# Grant Aerona R290 Short Cycling

**URL:** <https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462>\
**Category:** Home Assistant\
**Tags:** grantr290\
**Created:** [13 October 2026 20:15 UTC](https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462 "2026-10-13T20:15:58Z")\
**Posts on this page:** 12\
**Page:** 1

<div class="post-metadata">

**Author:** ![germarsh](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/g/b782af/32.png) [@germarsh](https://community.openenergymonitor.org/u/germarsh)\
**Post date:** [13 October 2026 20:15 UTC](https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462/1 "2026-10-13T20:15:58Z")

</div>

Sorry I haven’t been on this forum for a while. It has been a learning curve compared with an older IVT GSHP. Many more sensors and not helped by three “circuits”.

Firstly, a general description of the hydraulic and electrical systems. Three storey house built in 2010 with UFH throughout. Every floor has a separate circ pump and zone valve originally controlled by Uponor C35 controllers. (I used a proprietary Raspberry Pi interface with the IVT to input the data via MQTT so I know something about tuning heat pumps regarding weather compensation - We lived in the Brecon Beacons.)

The ASHP was installed around April and it has be behaving well but I noticed some “short cycling” the last couple of weeks when the outside temp decreased. It is a 15.5 kW HP.

There seems to be a constraint with the Smart Controller that only circuits 2 and 3 have temp sensors. (By the way, the manual suggests putting the sensors on the flow after the control valves but that is silly. As soon as the zone valve opens, the circuit gets up to the target temp!)

We are expecting a Grant engineer in the next few days to give the system a once-over but I was wondering if anyone else has encountered some extreme cycling periods as we have - about four minutes of compressor running then about four minutes not. The heat pump circ pump is running so it is not a fault detection situation.

The only circuit currently with a Grant thermostat is Circuit 3 as that is the main living area. Circuit 2 is a basement flat which is rarely occupied hence zoning being a good idea.

I have attached an analysis using Home Assistant’s metrics so if anyone has any ideas I would be very grateful to hear them!

[Heat Pump Cycling Problem - v2.pdf](https://community.openenergymonitor.org/uploads/short-url/p2iQvZRxcTRkvsOcG9F3SEtEIus.pdf) (779.2 KB)

The IVT GSHP had fewer sensors than this one but there again it was controlled by just “radiator return” temp compared with the outside.

Any help would be gratefully received.

---

<div class="post-metadata">

**Author:** ![Johnmo](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/j/df705f/32.png) [@Johnmo](https://community.openenergymonitor.org/u/Johnmo)\
**Post date:** [13 October 2026 21:35 UTC](https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462/2 "2026-10-13T21:35:22Z")

</div>

Are you running a buffer? If you are closing the flow off to 2x floors, where is your 15.5kW ASHP pushing it’s water flow too? Not sure exactly what the flow rate is for a 15.5kW heat pump but suspect about 2 to 3m³/HR, so if the circulation has nowhere, or a limited amount of circuits to move the water through, the heat cannot be shifted either - you get short cycles.

---

<div class="post-metadata">

**Author:** ![germarsh](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/g/b782af/32.png) [@germarsh](https://community.openenergymonitor.org/u/germarsh)\
**Post date:** [14 October 2026 10:21 UTC](https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462/3 "2026-10-14T10:21:36Z")

</div>

Thank you for the quick response. There is a Grant Low Loss Header but the Hydraulic Scheme is set to Direct. (By installer with Grant specialist on the phone.)

It happened again this morning. The flow rate was about 35 m³/h. That seems a lot to me!

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/0/5/05daf1a7037541828f1ef7c1278d5f037f795a2e.png)

---

<div class="post-metadata">

**Author:** ![Johnmo](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/j/df705f/32.png) [@Johnmo](https://community.openenergymonitor.org/u/Johnmo)\
**Post date:** [14 October 2026 11:09 UTC](https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462/4 "2026-10-14T11:09:29Z")

</div>

Are you sure you haven’t missed a decimal place 3.5m³/h sounds a realistic flow rate for your heat pump. It’s still pretty mild really so heat loads aren’t high, so maybe it’s not getting rid of the heat quickly enough via one floor. I would engage more of the house and that should fix things. You will most likely cost less to run, as the heat pump can run steady state and achieve a much higher CoP.

> [@germarsh](#):
>
> By the way, the manual suggests putting the sensors on the flow after the control valves but that is silly

If you split the heating in to zones the heat pump is expecting a different flow temp for each zone via a mixer valve and hence the need for an indication of flow temp, so it can control the mixer valve. If you don’t have the temp sensor you don’t let the heat pump control that circuit.

Think you have made life more complex than it needs to be by over laying another control system. You have also sized the heat pump for the whole house, but only let it play with 1/3 of it, so the heat pump is in effect 2/3 to big.

I would be opening the system up to the heat pump, giving it plenty of room to flow into and the heat somewhere to go. I would operate as a single zone as far as the heat pump is concerned. Long steady runs give you a good average CoP, short run give a much poorer CoP.

---

<div class="post-metadata">

**Author:** ![germarsh](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/g/b782af/32.png) [@germarsh](https://community.openenergymonitor.org/u/germarsh)\
**Post date:** [14 October 2026 12:25 UTC](https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462/5 "2026-10-14T12:25:50Z")

</div>

One zone is for the basement which is rarely used. Another is for the second floor which is just a bedroom, bathroom and dressing room. The first floor is the main living area and that always has a UFH circuit open otherwise the thermostat would kick in the pump which would hit closed actuators. A Grant engineer is arriving tomorrow so I shall let you know what happens. Thanks for your help.

