> [@vbob](#):
>
> Wonder if there are other means to match it rather than measuring return temperatures on the buffer.

Measuring the temperatures at each of the 4 ports of the buffer can help determine if the two pumps are adequately matched. Can use cheap digital thermometers like [Mark did here](https://community.openenergymonitor.org/t/mitsu-zubadan-flow-temperature-issue/29576/130) using [John’s spreadsheet](https://community.openenergymonitor.org/t/mitsu-zubadan-flow-temperature-issue/29576/80) to calculate how it affects power delivery.

---