# Estimating Power from MelCloud data

**URL:** <https://community.openenergymonitor.org/t/estimating-power-from-melcloud-data/26767>\
**Category:** Heatpump\
**Tags:** melcloud, emontx, ecodan, emoncms\
**Created:** [25 September 2024 13:34 UTC](https://community.openenergymonitor.org/t/estimating-power-from-melcloud-data/26767 "2024-09-25T13:34:54Z")\
**Posts on this page:** 1\
**Showing post:** 2

<div class="post-metadata">

**Author:** ![Timbones](https://community.openenergymonitor.org/user_avatar/community.openenergymonitor.org/timbones/32/20308_2.png) [@Timbones](https://community.openenergymonitor.org/u/Timbones)\
**Post date:** [25 September 2024 15:07 UTC](https://community.openenergymonitor.org/t/estimating-power-from-melcloud-data/26767/2 "2024-09-25T15:07:04Z")

</div>

I have been doing something similar to estimate heat from Melcloud for a handful of systems.

I’ve calculated the heat output for different flow rates. 24 l/min equates to 1672 W per K of dT, where dT is the difference between flow and return. If 20% glycol then this drops to 1572.

- water: 4182 x _flow rate_ / 60
- glycol: 4000 x _flow rate_ / 60

(If you’re able to read actual flow rate, use that instead)

The feeds you need to pull from MelCloud are:

- **FlowTemperature**
- **ReturnTemperature**
- **WaterPump1Status** - primary pump
- **ValveStatus3Way** - 0 = heating, 1 = dhw

Then use input processing to compute the following:

**FlowTemperature** - ReturnTemperature × WaterPump1Status × WperK → heat and heat\_kwh

 ![image](https://community.openenergymonitor.org/uploads/default/original/3X/d/7/d7e6315163ef3b7117fd7390779303e237ca160f.png)

As this uses `Log` and `Power to kWh` processes, so can’t be done with virtual feeds.

I also have a method to estimate electrical consumption from MelCloud, but you don’t need that if you have power from emonTX.

---

_[View the full topic](https://community.openenergymonitor.org/t/estimating-power-from-melcloud-data/26767)._