I agree with the above.
It could be that the thermostats are pulling and shutting down individually..
When I had our one thermostat controlling, it was very unsatisfactory! On / Off, too much hysteresis to be useful..
A temporary fix was to set impossibly high and then tune the system to actually supply what’s needed in water temp for the heat loss (depends on outdoor temp causing property to lose heat).
I assume you have a weather curve setting and can run on Leaving Water Temperature?
What I would try is to set all the room thermometers to impossibly high (while system is off.
Or disable all the thermostats in the controller and go Leaving Water Temperature.
Then set to Leaving Water Temperature and adjust the Weather Curve something like this..
At -9°C outside LWT is 43°C
At 13°C outside LWT is 25°C
I tried to upload a pic but can’t..
This is of course for our house and conditions.
South England, UFH, haouse built 10 years ago..
You then adjust the flows on the manifolds to each zone to achieve a stable whole house temperature.
Can have warmer downstairs and cooler upstairs like this.
We rarely see sub zero, but if we did see -9°C the Heatpump would output 43°C water.
During the shoulder months it spends much more time at the other end of the curve..
Right now it’s 11 or 12°C outside and the leaving water temp is 27 - 28°C.
What you get is a nice stable temperature throughout the whole house and no on offs.
If it went to below -9°C outside I could change the Weather Curve in 20 secs to accommodate.
This may seem a lot of work, but if you value comfort and Heatpump efficiency it was the only way with our system.
Maybe yours is smarter but not there yet?