> [@datoon](#):
>
> I’ve seen it higher previously.

That’s great you’ve seen it higher.

I was in the same position, I recollected (but had no evidence- monitoring etc) of low 30s l/m, and noticed once I hooked my system up to EmonCMS it wasn’t going beyond 22l/m….got back to 34l/m after cleaning both.

This was one year and only one of the two filters/strainers:

> [@Thank you OpenEnergyMonitor: Octopus Daikin ASHP monitoring](https://community.openenergymonitor.org/t/thank-you-openenergymonitor-octopus-daikin-ashp-monitoring/24589/372):
>
> I was wrong, Octopus did put a strainer/filter on the return correctly as well as the flow out to the heating system. I hadn’t appreciated there might be two, and the second on the return looked like a standard isolation valve. Unfortunately it was jam packed with debris - literally so bad whilst still in the valve, I couldn’t get a finger in and had to dislodge the sediment which promptly fell onto the floor. No idea how it was still working. I then pulled out the strainer/filter on the ret…

---