---

<div class="post-metadata">

**Author:** ![germarsh](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/g/b782af/32.png) [@germarsh](https://community.openenergymonitor.org/u/germarsh)\
**Post date:** [14 October 2026 12:30 UTC](https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462/6 "2026-10-14T12:30:27Z")

</div>

I cannot see why sometimes Circuit 3 works perfectly like it did from 06:46 this morning. Circuit 1 (second floor) kicked in at 08:27 but DHW stopped both circuits. When Circuit 3 started again at 09:26 it started playing silly buggers! I wouldn’t mind it if permanently played up. I’d have a chance to sort it out.

---

<div class="post-metadata">

**Author:** ![Johnmo](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/j/df705f/32.png) [@Johnmo](https://community.openenergymonitor.org/u/Johnmo)\
**Post date:** [14 October 2026 13:01 UTC](https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462/7 "2026-10-14T13:01:10Z")

</div>

So circuit 1 and 3 together runs ok, but circuit 3 alone, it plays up?

Is that correct?

---

<div class="post-metadata">

**Author:** ![germarsh](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/g/b782af/32.png) [@germarsh](https://community.openenergymonitor.org/u/germarsh)\
**Post date:** [14 October 2026 16:11 UTC](https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462/8 "2026-10-14T16:11:05Z")

</div>

Not all the time. This morning CIrc 3 ran perfectly happily by itself then Circ 1 kicked in as well and they both behaved. That was interrupted by 18 minutes of DHW demand then they both behaved again. Circ 1 stopped after about 15 minutes while Circ 3 continued for a total of about 30 mintes. Another DHW interruption (family taking showers in the morning after I told them to spread them through the day) and Circ 3 then started being daft.

---

<div class="post-metadata">

**Author:** ![germarsh](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/g/b782af/32.png) [@germarsh](https://community.openenergymonitor.org/u/germarsh)\
**Post date:** [14 October 2026 16:14 UTC](https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462/9 "2026-10-14T16:14:09Z")

</div>

Here is the sequence showing the pump frequency…

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/1/5/1568a360e4f90b6403ae165aa5649b697672e307.png)

…and here are the other metrics:

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/3/5/35c3d7f5cef13a7b0a1a6ecbb104c33677219b45.png)

---

<div class="post-metadata">

**Author:** ![germarsh](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/g/b782af/32.png) [@germarsh](https://community.openenergymonitor.org/u/germarsh)\
**Post date:** [17 October 2026 10:06 UTC](https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462/10 "2026-10-17T10:06:49Z")

</div>

**Grant Engineer Visit - Conclusions and Recommendations**

I shall put this in here in case anyone else has similar problems.

Fair play to the engineer, he quickly realised that the heat pump was outputting a much bigger flow than the Low Loss Header could clear on any circuit where there was only one UFH loop active. Basically, the heat pump could not modulate down low enough.

The answer to this one is to open up bigger circuits and - at least for the main living floor - use the Grant thermostat to control the overall temperature. This means that we can still use the Uponor thermostats to keep a cooler temperature in the three bedrooms on that floor.

However, the second floor under Circuit 1 is still a pain in the anal sphincter due to draughts and the like. This floor only has Uponor thermostats so no Grant thermostatic control. The circuit will only switch off if all the thermostats are not calling for heat. If one calls for heat we end up with the short cycling again. By the way, the flowchart in the Smart Controller manual does not help matters when there is no thermostat. I cannot work out how the smart controller / heat pump would control the temperature left under its own devices.

I shall keep an eye on the situation over the next few (colder) days.

---

<div class="post-metadata">

**Author:** ![Johnmo](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/j/df705f/32.png) [@Johnmo](https://community.openenergymonitor.org/u/Johnmo)\
**Post date:** [17 October 2026 12:15 UTC](https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462/11 "2026-10-17T12:15:56Z")

</div>

You need to do some room balancing of the UFH output. Then slowly do away with single room control. You have the system setup to micro control room temperature but really you need to work heat out matching heat lost by the room so you can run whole system open loop.

I started the same room thermostats everywhere, now it is one in the hall and the whole system is on or off, nothing in between. ASHP gets a very stable long run, gets great CoP while doing so, energy consumption has dropped like a stone. Any micro management and heat pump is a cost adder bit a cost saver.

---

<div class="post-metadata">

**Author:** ![germarsh](https://community.openenergymonitor.org/letter_avatar_proxy/v4/letter/g/b782af/32.png) [@germarsh](https://community.openenergymonitor.org/u/germarsh)\
**Post date:** [17 October 2026 13:05 UTC](https://community.openenergymonitor.org/t/grant-aerona-r290-short-cycling/30462/12 "2026-10-17T13:05:58Z")

</div>

You and others are quite correct, Johnmo. This morning the ground floor thermostat called for heat and, although the one thermostat covered 5 UFH loops, it still short cycled. I had to disable Thermostatic pump blockade on Circuit 3 - the only one with the grant thermostat - as that has a couple of big permanently open loops.

Thank you everyone for your help on this.