After months and months of research and quotes from Octopus, Heat Geek and British Gas I have finally got to the point of committing to the install.
I have chosen British Gas as they have proposed a better install over Octopus (and also price matched them). Both recommended a Daikin EDLA08EV3
The survey was light years ahead of Octopus, using far more sophisticated and thorough heat loss calculations, were far more flexible on installation options and have designed the system to 42.5c at -1.7c. They even followed up with pages and pages of detailed information which has been very useful.
BG were also £7000 cheaper than the local Heat Geek installers, (the BG total price to pay is just over £3000 including a 210l slimline HP cylinder and 25l volumiser) for a similar install.
Iād like to run by the forum the radiator proposal, just to make sure it is sensible. (I have followed Matt Dās posts and journey and am particularly keen to ensure the radiators are about right!).
4 bed mid 50ās semi including extension in 2007 (which doubled the house from a 2-4 bed)
135m2
Insulated cavity walls on 50ās house
200mm loft insulation
Electric underfloor heating in kitchen extension
10 radiators (plus 1 proposed addition for landing)
BG heat loss calculation 6.2kW (Octopus 6.9kW)
BG have designed the house @ 21c everywhere, including bedrooms (other than 22 for bathrooms), to maintain that temp throughout.
The bedrooms at 21c is the main question.
Is this in the real world likely to be ok? We donāt want overheating bedrooms, but also recognise that having bigger radiators, may actually be a benefit to the system as a whole.
BG will install TRVs to the bedroom radiators only.
This is the radiator schedule, which Iāve calculated should have enough capacity at 30c flow temp to allow the 8kw Daikin to modulate low enough.