
**Post date:** [1 December 2022 07:20 UTC](https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727/6 "2022-12-01T07:20:42Z")

</div>

> [@raymop](#):
>
> If so, I’m lost as to how!!!

Look at this post by @Zarch although I’m not sure how to add that to the app 🙂

> [@Vaillant Arotherm Owners Thread](https://community.openenergymonitor.org/t/vaillant-arotherm-owners-thread/21891/16):
>
> Before we start, we have to remind ourselves of the following Heat Output = Specific heat capacity x flow rate (l/s) x (flow temperature - return temperature) Specific heat capacity (SHC) of water is 4.2 and it’s 3.8 for Gylcol. Flow Rate conversion m3/h to l/s = (m3h \* 0.277) Flow Rate conversion: l/hr to l/s = (l/hr / 3600) So 860l/hr = 860 / 3600 = 0.238 l/s 3.8 x 0.238 x 5DT = 4.5kW No if we go back to our ‘gold’ tech document, whilst it doesn’t list the 3.5kW model, it lists a 3kW…

---

<div class="post-metadata">

**Author:** ![Zarch](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/zarch/32/7947_2.png) [@Zarch](https://community.openenergymonitor.org/u/Zarch)\
**Post date:** [1 December 2022 08:15 UTC](https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727/7 "2022-12-01T08:15:41Z")

</div>

The heat pump app takes the following inputs

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/1/3/1376e24524a4b8988f2620a679d4e5d5feaab0c9.png)

ie, it expects the heat meter to provide the heat output.  
The heat meter is doing the following calc under the hood for us.

> Heat Output = Specific heat capacity x flow rate (l/s) x (flow temperature - return temperature)

So if you have those raw figures available to you, perhaps you can create your own ‘heat output feed’ based on the inputs you have?

---

<div class="post-metadata">

**Author:** ![AndyS](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/a/f4b2a3/32.png) [@AndyS](https://community.openenergymonitor.org/u/AndyS)\
**Post date:** [1 December 2022 09:14 UTC](https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727/8 "2022-12-01T09:14:44Z")

</div>

> [@Zarch](#):
>
> Heat Output = Specific heat capacity x flow rate (l/s) x (flow temperature - return temperature)

You need to add in density for the methanol mixture (Mick is using water only in his system I think): [Design of a central heating pump with example calculation](https://www.buildingservicestutor.com/design-of-a-heating-pump-with-example-calculation/) has a nice worked example.

If the density and SH are relatively constant across your operating conditions (dT) then it looks like you should have enough info to process some inputs into a feed suitable for the heat pump app.

---

<div class="post-metadata">

**Author:** ![Zarch](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/zarch/32/7947_2.png) [@Zarch](https://community.openenergymonitor.org/u/Zarch)\
**Post date:** [1 December 2022 09:22 UTC](https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727/9 "2022-12-01T09:22:29Z")

</div>

> [@AndyS](#):
>
> You need to add in density for the methanol mixture (Mick is using water only in his system I think):

Yep, i’m water only.

From the Heat Geek materials I’ve seen,

Specific heat capacity (SHC) of water is 4.2 and it’s 3.8 for Gylcol.

There might be more complex ways of working that all out, but those are the figures I’ve been passing on.

---

<div class="post-metadata">

**Author:** ![AndyS](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/a/f4b2a3/32.png) [@AndyS](https://community.openenergymonitor.org/u/AndyS)\
**Post date:** [1 December 2022 09:27 UTC](https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727/10 "2022-12-01T09:27:13Z")

</div>

> [@Zarch](#):
>
> Specific heat capacity (SHC) of water is 4.2 and it’s 3.8 for Gylcol.

> **[Ethylene Glycol Heat-Transfer Fluid Properties](https://www.engineeringtoolbox.com/ethylene-glycol-d_146.html)**
>
> Properties like freezing point, viscosity, specific gravity and specific heat of ethylene glycol based heat-transfer fluids, or brines.

> **[Propylene Glycol based Heat-Transfer Fluids](https://www.engineeringtoolbox.com/propylene-glycol-d_363.html)**
>
> Freezing points of propylene glycol based heat-transfer fluids suitable for the food processing industry.

(eg Sentinel R600)

---

<div class="post-metadata">

**Author:** ![raymop](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/raymop/32/14866_2.png) [@raymop](https://community.openenergymonitor.org/u/raymop)\
**Post date:** [2 December 2022 01:30 UTC](https://community.openenergymonitor.org/t/ground-source-heat-pump-temp-monitoring/21727/11 "2022-12-02T01:30:14Z")

</div>

Hey, thanks for jumping on with the replies. Super helpful.  
Here’s what I found for a 50:50 MeOH:H20  
Specific heat = 3.437 [kJ/kg-K] or [J/g-C] from [Table 8-3-2](https://detector-cooling.web.cern.ch/data/Table%208-3-2.htm)  
Density 0.92606 g/ml @ 4 degC from [Density and Concentration Calculator for Mixtures of Methanol and Water](https://www.handymath.com/cgi-bin/methanoltble3.cgi?submit=Entry)  
Flow Rate of 36 rpm = 2.2712 Liters per second  
Delta T is 1.2 deg C.  
Using from above:  
Heat Output = Specific heat capacity x flow rate (l/s) x (flow temperature - return temperature) \* Specific gravity  
Heat output = 8,674.72 (J/sec) or W or 8.674 kW

Thanks all for the help!

I’ll create a feed using these data and see what happens!